    Toshiba VRV



    Hi Guys,
    2 compressors in this unit,is one of them contolled by inverter?how do i go about testing them? is it the same as a electrical motor ?can i put a megger across it? any info please.



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Toshiba VRV

    what are you testing 'for' ?

    you can test a compressor in the normal way for winding condition..
    however remember if you megger the inverter board it will blow..

    comeback and give us a proper description of whats going on here...

    cheers


    richard

  3. #3
    Join Date
    Feb 2004
    Location
    scotland
    Age
    62
    Posts
    15
    Rep Power
    0

    Re: Toshiba VRV

    Sorry mate, the VRV keeps tripping out it`s controlled by toshiba interactive intelligence software ,there are 4 ceiling units connected to it and when i ask it to work hard it goes out on high pressure switch tripped or abnormal inverter fault someone suggested compressor problem????
    Frank McBride.........

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: Toshiba VRV

    is it running in heat or cool?

    bit difficult to diagnose but make sure condenser is clean and filters are clean.

    then fit your gauges and watch the compressor on the hi side -ramp it up till it trips -this will narrow it down to this (providing the hp itself isn't dodgy

    then come back

    alternitively phone toshiba technical when on site and they will talk you through..

    cheers

    richard

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Toshiba VRV

    hi frank,

    I'm not much help in VRV but it looks to me that the compressor is fine, the problem could be, as richard said, dodgy HP control.

    remeber that high presure switch is protecting compressors from drawing high currant.

    overload protecting compressors from high currant or low voltage.

    I suggest from reading only that the problem is elsewhere.

    chemi

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Toshiba VRV

    Not overfilled in the winter?

  7. #7
    Join Date
    Feb 2004
    Location
    scotland
    Age
    62
    Posts
    15
    Rep Power
    0

    Unhappy Re: Toshiba VRV

    Thanks again guys,i`m electrician finding my way so using a set of gauges is not a strong point although i do have them to use if need be ,the unit trips out on both heat & cool but if i switch two of the five ceiling units off it seems to cope!!!
    Frank McBride

  8. #8
    rbartlett's Avatar
    rbartlett Guest

    Re: Toshiba VRV

    get an amprobe on and take some readings -then switch on indevidual units till it trips...can be very difficult confirming inverter drive c.b and /or compressor..

    cheers

    richard

  9. #9
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23

    Re: Toshiba VRV

    High pres cut out, non condensibles come to mind, may be a poor installation

  10. #10
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Toshiba VRV

    To test the inverter, check the noise filter and make sure you have power in and out and check the fuses. Test the resistance in and out of the reactor and make sure that the converter is putting out power to the compressor. I assume it's three phase so check the resistance across the terminals (with the cables removed) it should be the same. If the systems going out on HP them it's unlikely to be a fault with the compressor. It's usually the system failing to get rid of the heat-in other words a condensing problem. Maybe non condensables, faulty HP control, condenser fan etc etc. Check the temps on the pipe in and out of the condenser. This will give you an idea of heat rejection in the condenser. You can check the compressors current draw, but do not put high voltage (such as from a Megger) through the inverter. I don't work on huge amounts of Toshiba VRF, but assume there isn't much product difference from Daikin, Mitsubishi and Hitachi etc

    Regards
    James
    a problem shared is a problem halved

  11. #11
    Join Date
    Feb 2004
    Location
    scotland
    Age
    62
    Posts
    15
    Rep Power
    0

    Re: Toshiba VRV

    Thanks guys ,you have given me plenty to look at ,the system was installed 18 months ago i have about 70 ceiling mounted units & 18 or so VRVs so any info you guys put my way is brill,Tosh warranty is now up so i`m left holding the baby ............
    Frank McBride

  12. #12
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Toshiba VRV

    Quote Originally Posted by frankmcbride
    Thanks guys ,you have given me plenty to look at ,the system was installed 18 months ago i have about 70 ceiling mounted units & 18 or so VRVs so any info you guys put my way is brill,Tosh warranty is now up so i`m left holding the baby ............
    Frank McBride

    ............Toshiba's warranty in the UK is 3 years.

    Why not give them a call?
    ________
    Ford Performance Vehicles specifications
    Last edited by Argus; 07-02-2011 at 08:03 AM.

  13. #13
    Join Date
    Mar 2004
    Location
    australia
    Posts
    25
    Rep Power
    0

    Re: Toshiba VRV

    hi guys,

    sorry to but in but can anyone tell me wat a VRV and a VRF is?

    cheers

    paul

  14. #14
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Toshiba VRV

    Paul, they are both terms for exactly the same thing.

    They mean ?Variable Refrigerant Volume? and ?Variable Refrigerant Flow?.
    The former has been registered as a trade name, I believe, in Europe by Daikin. The latter, VRF, is a generic term for what I am going to describe briefly below.

    In origin it is a Japanese product that consists of a large number of DX indoor units. They go up in multiples, 4, 8 16 even 32 indoor units on one system, or any number to suit in between.

    It can be Cool Only, Heat Pump or simultaneous Heat / Cool where the heat rejected from units in the cool mode is put back into the building instead of being rejected outside. Crazy as it sounds, this is a very viable product in Northern Europe, where many large commercial buildings can be net producers of heat, especially in the central core. They are a serious challenge to chillers in many areas.

    It works with an Inverter driven compressor and the refrigerant is metered to each indoor coil exactly by electronic expansion valves. These systems are capable of huge energy cost reductions if they are designed and installed correctly. Not only that, they are almost infinitely flexible if the building layout or use changes.

    If you want to know more, there are numerous UK web sites detailing their operation mode in more scope.
    ________
    Sparta
    Last edited by Argus; 07-02-2011 at 08:03 AM.

  15. #15
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Toshiba VRV

    Hi Paul

    Basically they are the same thing. Daikin call their system VRV (variable refrigerant volume), and the title is copywrited so all the others have to use the title VRF (variable refrigerant flow). Samsung have their version called a DVM (digital variable multi).

    Each condenser has multiple evaporators. The speed of the compressor is varied by an inverter (except Samsung) to match demand (hence the name).

    Hope this helps
    James
    a problem shared is a problem halved

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Toshiba VRV

    Hi Argus

    On the new Daikin VRV II you can connect up to 40 indoor units to one outdoor unit.

    Marvellous piece of kit. The new VRV II even tells you if it has a refrigerant leak and shuts itself down!

  17. #17
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Toshiba VRV

    if i switch two of the five ceiling units off it seems to cope!!!
    That certainly doesn't seem like a compressor fault or a HP fault.

    Has the system operated correctly in the past? Could the system be incorrectly designed? Has the maximum pipework length been exceeded?

    Do the indoor unit's capacity (index) exceed the outdoor unit's capacity? Post the system details and I'll let you know (model numbers).

    All sorts of questions come to mind.

  18. #18
    Join Date
    Feb 2004
    Location
    scotland
    Age
    62
    Posts
    15
    Rep Power
    0

    Re: Toshiba VRV

    Hi Frank,
    The plot thickens!!!!!!!!! above the ceiling there seems to be some kind of marshalling box with a lot of pipiework looks like solinoid valves opening and closing a low squealling noise ,wonder if one or more of these valves is jamming open or close ,VRV icing up badly at times are heating solinoid jamming?
    Frank Mc Bride

  19. #19
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Toshiba VRV

    Frank,

    It's the multi- controller. It contains all the solenoids and electronic expansion valves for the circuits attached to it.

    It also has a self diagnostic feature on the PCB that will tell you what's wrong with it, but you will need to know what the codes mean.

    If you get the model number and search Toshiba's UK web site you sjhould be able to down load the service manual.

    You are wasting your time without it.

    You could also call Tosh in Leatherhead they should be able to talk you through it.
    ________
    Toyota eCom specifications
    Last edited by Argus; 07-02-2011 at 08:04 AM.

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Toshiba VRV

    If the unit is in heating mode and working hard then you will find that the outdoor unit ices up periodically. This is quite normal. The unit will defrost itself so don't worry.

    What leads you to the conclusion that the system is not working OK? Are the rooms at or near stat set point? Is it just because the system makes a noise?

    VRV/VRF systems have advanced electronic controls and seem not to be working as we usually understand them but 9 times out of 10 they are. Check the basic stuff first - is there a fault code showing on the controllers? can you feel heat being rejected/cool air being discharged? I think more information is needed.

  21. #21
    Join Date
    Mar 2003
    Location
    ireland
    Posts
    6
    Rep Power
    0

    Re: Toshiba VRV

    possibly overcharged, decant entire system and re charge, doing calculations for pipe length. is main run to BC box exceeding maximum allowable length? check all illet/outlet temperatures with the system running at full load.

    on heating, inverter takes control input from discharge pressure transducer to maintain a target pressure, suction pressure transducer on cooling. possibly faulty transducer, run all units flat out on heating and record high side pressure over a period of time, if too high then possibly faulty transducer or outdoor unit board. its also possible that this is happening during heating startup if the EEV at the outdoor unit is not opening quickly enough.
    is the system SHRM or SMMS? silly question but are all the shutoff valves open?

    VRVs are not the easiest thing in the world to diagnose first time (see above list !)

    as ARGUS said, get yourself a copy of the manuals, you might as well be attempting to fix a space shuttle without them.

    hope this helps, best of luck

  22. #22
    Join Date
    Nov 2006
    Location
    kuwait
    Age
    52
    Posts
    5
    Rep Power
    0

    Re: Toshiba VRV

    Hi,
    Normally indoor units are selected for a capacity 130% of condenser in VRV. But, one thing is to be taken care - All in indoor units should not be operated in maximum capacity simultaneously. This is done in locating the indoor units. IDU should be located such that the peal heat load timing should not match. If it happens, that also in peak sumer, the discharge pressure will go beyond the HP switch setting.As the compr tripping is on HP, no chance of any compr fault.
    Other factors such as choked condenser coil, faulty condenser fan, im-proper evacuation, overcharging of refrigerant etc can also lead to tripping of compressor on HP.

  23. #23
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Toshiba VRV

    I hope he managed to fix this unit as the post was dated back in 2004
    Maybe Mr.Mcbride would care to inform!

  24. #24
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: Toshiba VRV

    Quote Originally Posted by frankmcbride View Post
    Hi Guys,
    2 compressors in this unit,is one of them contolled by inverter?how do i go about testing them? is it the same as a electrical motor ?can i put a megger across it? any info please.
    hi frankie...has this system got 2 compressors in the one shell???? if so, problems with those compressors i have come accross.. i recommend checking compressor windings for balance and earth leakage...i came acrosxs alot of earth leakage faults causing internal clixon to be active when voltage is increased from inverter which is in series with a head pressure fault ....why not watch head pressure whilst running and if nothing is abnormal, disconnect inverter compressor and let run on d.o.l..me thinks you need new compressor

  25. #25
    Join Date
    Feb 2007
    Location
    Australia
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Toshiba VRV

    Hi guys new to the scene.
    If its the model i am thinking of the condenser fans are variable speed (inverter). These may not be reaching full speed due to faulty tranducer on HP side of system. Part is in a nice place to change out. Do you have a fault code?.

    Regards Peter.

Similar Threads

  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Replies: 19
    Last Post: 18-10-2010, 02:45 PM
  2. Toshiba Warranty
    By gwilliamson in forum Air Conditioning
    Replies: 1
    Last Post: 17-05-2006, 05:59 PM
  3. Replies: 1
    Last Post: 19-02-2006, 12:08 AM
  4. Toshiba A/C Compressor size
    By Chris2005 in forum Air Conditioning
    Replies: 9
    Last Post: 10-04-2005, 09:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •