    Daikin VRV III U3 error



    This is the first time we do installation of vrviii, and we make all wiring connections according to the installation manual diagrams, but when we turned on the power for the indoors and outdoors units H2P is blincking and U3 error monitored on the remote controller.
    would you please make your effort to assist us



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin VRV III U3 error

    U3 with VRVII shows that the initial CHECK function has not been completed.

    Do you VRVIII Design Guide ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2008
    Location
    LIBYA
    Age
    48
    Posts
    6
    Rep Power
    0

    Re: Daikin VRV III U3 error

    Thank you for your reply
    would please explain what do you mean by internal check

  4. #4
    Join Date
    Sep 2005
    Location
    england
    Age
    41
    Posts
    21
    Rep Power
    0

    Re: Daikin VRV III U3 error

    press and hold the test button to perform a test run. this will last for approx 45 mins. Or do a quick test with mode 2 binary 3. When your test run has completed, all of the controllers will flash "p7" when this happens, press the return button on the condensing unit, and happy days. This is the quick way of commissioning, but the refrigerant containment function will not be available.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin VRV III U3 error

    ^^ Demonstrates the need to have the correct instruction manual to hand and also to read it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin VRV III U3 error

    Quote Originally Posted by Suffolk Fridge View Post
    press and hold the test button to perform a test run. this will last for approx 45 mins. Or do a quick test with mode 2 binary 3. When your test run has completed, all of the controllers will flash "p7" when this happens, press the return button on the condensing unit, and happy days. This is the quick way of commissioning, but the refrigerant containment function will not be available.
    Hi all.
    Do the right long test too feed correctly the oil from the accumulator to the compressor and wait to reach the same temperature between the inlet and the outlet of the accumulator.
    From factory there's a low oil level inside the inverter compressor to facilitate startup at low ambient condition and avoid stall prevention.
    rgds
    cool#9

  7. #7
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: Daikin VRV III U3 error

    Hi
    This will help:

Similar Threads

  1. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  2. Daikin RZYQ8PY1 'E3' error?
    By Drew in forum Air Conditioning
    Replies: 7
    Last Post: 27-09-2008, 11:21 AM
  3. Daikin U4 error code
    By Minty in forum Air Conditioning
    Replies: 6
    Last Post: 16-05-2008, 11:36 PM
  4. E0 error code daikin vrv
    By coriolan in forum Air Conditioning
    Replies: 2
    Last Post: 21-06-2007, 03:55 PM
  5. DAIKIN AI ERROR help!!!!
    By philjd26 in forum Air Conditioning
    Replies: 17
    Last Post: 16-04-2007, 01:01 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •