    Power factor correction



    HI Guy,s

    I need some help please . I have an old 28 KW split system it has two direct on line compressors and a single phase condensor fan motor. The indoor is a 28 kw high static ducted unit.

    The problem is my client has a wattless charge on his bill. Which I'm informed by the Electricial company is being generated by the old aircon system. They have had an energy audit and have checked all other equipment in the building. Apparently if the wattless charge is more than 30% of the total bill the wattless charge is applied.

    The power factor efficiency( if thats the correct term of the outdoor is 88%) we are operating on 3 phase 400v AC and the rated power input is 11 KW. There is no witch hunt here my client just needs advice on what size type of power factor correction system can be purchased.

    The only thing I know about Power Factor Correction is how to spell it. Any advice would be greatly appreciated

    Thanks in advance

    T



  2. #2
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Power factor correction

    I dont have any knowledge on what equipment might be available.
    If my math is correct the AC system have a reactive/active amps ratio of 47/88. That is way above the 30% (30/100) stated by the power company.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Power factor correction

    At first, you have to install a three phase power monitor and analyser to have a magnitude of the reactive power. Possibly you have to diagnose whether the reactive power is due to phase displacement of harmonic distortion.
    When the assessment is complete, you can go to a consultant for sizing the capacitors bank

  4. #4
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Power factor correction

    He who dies with the most Toys, WINS!

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Power factor correction

    tony

    check your inbox.

    Al

  6. #6
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Power factor correction

    Hi All,

    Thanks for the input. Between Sinewaves PDF and Al's info. I have enough info. I really appreciate the input and if I can ever do anything for you guy's just ask.

    Thanks AGAIN

    T

Similar Threads

  1. Power Factor calculation
    By K.R.Iyer in forum Fundamentals
    Replies: 11
    Last Post: 08-02-2009, 08:37 PM
  2. compressor ratings in horse power
    By themba in forum Fundamentals
    Replies: 6
    Last Post: 30-03-2008, 12:07 AM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  4. Daikin KRP2A61 Card Power consumption
    By EddieC in forum Air Conditioning
    Replies: 5
    Last Post: 19-08-2006, 04:08 PM
  5. NEW 3-Phase IGBT Inverter Power IC
    By theberes in forum New Technologies
    Replies: 14
    Last Post: 01-03-2004, 01:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •