26-02-2009, 06:54 AM #1
Air to water split heat pump design
Hi, we want to design a new Air to water split heat pump, we have three questions:
1.The compressor should be located in the outside unit or inside unit? Which one is better?
2.Can we place the buffer tank in the inside unit?
3.we want to design a double jacketed hot water tank , which means that it consists of two separate tanks. The hot water is heated in the inner jacket.The inside tank is 200L,the outside tank is 300L, is it ok?
-
26-02-2009, 07:27 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Air to water split heat pump design
Outside. Reasoning:
Noise is generated outside
Smaller dimensions of indoor unit
Possibility to install more then one indoor unit
2.Can we place the buffer tank in the inside unit?
3.we want to design a double jacketed hot water tank , which means that it consists of two separate tanks. The hot water is heated in the inner jacket.The inside tank is 200L,the outside tank is 300L, is it ok?
-
26-02-2009, 07:39 AM #3
Re: Air to water split heat pump design
we want "tank in tank "because we think it's more efficient---the heating area is bigger than spiral tube.
-
26-02-2009, 08:00 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Air to water split heat pump design
Did you make calculation on surface area of cylindrical tank of 200L and say 10m of pipe of 1" diameter?
Cylinder of 0,4m height and 0,4m radius has volume of cca 200L and active area (in other cylinder active is only mantle and bottom area) of cca 1,5m^2.
Pipe of 1" diameter and 10m lenght roled in spiral (8 windings of 0,2m radius) have active area of 1.59m^2.Last edited by nike123; 26-02-2009 at 08:39 AM.
Similar Threads
-
Sensible Heat Factor / capacity of Inverter split Systems at part load?
By Greengrocer in forum Technical SpeculationsReplies: 31Last Post: 09-02-2009, 04:57 PM -
water source heat pump
By gramcor in forum Air ConditioningReplies: 1Last Post: 11-03-2008, 12:06 AM -
chilled water pump design
By afeef in forum FundamentalsReplies: 5Last Post: 16-09-2005, 12:06 AM -
Water Source Heat Pump
By aliugur in forum FundamentalsReplies: 1Last Post: 02-06-2002, 03:24 PM -
R134a <-> liquid heat exchanger design
By DaBit in forum Technical SpeculationsReplies: 19Last Post: 10-05-2002, 08:36 AM