    VRV heat recovery which manufacturer.



    Just a quick question, which manufacturer for a heat recovery vrv/vrf air conditioning system. Do we install a 2 pipe or other manufacturers using 3 pipe.

    What are the advantages for the installer of each method of system and which are easier.

    We have looked at Sanyo (preffered at the moment), Mitsi, Hitachi, Daiken which is really best for us and who helps the installer most.

    System size 90Kw over 2 floors with 15 indoor units of mixed cassette & high wall.

    Kind regards
    LRAC


    Grumpy men live longer

  2. #2
    Join Date
    Nov 2008
    Location
    UK
    Posts
    69
    Rep Power
    16

    Re: VRV heat recovery which manufacturer.

    Support from Sanyo and Hitachi are top notch in my opinion, Daikin only if you are already or have the potential to be a D1 and Mitsi likewise for their "partners", for one off jobs support from both of those can be lacking and you'd probably be better off dealing with one of their distributors, you'll get the same price. As you've said Sanyo is the preferred option at the momen be ready to supply their quote when asking for alternatives, price matching is common place now and all the manufacturers you mention should be able to hit the same price points. As for the 2 pipe vs 3 pipe debate, there's a whole stack of info on that around here somewhere already with all the pros and cons.

  3. #3
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    18

    Re: VRV heat recovery which manufacturer.

    2 pipe/3 pipe. that is a million dollar question. I think it all depends on the building you are applying it to.
    Maybe get some reps and speak to them.
    I dont no anything about Sanyo (Mitsi/Daikin man myself) but i am interested to see there take on things.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: VRV heat recovery which manufacturer.

    Most, if not all manufacturers offer decent vrv/vrf kit nowadays, and they all work to the best that the electronic controls can provide.

    There are obviously differences in the software programming so some brands perform better than others, but, hey, it takes a good man to see the difference

    There are however, basic differences between 2 pipe and 3 pipe systems (Mitsi excluded). A 2 pipe system outdoor unit can only provide heating or cooling at any one time (heat pump) whereas a 3 pipe system can heating and cooling at the same time.(heat recovery)

    You need to determine what you need indoors and then make your selection based on this. If you are looking to condition a large open plan office that has one side in sun and one side in shade then the 3 pipe system may be best suited, as it would also be with a hotel install, 3 pipe is nearly always needed. One room may call for cooling but the adjacent room may want heating.

    At the end of the day it will all come down to cost

  5. #5
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    18

    Re: VRV heat recovery which manufacturer.

    Frank i totally agree, but why not get the best of both world. 2 PIPE HEAT RECOVERY.!! Mitsubishi electric systems are one step ahead. As for cost mitsi seem to be in the same ball part with price to other manufacturers. I guess the application is the important aspect to consider.

  6. #6
    Join Date
    May 2008
    Location
    England
    Posts
    101
    Rep Power
    16

    Re: VRV heat recovery which manufacturer.

    Am i correct in assuming Sanyo is rebadged Airwell?
    Not that there is anything wrong with either of them.

  7. #7
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: VRV heat recovery which manufacturer.

    Airwell have badged up the Sanyo VRF system as Airwell.
    Grumpy men live longer

  8. #8
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: VRV heat recovery which manufacturer.

    If you have simulataneous heating & cooling demands (e.g. internal & external offices or meeting rooms) then you should consider 3-pipe otherwise you will have the age old problem of one or two areas "locking up" the system operation in one mode or the other to the exclusion of others.
    If you don't want to have all your "eggs in one 3-pipe refrigerant system basket" then consider multiple smaller capacty 2 pipe systems serving individual zones, floors or faces of the building e.g. internal, north / south etc. This makes for smaller outdoor units which are easier to manhandle and locate on crowed roofs. Also individual system refrigerant charges are reduced which helps to comply with BSEN 378 (min frig charge in relation to smallest room volume).
    In my experience you can buy at least 20% cheaper than Daikin / Mitsi Elec. Not every job needs or can afford a premium manufacturer in the current climate.
    If in doubt read the instructions. If still in doubt follow them.

  9. #9
    Join Date
    Sep 2005
    Location
    england
    Age
    41
    Posts
    21
    Rep Power
    0

    Re: VRV heat recovery which manufacturer.

    Any application has to be mitsubishi's new pury-yhma series. Best kit on the market by far, fit the fan coils with par-27 controllers and you are laughing. The only thing where daikin excell is the I touch controller, but mitsubishi are now bringing out a touch screen version of the G50 to compete, although im yet to commission one.

  10. #10
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: VRV heat recovery which manufacturer.

    The Mitsubishi Electric AG150 touch screen central control is a very good controller which is installed the same as a G50.

    It is very easy to set up & use

    Commissioned one this week

    Set up & full operational in about 10 to 15 mins

    No activation code needed
    No manual needed
    No phone calls to tech help desk needed

    For basic set up just set the
    language
    date & time
    each indoor unit / remote control / group & name
    time clock schedule

    Bobs your uncle
    Job done.

    There is loads more you can do with it which you would need to look at a manual or ask technical help.
    But for basic set up & operation its plug & play.

  11. #11
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: VRV heat recovery which manufacturer.

    Having looked at all of the pro's and con's it looks like Sanyo 3 pipe system, cheers for your advice guys.
    Grumpy men live longer

  12. #12
    Join Date
    Mar 2009
    Location
    Ireland
    Age
    39
    Posts
    25
    Rep Power
    0

    Re: VRV heat recovery which manufacturer.

    we recently installed 3x 3-pipe sanyo vrf systems into a car dealership for a contractor and thought they were a great piece of kit!! very easy to setup and commision with no niggling little problems on start up. highly recommended!!

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Replies: 10
    Last Post: 18-07-2007, 08:07 AM
  5. Heat recovery and aquifer heat/cold storage
    By RicHoe in forum Supermarket Refrigeration
    Replies: 23
    Last Post: 23-06-2006, 01:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •