Thread: York YCAF sensor problems
Hybrid View
-
19-02-2009, 01:23 PM #1
York YCAF sensor problems
Hi all,
Can anyone help me with the following problem on a 1994 York YCAF single circuit water chiller?
The unit will start up fine, but after a time (more often than not 16 minutes) stop with the message "LWT (leaving water temp) sensor fault". It then starts up again after the recycle time and does the same again, locking out after the third attempt. I know that the sensor and it's wiring back to the board are not the problem. I removed the sensor and put in a resistor of suitable value to make the unit think the water was at 16 deg. C. I also put in a new piece of cable from the sensor to the board. I have also changed the control board with one salvaged from a scrap twin-circuit unit after swapping the EPROM and RAM chips. All to no avail. HELP!
-
19-02-2009, 06:48 PM #2
Re: York YCAF sensor problems
HI and welcome to the forum.
Not sure about this particular chiller but what is the actual water temperature at the time ?
Sometimes two faults can trigger the same fault code.
Is the machine hitting minimum water temperature and going for freeze protection ??Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-02-2009, 08:02 PM #3
Re: York YCAF sensor problems
on start up these older chillers take lwt and compare it to suction temp i think, if the difference is too large then it faults with lwt fault. check gas and water flow rates are ok, ie could be blocked water filter or gas leak.
also if water temp is too high then this results in lwt fault showing.
al
-
19-02-2009, 08:05 PM #4
Re: York YCAF sensor problems
Check eeprom is right way up with all prongs inserted!!
also i had previous probs with 5vdc being dragged down by an intermittant fault on the oil sensor.....keep us informed!
al
-
30-07-2009, 02:40 PM #5
Re: York YCAF sensor problems
braın abi ben tr den erol dilimi anlarmısın bilmiyorum ama Allah senden razı olsun.Sayende york chilleri çözdüm.lwt sensör fault artık tarih oldu kendine çok iyi bak bana yazarsan sevinirim abi....
-
20-02-2009, 02:07 AM #6
Re: York YCAF sensor problems
Change it to return water control. al is correct in his diagnosis. You will also find the start to run time is a excessively high ratio. Seen this before return water sensing solved the problem.
-
20-02-2009, 01:17 PM #7
Re: York YCAF sensor problems
Thanks Gents for your replies.
To continue, leaving water temp is about 17 C, so no danger of frost protection. Plenty of water flow as well. Pressures are 3.5 bar suct. 17.5 disch. (R 22) Strangely for a York, the unit does not have an inlet water temp sensor. Nor does it have gas temperature sensors, only pressures. So changing to return temp control is out. Haven't checked 5v yet, but I will.
However, there has been another development. The chiller is connected to a large (90,000 litre) tank, so any temperature changes happen very slowly. It's quite cool today (7 C) so I took the LWT sensor out of it's hole and left it dangling in free air and set the unit to 4 C. Now the thing has been running for 4 hours without stopping. Al is indeed correct. Why does it think that 17 C is too hot? What kind of strange York logic is this? At what point does it think the water is cool enough to continue?
-
20-02-2009, 04:45 PM #8
Re: York YCAF sensor problems
Hi, just a quick thought, 3.5 bar r22 is evaperating at below freezing(sorry no comparitor handy)at 17 deg c I would expect a lot higher suction pressure.SOG or starving tev perhaps? All the best, Kev.
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
YORK ducted split
By ALONEI in forum Trouble ShootingReplies: 7Last Post: 10-07-2010, 02:18 AM -
York YCUM (YCAM) ICOM needed.
By Jacek in forum Trouble ShootingReplies: 6Last Post: 01-02-2010, 10:14 PM -
York Recip NH3 Compressor Info
By CIR391 in forum Industrial CompressorsReplies: 1Last Post: 05-05-2009, 11:51 AM -
York Lch Series Schematics
By greg56 in forum Supermarket RefrigerationReplies: 0Last Post: 04-08-2008, 02:31 AM