01-04-2004, 09:29 PM #1
H/p L/P switch settings
When setting up switches is there is there a method for working out the settings including differential. At present I normally set up H.P. at 300 LP at 10. should this alter depending on the gas.
Regards to the wise ones.
BernardLast edited by bernard; 04-04-2004 at 07:04 PM.
-
01-04-2004, 09:46 PM #2
Re: H/p L/P switch settings
HP/LP Settings should be different depending on gas.
Take R12/R409(FX56) Head pressure should be about 120psi therefore when the system was pressure/strength tested is was probably put upto 150psi max. A HP switch set at 350 would be useless because the system whould blow well before then. Also if these gases were used in a low temp application (Unlikely i know) but the system would stop because the suction pressure would be if anything in a vac.
R404 Head pressure should be about 240psi running so an HP at 350psi would be higher than i would put it (Prob 325 at most)
R22 runs about 190-200 so 350psi also well excessive.
Let us know what kind of equipment and gases you are woking on and i am sure someone will post the OFFICIAL HP Guidelines.
Regards
Raymond
-
01-04-2004, 09:53 PM #3
Re: H/p L/P switch settings
Raymond
Thankyou for your reply:
The one I am most concerned about is R407c.But what you say makes sence there must be a guide or % to set these switches above the hp running pressure.
Thankyou
Bernard
-
01-04-2004, 10:05 PM #4
Re: H/p L/P switch settings
Sorry Bernard,
Got me on that one, never used the stuff yet & my HRP sliderule doesnt show it. If anyone has a list of HP switch settings or wants to put one together i would like to see it
regards
Raymond
-
01-04-2004, 10:12 PM #5
Re: H/p L/P switch settings
One way of deciding on the settings is to work out the condensing temperature at maximum design ambient then add a small overshoot allowance.
The differential should be quite wide to reduce compressor cycling; remember everytime the compressor starts it pumps a bit of oil out, if it doesn't run for long enough then the oil doesn't return.
End result - dry compressor - bang
If there is a continual head pressure problem then it should be investigated and rectified.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
01-04-2004, 10:16 PM #6
Re: H/p L/P switch settings
Hello Brian,
Maximum design ambient, now there is a subject that could take up a lot of space within the forum.
Anyone out there know the head pressures of R407 & R410 & what the HPCO's should be.
Regards
Raymond
-
01-04-2004, 10:18 PM #7
Re: H/p L/P switch settings
hi raymond,
there is no such thing,
what you said before is right for the uk.
over here, R22 works around 250 and more in the summer.
so the settings will be different.
I guess the setting depend on the working conditions.
chemi
-
13-06-2010, 10:06 PM #8
Re: H/p L/P switch settings
1.you take the max avarage ambient for the region,say 35 deg.
2.take condensor td,say 15k.
3.add 5psi for safety
add 1,2 and 3 =35+15+5=55 degrees. this temp should match the pressure on hp gauge.
That applies to all gasses
Similar Threads
-
flow switch connection
By afeef in forum The Trail of TearsReplies: 18Last Post: 23-12-2009, 06:55 PM -
Supermarket Refrigeration System's Settings
By monsker in forum Supermarket RefrigerationReplies: 8Last Post: 10-04-2006, 02:18 AM -
RCV and HIGH PRESSURE SWITCH
By abbasi in forum FundamentalsReplies: 3Last Post: 22-03-2006, 08:51 AM -
shower switch fault !
By Krups in forum ElectricalReplies: 10Last Post: 19-10-2005, 09:10 PM -
Oil Pressure Switch
By Abe in forum CommercialReplies: 9Last Post: 15-03-2003, 11:18 AM