Results 1 to 20 of 20
    Jul 2008
    London
    848
    largish freezer room
    we are hoping to tender a 20 x 20 x 6 m freezer room and we would like to give the client something to contemplate.
    So as it's a clean sheet operation we'd like to recommend things like (say)
    screw compressors with inverters
    floating head
    heat recovery for water/underfloor heated by heat recovery
    recommended insulation thickness?
    etc etc
    Anyone got any great ideas we can work on
    Multisync
    London
    Re: largish freezer room
    Good quality air lock type access, if you have the room for it.
    For your own benefit - design it around the need for maintenance.
    Jul 2008
    London
    848
    Care to expand on the first one and the reasons why?
    I suppose 'air lock' may be overkill but thinking of keeping the inside air in and the outside out.
    It all helps to maintain conditions and can hold down running costs if you're not losing temperature through the access points.
    The design depends of course on whether you need vehicle access or not
    Aug 2005
    5,302
    Absolutely right.
    Sooner or later this will need service.
    The air infiltration through the doors can be huge. Anything you can do to limit this might allow you to reduce the total installed refrigeration capacity.
    Jan 2009
    Australia
    108
    Internal Dehumidifiers work well at keeping down the frost buildup. These a company here in Queensland who are using cascade CO2 systems in large low temp rooms which are high power, low energy and are getting good results. If you want to know more I'll shoot over the contact details.
    Jul 2008
    London
    848
    Would we be able to use a Daikin convipak thingy ?
    India
    688
    Dear Scramjetman
    Can you post more details on that pl.
    Jan 2009
    Australia
    108
    Contact me at richard@enviroenergysys.com and I'll forward the info you need.
    Jul 2008
    London
    848
    Okay, been to site -roughly 3500 sq ft of freezer.We now are trying to find out about inverters and electronic valves and controls etc. However this seems slightly out of the range of the std wholesalers
    I guess we are after 'supermarket' level of kit and control. So we need suggestions as to where/who we should contact for the whole refrigeration 'pack'
    Aug 2005
    5,302
    Quote Originally Posted by multisync
    You are getting into an area where a highly specialized factory supplied system is required or one that is custom engineered and built from individual components by someone other than a manufacturer (a contractor perhaps?).
    Feb 2006
    derbyshire
    610
    artic circle down hereford,or accross to you they were developing there own inverter semi,s a few years ago so i would hope there ready for sale by now,there bussiness in building custom packs but you will be a lucky chap if you can price on what you want to in this climate,best of luck ,
    Jul 2008
    London
    848
    Of course price is an issue but as the customer spends 2.5k per month on leccy at just one of the two sites he's shutting, we hope to convince him of the old adage "Cheap to buy -dear to own"
    An all singing all dancing may cost him 20%+ more but save 30% on running costs payback in less than 5 years is not out of possibility.
    I suspect the supermarket bods should be up on where the market is going. We will shy away from CO2 as we do not have sufficient experience of it and if it goes wrong we would be bankrupted by penalty clauses
    scotland
    756
    i install rooms of this size all the time in supermarkets for ease if i were you i would ask your local climate centre to quote you on 1 of there own built lt scroll packs they come with 4 zf18 scroll compressors and you would probally need 3 ks70 coolers or 2 km95 coolers these can be controlled through simple rdm coldroom panels which are very good they are cheap and reliable and can be configured for electronic or tev valves going for something like this is easy to install very cheap to run and very easy to fix when when it breaks also parts are easy to find.
    Jan 2009
    58
    161
    Talk to Tony Mills at Space engineering. They do scroll packs utilising subcooled liquid, if you choose Danfoss control systems then you can have floating suction and discharge. We use them on Tesco and have proved they save at least 30% energy over a standard scroll pack!
    Regards.
    Jul 2008
    London
    848
    Quote Originally Posted by Silhouette View Post
    Regards.
    Sounds great but he's not going to want to help us out without taking over the job now is he?
    Jan 2009
    58
    161
    We Supply packs to independants!!
    Jul 2008
    London
    848
    Quote Originally Posted by coolhibby1875 View Post
    great I shall contact them for their thoughts. Someone else mentioned Hubbard.....?
    Jul 2008
    London
    848
    Mel,
    Is he in Bristol -or do you have an email addy for him
    Jan 2009
    58
    161
    tony.mills@space-engineering.co.uk he resides at Bristol Templemeads office and is the pack production manager. If you call Space engineering systems main number and ask for Tony Mills they will put you through. 0845 602 0670
  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Last Post: 09-08-2010, 12:10 PM
  2. Cold room/ Freezer combo.
    By dogma in forum Commercial
    Last Post: 09-11-2008, 02:25 PM
  3. Freezer Room Defrost
    By Samarjit Sen in forum Commissioning
    Last Post: 21-06-2007, 06:16 AM
  4. Misa Kit Freezer Room
    By Abe in forum Commercial
    Last Post: 03-01-2007, 09:04 PM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Last Post: 22-04-2005, 05:58 AM