    HI all of you
    I have on York Air cooled chiller those data.
    OIL pressure 18.5 barg -- OIL temperature 60.82 C
    SP 5.32barg --ST 9.9 C
    DP20.2barg --DT78.8
    SAT SUC 9.1
    SH 0.4
    SAT DISCH 52.3
    DISH SH 29.5
    AMBIENT T 30
    Leaving Water T 7.9
    Retuern Water T 93.7
    STEP 75
    With a Laser thermometer i have on
    The liquid line 32 C and afetr the economizer tthe liquid line is 12 C going to TXV .Before entrying the TXV , liquid line is 14 C , sight glass bubbling .TXV is iceing.

    I have 43 C (1699KPA) at entrying of the dryer

    Here is my conclusion
    I have too subcooling and highdischarge pressure .
    Super heat too small
    for me there is to much refrigerant is the system .
    Ive try to explain the Ice on TXV and Bubble on the sigthglass by the fact thtat the liguid line entryig the TXV too cool and surely the economizer( heat exhanger) should be full of liquid refrigerant.
    Someone has try too set the TXV super-heat(I ve put back to the factory setting )but no change .
    Was this troubleshooting correct.

    PS It is R407C -Screw type chiller



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Correct me if I am wrong

    Quote Originally Posted by LDK View Post
    HI all of you
    I have on York Air cooled chiller those data.
    OIL pressure 18.5 barg -- OIL temperature 60.82 C
    SP 5.32barg --ST 9.9 C
    DP20.2barg --DT78.8
    SAT SUC 9.1
    SH 0.4
    SAT DISCH 52.3
    DISH SH 29.5
    AMBIENT T 30
    Leaving Water T 7.9
    Retuern Water T 93.7
    STEP 75
    With a Laser thermometer i have on
    The liquid line 32 C and afetr the economizer tthe liquid line is 12 C going to TXV .Before entrying the TXV , liquid line is 14 C , sight glass bubbling .TXV is iceing.

    I have 43 C (1699KPA) at entrying of the dryer

    Here is my conclusion
    I have too subcooling and highdischarge pressure .
    Super heat too small
    for me there is to much refrigerant is the system .
    Ive try to explain the Ice on TXV and Bubble on the sigthglass by the fact thtat the liguid line entryig the TXV too cool and surely the economizer( heat exhanger) should be full of liquid refrigerant.
    Someone has try too set the TXV super-heat(I ve put back to the factory setting )but no change .
    Was this troubleshooting correct.

    PS It is R407C -Screw type chiller
    Hi LDK

    at a quick glance pressures look ok for +30c and reading this and your other post together - i would be leaning towards low on gas or blocked drier- oil seperator is a good place to start for leaks- common fault

    check your temp readings again with k-type thermocouple - especially water temps as 7 leaving and 93 return are not right

    take pressure and temp readings from same point on liquid line(subcooling)

    check temp either side of drier - if blocked this will account for drop in temp on liquid line and flash gas in sight glass
    Last edited by chillerman2006; 01-02-2009 at 01:41 AM.

  3. #3
    Join Date
    Feb 2008
    Location
    Saudi Arabia
    Age
    52
    Posts
    69
    Rep Power
    17

    Re: Correct me if I am wrong

    Hi,

    I think you have to check again your readings

  4. #4
    LDK's Avatar
    LDK Guest

    Re: Correct me if I am wrong

    Thank you Chillerman

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Correct me if I am wrong

    Quote Originally Posted by LDK View Post
    The liquid line 32 C and afetr the economizer tthe liquid line is 12 C going to TXV .Before entrying the TXV , liquid line is 14 C , sight glass bubbling .TXV is iceing.

    I have 43 C (1699KPA) at entrying of the dryer
    If I understand this correctly, you have 43C before the drier and 32C after the drier. If so, the drier is plugged.

Similar Threads

  1. The correct way to write CO2.
    By nic_f in forum CO2
    Replies: 5
    Last Post: 09-02-2009, 07:27 PM
  2. Can someone point what's wrong
    By Peter_1 in forum Industrial
    Replies: 30
    Last Post: 22-04-2008, 07:04 PM
  3. Replies: 5
    Last Post: 11-07-2007, 03:06 AM
  4. Whats the correct procedure for R22
    By cold as ice in forum Fundamentals
    Replies: 19
    Last Post: 18-11-2006, 06:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •