    Ahu Condenser size?



    Hi Guys,

    We have asked to quote for a condensing unit to match a DX coil within a AHU, but the only information we have at the moment are air volumes across the evaporator coil and room design temperatures.
    So my question is, is it possible to size a condensing unit from that information alone, and is it something that can be done using coolpack?

    Regards

    Danny



  2. #2
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    19

    Re: Ahu Condenser size?

    You can make some very good approximations using air volume and room temps. plot them on a psychrometric chart .
    Additionally you can get the detail of the evap coil, tubes high ; rows deep; number of circuits, tube size, fins/inch. assume a suitable evap temp and gas then call a coil manufacturer and ask for an equiv duty.

    Or reverse engineer the evap coil and use software to determine the duty

    This site has a software that can be used.

    http://www.spcoils.co.uk/

    I haven't looked at the coolpack software for a long time so I can't remember if it will help or not.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  3. #3
    Join Date
    Mar 2005
    Location
    uk
    Age
    48
    Posts
    34
    Rep Power
    0

    Re: Ahu Condenser size?

    can you provide the relevant information, application type ,refrigerant type room size? Your responce will only be as good as the information you provide.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Condenser size for home AC
    By sageoldmann in forum Technical Speculations
    Replies: 4
    Last Post: 31-05-2008, 08:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •