Results 1 to 3 of 3
Thread: Ahu Condenser size?
-
26-03-2009, 09:05 PM #1
Ahu Condenser size?
Hi Guys,
We have asked to quote for a condensing unit to match a DX coil within a AHU, but the only information we have at the moment are air volumes across the evaporator coil and room design temperatures.
So my question is, is it possible to size a condensing unit from that information alone, and is it something that can be done using coolpack?
Regards
Danny
-
26-03-2009, 10:20 PM #2
Re: Ahu Condenser size?
You can make some very good approximations using air volume and room temps. plot them on a psychrometric chart .
Additionally you can get the detail of the evap coil, tubes high ; rows deep; number of circuits, tube size, fins/inch. assume a suitable evap temp and gas then call a coil manufacturer and ask for an equiv duty.
Or reverse engineer the evap coil and use software to determine the duty
This site has a software that can be used.
http://www.spcoils.co.uk/
I haven't looked at the coolpack software for a long time so I can't remember if it will help or not.Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
30-03-2009, 07:49 AM #3
Re: Ahu Condenser size?
can you provide the relevant information, application type ,refrigerant type room size? Your responce will only be as good as the information you provide.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM -
Condenser size for home AC
By sageoldmann in forum Technical SpeculationsReplies: 4Last Post: 31-05-2008, 08:56 PM