    Hermatic klixon question



    Hiya all ..... forgive the ignorance .... however looking at a foster freezer cabinet (out of my field really) earlier that has a CAJ2446Z compressor that is tripping the klixon that is in the top of the compressor after 10 15 mins running time have checked wht I consider normal stuff (levels vacced etc) but still it does it .......... is there a test to "prove" the klixon ok, or as I am contemplating, Compressor renewal time is upon us ?? runs fine with no noises (with klixon in the air above the comp) it does run hot but really seems no hotter than the chiller next to it ? you can put your hand on it but you wouldn't want to leave it there too long !

    Cheers in advance

    Brian



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hermatic klixon question

    I suppose that if you could find the specification for the Klixon and the trip temperature then you could test it.

    Temperature: maybe by heating in boiling water ??

    Amperage: you'd have to find a way of overloading it.

    Cheapest option perhaps is to buy a new Klixon and see what happens.

    I assume that the amperage is not excessive.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2009
    Location
    Isle of Man
    Posts
    23
    Rep Power
    0

    Re: Hermatic klixon question

    Hiya ..... wasn't aware that an amps issue could cause tripping but am now ? in other words didn't check amps ! .... left unit running with klixon away from compressor as didn't seem any detrement in doing that ? unit refrigerates fine, or seems to ? prior to that has struggled to pull temp for approx a year ! according to friend that owns it ? he even said earlier that he thought that it was supposed to stop even though it wasn't at temperature or on defrost ?

    Cheers again

    Brian

  4. #4
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Hermatic klixon question

    blocked condenser / blocked capillary / SOG

    above three or combinations of maybe possibilities

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Hermatic klixon question

    Hi manaircrest its RLA 3.8A,MAX CURRENT 7.5A, LRA 29A,the klixon opens at120c and closes at 69c, its start cap is 88uf and run cap 15 uf and winding reading at 20c is 2.2 ohms main and 9.2 ohms aux

  6. #6
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Hermatic klixon question

    check amps pulled and then check compressor over heating. i take it the fans ok and condensers clean?

  7. #7
    Join Date
    Feb 2009
    Location
    Isle of Man
    Posts
    23
    Rep Power
    0

    Re: Hermatic klixon question

    Hi all thanks for replies I vacced out the unit with no problems or issues to full tor, recharged on 404 (as was) with 600g as stated on the rateing plate unit pulls down fine. fan working ok and condenser although not pristine does not appear blocked and pipework away from condenser is not hot (mildly warm)pipework into condensate tray and to condenser is very hot and is steaming away the condensate so I'm fairly sure its ok I have noticed however that the rubber feet on the compressor have seen better days other than that everything looks as i think it should ?

  8. #8
    Join Date
    Dec 2008
    Location
    South Wales
    Age
    61
    Posts
    17
    Rep Power
    0

    Re: Hermatic klixon question

    Your original post stated that there was another chiller next to the one giving a problem. If it was the same model compressor you could have swapped the klixons over from one to another. the outcome of this would have helped you in your diagnosis.

  9. #9
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Hermatic klixon question

    if u mean all squashed down probly means comps been cooking herself

  10. #10
    Join Date
    Feb 2009
    Location
    UK
    Posts
    36
    Rep Power
    0

    Re: Hermatic klixon question

    I would Megga test the comp to determin what the insulation resistance of the windings are.

    If the winding are below 500 ohms, then the compressor will turn into a kettel.

    Every time i hear a kixon i go get my insulation tester, then test the caps, then test the winding resistance.

    hope that helps

    wombat

  11. #11
    Join Date
    Feb 2009
    Location
    Isle of Man
    Posts
    23
    Rep Power
    0

    Re: Hermatic klixon question

    Hi Thanks to all ..... comp on unit next door is of differant type to answer that one had thought of that .... comp has side electric box not top and was worried re the difference and the robbing peter to pay paul issue ..... also the mounts are all squashed down which was why i mentioned that coz I was along that thought train in that am going to price and avail a new comp 2 moz and give my friend that option as opposed to a replacement unit that he was considering ?? thanks to all again, all the very best Brian

  12. #12
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    65
    Posts
    113
    Rep Power
    16

    Re: Hermatic klixon question

    A CSR compressor will run hot and and sometimes cycle on the klixon when the run capacitor is stuffed. I'd suggest you check it with a capacitance meter. It should be within 10% of the capacitance written on the cap.
    According to GHAZ that should be 15uf in our case.
    As these compressors rely to a certain extent on suction vapor to cool the windings, check your total suction superheat.
    if it's too high you'll also be cooking your oil due to excessive discharge temperature.

Similar Threads

  1. Heat Transfer Exam Question
    By alexdouglas1969 in forum Fundamentals
    Replies: 10
    Last Post: 13-12-2008, 04:19 PM
  2. Refriferation cycle question
    By ozmecheng in forum Fundamentals
    Replies: 32
    Last Post: 26-03-2008, 10:38 PM
  3. Hitachi RAC25NH5 question
    By Yonas in forum Heat Pumps
    Replies: 11
    Last Post: 30-01-2008, 10:53 AM
  4. quizy type question thingy
    By rbartlett in forum Chit Chat & Service Stories
    Replies: 25
    Last Post: 06-02-2006, 09:22 PM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •