Results 1 to 8 of 8
Thread: Carrier 30GK 085
19-02-2009, 10:00 AM #1
Carrier 30GK 085
Having a problem with fault 701, hot gas thermostat contact open having trouble finding the cause. Does anyone have a wiring diagram?
19-02-2009, 07:12 PM #2
Re: Carrier 30GK 085
HI, according to the Prodialog codes, 701 is a high discharge gas temperature fault.
Which probably means you either have a faulty probe or you are short of gas.
The probe is in the compressor head.
Control manual here if wanted
http://eto.carrier.com/litterature/cm/13411.pdf
Full set of manuals for the chiller
http://eto.carrier.com/lit.asp
Scroll down to your model and 'search'.Last edited by Brian_UK; 19-02-2009 at 08:14 PM. Reason: Wrong link
19-02-2009, 07:58 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
This link doesnt goes where it should be!
I think this is Ok link:
19-02-2009, 08:15 PM #4
20-02-2009, 02:03 AM #5
Could be a nuisance trip if everything else is in order. Carrier had issues with the DTS years ago. It is on a dry circuit. You ohm it out and it reads good, but the board does not see it as closed. Carrier tech support had me jump them out as they felt the breakers and HP control would protect the compressor and the DTS wasnt needed. Just food for thought here.
23-02-2009, 10:18 PM #6
I don't speak english very well. Excuse me
The DGT cut off near 115°C. Check the SDT.
If you don't read this temp, you have 2 solutions
1/ replace the dgt
2/check the starter guard board (put a jump)
If you read SDT near 100°C
Check the compressor.
25-02-2009, 07:23 PM #7
Thanks for your help guys turned out that the jump on the board for B3 had a loose connection...
25-02-2009, 07:45 PM #8
Thanks for the update and pleased to read that it was an easy/simple cure.
carrier 30GK 085
By ding dong in forum CommercialReplies: 7Last Post: 15-02-2011, 12:48 AM -
30GK carrier chiller wiring diagram
By ash_sabi2006 in forum ElectricalReplies: 6Last Post: 20-05-2010, 04:26 PM -
Carrier Chillers
By Ed Burris in forum Technical DiscussionsReplies: 6Last Post: 27-03-2010, 02:00 AM -
Geoff in NY ~ Carrier Parts
By Futsal1st in forum Trouble ShootingReplies: 6Last Post: 30-12-2009, 04:07 AM