Thread: Sabroe Compressor
09-01-2009, 07:46 PM #1
Sabroe Compressor
Hi All
I have a faulty oil differential transducer on a Sabroe compresser. HPC series. What i would like to know is, the transducer under pressure, ie, will i lose some of the charge if i dont pump the system down when i remove it. I ask the question because a sub-contracting engineer told me a temperature probe, PT100, on the same system was under pressure. However when i removed it due to a fault i found it wasnt under pressure.
09-01-2009, 09:04 PM #2
Re: Sabroe Compressor
Hi mish.
To be fair to the contractor it can depend upon which model of compressor you have.
You can find temperature probes which are within a pocket or in direct contact with the gases that are being measured.
Therefore they can be termed as in direct or indirect contact.
But an oil pressure transducer will always be in direct contact.
And yes it would pay to pump down the compressor prior to transducer removal.
As even if you have 0 oil pressure.
There will always be system pressure within or behind it!
If you understand what I mean?
Besides which you then are able to remove any air introduced prior to re-instalment!
09-01-2009, 10:41 PM #3
Temperature probes may be either located directly in the piping or indirectly in what's called a thermowell.
Here's a link.
http://www.omega.com/toc_asp/framese...=260_Commodity
The thermowell isolates the probes from the pressure, so where these are used it is safe to remove the temperature probe.
Under NO circumstances should a pressure transducer be removed before de-pressurizing the piping where the instrument is located!If all else fails, ask for help.
10-01-2009, 08:50 PM #4
HI
The pressure transduser on a sabroe is always under pressure
11-01-2009, 04:22 PM #5
Hey thanks for the advice all...much appriceated!!!!
Sabroe Co2 compressor
By Sturt in forum Old Refrigeration PhotosReplies: 5Last Post: 19-02-2010, 03:29 PM -
LG heat pump problem
By back2space in forum Heat PumpsReplies: 132Last Post: 01-02-2009, 11:23 PM -
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 09:27 PM -
Compressor pumping efficiency
By shogun7 in forum FundamentalsReplies: 0Last Post: 25-02-2004, 10:50 PM