    APAC 65KW Ducted



    Merry Xmas All
    i have an old apac 65KW 2 Stage A/C Approx 32.5kw per stage recently burnt out Recip compressor...Manuerop mt 161... replaced with manuerop Scroll compressor SCZ 161...was told difference in capacity was approx 2KW...replaced burn out drierin suction line .. found leaks at suction line solenoid(Capacity Control???)removed solenoid alltogether. evac and charge and appeared to have failed tx (Danfoss TE5 )Replaced power element made no difference BTW suction pressure was below 200KPA (R22) found orifice size to be #2 should be #3 .... Changed orifice to #3 Suction pressure came up to 220KPA Disch\arge pressure @ 1600KPA ***the system is 2 stage. stage 1 is the concern ..have system set up so stage 2 still runs when stage 1 in fault. TX Valve is set up correctly (26mm spring length of cage)replaced power assy again in case new one faulty ,system still the same ... at my wits end HELP!!! (also coil restriction is 100Pa if this helps )



  2. #2
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: APAC 65KW Ducted

    hello icemakerman, any liquid line driers in the system if so are they blocked. haver you tried adjusting tx valve?

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: APAC 65KW Ducted

    So you replaced the suction burn out drier? Was there already on in there?
    Just asking because if it's had previous burnouts and welding etc, may have a blocked liquid drier or strainer.
    Besides that: airflow? pressures and temps at evap, compressor, before TXV etc?

  4. #4
    Join Date
    Dec 2008
    Location
    Lebanon, PA
    Posts
    25
    Rep Power
    0

    Re: APAC 65KW Ducted

    I agree,
    Blocked liquid line filter, after a burn out replace all the filters, that's been a policy that's worked out well enough for me.

  5. #5
    Join Date
    Dec 2008
    Location
    Australia
    Age
    61
    Posts
    44
    Rep Power
    0

    Re: APAC 65KW Ducted

    yeah ok guys.. thanx for all the suggestions did replace suction burnout drier core did try adjusting tx valve did try replacing liquid line drier also. on investigation found condensor coil to be badly choked with 15 years of build up(unit is located at local aluminium smelter)causing high discharge pressure and also evaporator coil restriction as i said was 100 pa so evaporator is also choked causing unusual low suction and thus appearing like restriction in flowof refrigerant. Have added refrigerant to acheive some subcooling to compressor discharge is at 2000kpa but compressor is not drawing excessive amps so should last till unit replacement,as money has been set aside to replace next year, as i said thanx for the input

  6. #6
    Join Date
    Dec 2008
    Location
    Lebanon, PA
    Posts
    25
    Rep Power
    0

    Re: APAC 65KW Ducted

    That choked? Assuming yuo meant the outside of the fins then. Got access to a pressure washer? Blow it down, then to really make sure it'll be okay run some denatured alcohol through it. Be careful, watch out for an ignition source.

Similar Threads

  1. Daikin Ducted Commission Probs
    By jdkmj in forum Technical Discussions
    Replies: 6
    Last Post: 23-11-2008, 08:21 PM
  2. Replies: 1
    Last Post: 18-06-2008, 06:05 PM
  3. Carrier ducted unit
    By Andy AC in forum Air Conditioning
    Replies: 10
    Last Post: 23-10-2007, 10:05 PM
  4. Ducted Split Units
    By harsen in forum New to RE
    Replies: 2
    Last Post: 06-02-2007, 05:45 PM
  5. LG ducted split
    By Abe in forum Air Conditioning
    Replies: 20
    Last Post: 08-06-2005, 07:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •