    HRV Server rooms



    Has anyone out there an example of how they would size heat recovery ventilation within a server room. I like the idea of these systems and will promote them because they supply free cooling in winter and can raise the r/h within the space. The sales reps that i've spoken to in the past work on 10 l/s per person, so I have a couple of questions in relation to this.
    1. How would you size HRV with no people occupying the space?
    2. Do you allow a certain % of extra cooling duty to allow for a high ambient (say 30c) with HRV in operation?



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: HRV Server rooms

    Quote Originally Posted by AbsoluteWDJ View Post
    Has anyone out there an example of how they would size heat recovery ventilation within a server room. I like the idea of these systems and will promote them because they supply free cooling in winter and can raise the r/h within the space. The sales reps that i've spoken to in the past work on 10 l/s per person, so I have a couple of questions in relation to this.
    1. How would you size HRV with no people occupying the space?
    2. Do you allow a certain % of extra cooling duty to allow for a high ambient (say 30c) with HRV in operation?
    1 Air changes per hr
    2 Add no more than 10% if in full HE mode

    http://www.engineeringtoolbox.com/ai...oom-d_867.html

    The problem with these numbers is that the ahu can end up being very large. just quote a VAM1000 every time ;-)
    Last edited by multisync; 19-02-2009 at 01:44 PM.

  3. #3
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: HRV Server rooms

    Quote Originally Posted by multisync View Post
    1 Air changes per hr
    2 Add no more than 10% if in full HE mode

    http://www.engineeringtoolbox.com/ai...oom-d_867.html

    The problem with these numbers is that the ahu can end up being very large. just quote a VAM1000 every time ;-)

    Very helpful....Thanks Multisync

Similar Threads

  1. Inverters in server room
    By AbsoluteWDJ in forum Air Conditioning
    Replies: 35
    Last Post: 22-02-2009, 08:45 AM
  2. Server Room A/C!
    By sinewave in forum Air Conditioning
    Replies: 14
    Last Post: 11-07-2008, 12:08 AM
  3. Porkka cold rooms
    By Andy AC in forum Commercial
    Replies: 6
    Last Post: 29-08-2007, 08:14 AM
  4. Server rooms.
    By Temprite in forum Air Conditioning
    Replies: 62
    Last Post: 01-08-2007, 11:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •