    compressor problem



    semi hermetic compressor won,t run
    3 phase supply is there,windings are not open circuit, klixon has continuity, control circuit is o.k and unit is calling for refrigerant.no current being drawn why won,t it run on artic circle guardion condensing unit



  2. #2
    shogun7's Avatar
    shogun7 Guest
    bernard
    You never mentioned if you had voltage?
    Roger

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    compressor problem

    sorry shogun 415v there

    ps I,m a pajero man myself

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    I it a Maneurop compressor with a clixon in the strat point?
    Did you measured 3 times same resistance?

  5. #5
    shogun7's Avatar
    shogun7 Guest
    Silly question but are you sure you have refrigerant in this system? and do you have a LP control You didn't mention if you put gages on and checked the pressures. If you close the contacter by hand for an instant will the comp run?(Stand aside)

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hi bernard,

    never ever close contactor contacts by hand!!!!

    check tention on compressor points.

    compressor can be stuck.

    what kind of startihg device do you use?

    try to change direction of rotation.

    chemi

  7. #7
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    compressor problem

    Its an artic circle guardian condensing unit. the control circuit is fine the contactor is energising and both condenser fan come in.the other compressor in parralel is operating fine gas pressure ok. manufacturer could not give me a technical answer to this but told me the compressor had failed. I replaced it and the system now works fine . as my children would say BUT WHY !!!!!!

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Was it a hermetic or a Maneurop?

  9. #9
    rbartlett's Avatar
    rbartlett Guest
    http://212.67.202.149/~acl/

    no artic use semi's of their own design

    marc knows them at the factory pretty well -as he has 'helped' them out a few times and done some commissioning work too

    however their quality control isn't 'err too great' and quite a few units come shipped with their own 'test the commissioning engineer' problems -mainly wiring errors

    cheers

    richard

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hi bernard.

    in that case, the clixon must have failed.

    its located inside the windings, and when open at high temp or failure, disconnecting the three phases,

    and thats why you get 440V reading on the contactor outlet, but machine will not run.

    chemi