    Ic 901



    Frosties

    Quick one. Has anyone see 99 come up on an Eliwell controller. We have tried changing from PTC to NTC no change. Controller damaged?



  2. #2
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: Ic 901

    What happens when the probe is disconnected,does it show a probe fault or just stay at 99?
    If it ain't broke, it doesn't have enough features yet.


    Damo

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Ic 901

    Basic I know but have you tried powering down and then powering back up?
    Just to confirm you don't just have a confused display.
    Pretty much what chunk is suggesting!
    Grizzly

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Ic 901

    Fuair.
    Please read the bottom line of the attached useful Eliwell Controller instructions.
    Grizzly

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Ic 901

    Quote Originally Posted by fuair View Post
    Frosties

    Quick one. Has anyone see 99 come up on an Eliwell controller. We have tried changing from PTC to NTC no change. Controller damaged?
    Back again, it is just possible that you have the keyboard LOC on as you can still access the programming mode via the set button.
    whilst viewing the set point. Which incidentally has a maximum value of 99 (sound familiar).
    Please read the attached info and hopefully all just may be revealed? (see bottom L/H of first paragraph)
    Grizzly

  6. #6
    Alan Twomlow's Avatar
    Alan Twomlow Guest

    Re: Ic 901

    This problem occurs when the controller is expecting to see one type of sensor input (i.e. NTC) and another is connected (i.e PTC). You can change the probe input type in folder CnF, parameter H00 but you MUST then power down the controller and then restart it, otherwise it will not accept the new probe input. It's simple when you know how.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Ic 901

    Quote Originally Posted by Alan Twomlow View Post
    This problem occurs when the controller is expecting to see one type of sensor input (i.e. NTC) and another is connected (i.e PTC). You can change the probe input type in folder CnF, parameter H00 but you MUST then power down the controller and then restart it, otherwise it will not accept the new probe input. It's simple when you know how.

    Welcome to the forum Alan.

    You are obviously a well informed Engineer?
    I am sure there will be more questions of you!
    Grizzly

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ic 901

    Ditto that, welcome to the forum Alan, we hope that you enjoy it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Ic 901

    Only took him 8 years for his first post, see you again Alan in 2017.
    Grumpy men live longer

  10. #10
    Alan Twomlow's Avatar
    Alan Twomlow Guest

    Re: Ic 901

    Quote Originally Posted by LRAC View Post
    Only took him 8 years for his first post, see you again Alan in 2017.
    I shall post again where I feel I am needed no doubt...