    Never take anything for granted



    I`ve got a problem with two Airdale units (apart from the one mentioned on a previous post) both tripping on HP. I can actually see the pressure rise until they trip on these ones. They are ducted heat pump ones.
    Checked the usual stuff: condensors, ducting filters and evaporators; all ok.
    The air flow didn`t seem quite right so climbed up into the roof void which was so tight the builders had to cut notches out of the roof trusses to fit over the ducting. After struggling to get the fan inspection cover off I found the reason for the tripping: the ducting manufacturers had fitted the fan upside down in the fan box so that the gap for the air to the fan is 1/2" this along with the filters and sound attenuation is the the cause of the tripping.
    The client said they`d had problems for years. His previous aircon guy had linked out the Hp switch on one unit resulting in the compressor failing TWICE.
    Now all I`ve got to do is cut the ducting out and turn it over!! after cutting the roof trusses away.
    Here`s a pic. the ratchet is a 3/8 drive to give scale



  2. #2
    Join Date
    Aug 2008
    Location
    Australia
    Age
    57
    Posts
    28
    Rep Power
    0

    Re: Never take anything for granted

    Looks like fun, glad I am not involved. It can get quite hot and cramped working in ceilings.

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Never take anything for granted

    hi glenn
    are the fan motors 3ph , is the direction right? I ,m sure its worth testing first,

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Never take anything for granted

    As above post says, it could be wired wrong causing it to run backwards.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Never take anything for granted

    Well done Glen.
    Doesn't it feel good when you are able to resolve a problem that is "historic".
    Good engineering practises reward all in the end.
    Meaning those that ask why as well as what needs replacing!
    Once again well done.
    Sounds like a job for the apprentice!!!
    (usually the only 1 slim enough to fit in tight spots!!)
    Grizzly

  6. #6
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Never take anything for granted

    Hi grizzly,
    Went back today to finnish the job, found the problem wasn`t the fan upside down but the AV mountings supporting the fan box had given way (incorrectly fitted) allowing the fan to fall directly onto the ducting stopping the air flow.I fitted new mounts and checked the air velocity into the outdoor grill, it was 1.18 m/sec before the repair and
    3 m/sec after. The HP is now steady at 220 psi before it was 450 and tripping out.

    Smug, self satsfied Glenn signing out;-)

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Never take anything for granted

    Quote Originally Posted by glenn1340 View Post
    Smug, self satisfied Glenn signing out;-)
    and why not, well done Glen.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •