    Anyone familiar with samsungs terminalogy and electronics?



    Samsungs use a part they call a NTC, it looks like a huge varistor and is inline with the power circuit running the compressor, capacitor and soft starter.
    They often just blow when the run capacitor dies
    They not only use them on their PCBs but also on flying leads between the run capacitor and neutral.

    Anyone know what they are and where to get them from?
    I'm trying to repair them in the field rather than order parts from samsung (which always takes months) when I come across ones blown just because the run cap dies?

    Here's a picture, I'm aware it has CNT written on it, but it is refered to in all the samsung manuals and printed on the PCBs as an NTC device.
    Attached Images Attached Images
    Last edited by paul_h; 23-12-2008 at 08:21 AM.



  2. #2
    Join Date
    Jan 2007
    Location
    UK
    Posts
    24
    Rep Power
    0

    Re: Anyone familiar with samsungs terminalogy and electronics?

    These are thermistors. NTC stands for Negative Temperature Coefficient. They are thermally sensitive resistors which change resistance due to ambient or internal temperature. They usually have a rating at 25c marked on them.

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Cheers.
    Do you know why samsung use them in the compressor power circuit(never seen them in any other brand), why do they usually explode when the run cap dies?

  4. #4
    Join Date
    Jan 2007
    Location
    UK
    Posts
    24
    Rep Power
    0

    Re: Anyone familiar with samsungs terminalogy and electronics?

    You will find them on PCB's from LG, Haeir etc, although usually smaller. They blow due to internal rise in temperature.

  5. #5
    Join Date
    Mar 2008
    Location
    Australia
    Age
    63
    Posts
    6
    Rep Power
    0

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Quote Originally Posted by paul_h View Post
    Cheers.
    Do you know why samsung use them in the compressor power circuit(never seen them in any other brand), why do they usually explode when the run cap dies?

    They are used to limit start up current. The current causes the thermistor to heat up and the resistance decreases. By the time the resistance has dropped, the back emf in the rotating compressor should have reduced the demand for current.

    If the capacitor has failed and the compressor does not start, the current increases as the thermistor heats up and eventually overloads it.

    The big problem with replacing them is finding a suitable replacement. I have started collecting old pcb's as a source of spare parts.

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Thanks all for the explanations.
    I'm still looking for some electronics/electrical place to supply them, as I said samsung are slooooow for parts.

    Thanks stev, i've done the same, saving PCBs for capacitors, fuses, relays and varistors etc.
    Though it's hard to find a samsung PCB that hasn't got these NTC things blown, these and the large ceramic resistors are the first thing to blow, so even though I have a bunch of PCBs, I don't have these and will never have any of these things as spares unless I get a supplier of new ones.

  7. #7
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    paul

    try dropping these people an email

    wrong side of the water but iam sure they would ship

    http://www.willow.co.uk/index.html
    Paul


    "KEEP IT COOL"

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Thanks.
    I guess I have to work out samsungs specs, then I'll look at trying to find a supplier.
    Now I know what I'm looking for and why it's there now
    Do they mainly get used in soft starters?
    Just asking because samsung are the only manufacturer that make their own soft starters for our market and that use NTC protection.
    Panasonic and other brands used locally made retrofitted soft starters (quick start and hyperstart) that don't use NTC protection. Fujitsu made their own soft starter for our market that had no NTC either (unless it was internal to their little black box).

    Do you guys have soft starters and NTC devices in samsungs? I've always heard soft starters on small a/cs are unique to only a few countries like australia and france, I don't know if you have them there.

    edit:
    Soft starters a real PITA and very common faults down here.
    It's fun when you have a burnt out one on a POS generic made in china brand that you don't have a parts supplier for though.
    I've got a "Blueway" in my file that needs a soft starter PCB too...
    Might just chuck in a locally made hyperstart like sharp and panasonic use for that blueway.
    Last edited by paul_h; 24-12-2008 at 12:33 PM.

  10. #10
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Quote Originally Posted by paul_h View Post
    Thanks.
    I guess I have to work out samsungs specs, then I'll look at trying to find a supplier.
    Now I know what I'm looking for and why it's there now
    Do they mainly get used in soft starters?
    Just asking because samsung are the only manufacturer that make their own soft starters for our market and that use NTC protection.
    Panasonic and other brands used locally made retrofitted soft starters (quick start and hyperstart) that don't use NTC protection. Fujitsu made their own soft starter for our market that had no NTC either (unless it was internal to their little black box).

    Do you guys have soft starters and NTC devices in samsungs? I've always heard soft starters on small a/cs are unique to only a few countries like australia and france, I don't know if you have them there.

    edit:
    Soft starters a real PITA and very common faults down here.
    It's fun when you have a burnt out one on a POS generic made in china brand that you don't have a parts supplier for though.
    I've got a "Blueway" in my file that needs a soft starter PCB too...
    Might just chuck in a locally made hyperstart like sharp and panasonic use for that blueway.
    PM me as we know i'am samsungs UK best friend,i will email them and ask your questions
    Paul


    "KEEP IT COOL"

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Quote Originally Posted by paul_h View Post
    Just asking because samsung are the only manufacturer that make their own soft starters for our market and that use NTC protection.
    Is there any regulation in Australia forcing use of soft starter? I don't see any reason for soft starter in small domestic split systems. And I could tell at least one against.
    I would bypass that circuit if compressor relay is capable to withstand 5-6 times FLA, or install one relay which is capable.
    Last edited by nike123; 25-12-2008 at 06:59 AM.

  12. #12
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Yes it's regulations that units higher than 6kw cooling capacity (ie. 2.5HP+ compressor motors) have soft starters here.

    That's why I was asking is soft starters are commonly used in european splits, as I've heard it's only australia and a couple of other countries they are regulated to use them.

    Some a/cs just use a small PCB for soft starters, or a small box.
    Others like larger samsungs have a huge collection of relays and resistors dedicated to it which takes up the whole space above the compressor, a 15cmx20cmx30cm box.
    Attached Images Attached Images
    Last edited by paul_h; 25-12-2008 at 08:54 AM.

  13. #13
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Hi Paul,
    Merry Xmas to anyone that is online, here in the UK almost every single split that is sold has an inverter driven compressor, this has been the case for a few years now.

    Regards
    El Padre

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Quote Originally Posted by paul_h View Post
    Yes it's regulations that units higher than 6kw cooling capacity (ie. 2.5HP+ compressor motors) have soft starters here.
    Do you all have maxigraph installed on electric consumption counter? We have here current limitators ( in fact very slow fuses) who easyly overcome starting current from compressor of domestic split systems.
    Last edited by nike123; 25-12-2008 at 10:04 AM.

  15. #15
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Anyone familiar with samsungs terminalogy and electronics?

    Quote Originally Posted by El Padre View Post
    Hi Paul,
    Merry Xmas to anyone that is online, here in the UK almost every single split that is sold has an inverter driven compressor, this has been the case for a few years now.

    Regards
    El Padre
    Yes, that is the case here too, inverters became an option many people started to use about 4 years ago, and now, almost every single split is an inverter.
    But that means a/cs up to about 4 years old, some were not inverters. And a/cs more than 5 years old, most were not inverters.
    So there's a lot of soft starters out there to repair.

    Nike, no meters or maxigraph or any other reasons why we have soft starters, they are just required by law.
    1.10.1.4 Limitations - Motors

    The starting current of motors, which is significantly higher than running current, can cause a significant fluctuation of the supply voltage. Motor installations with associated starting/control devices must be designed to ensure that the starting current will not cause the reduction in voltage measured at the point of supply to exceed 5% for more than 20 milliseconds.

    Table 1.3 provides a general guide for different types and uses of motors.

    In areas limited to 230/460 volt supply, contact the electricity distributor for advice on special supply arrangements.

    Table 1.3: Limits of Motor Starting Currents
    Motor Type
    Starting Current (A)
    Single Phase, 230V
    45A
    Last edited by paul_h; 25-12-2008 at 10:38 AM.