This may be a silly q but i have recently started working in commercial refrigeration and am wonder if any one has any helpful info on trouble shootin tx valves, i have a few systems running with full sight glasses and still not floodin evap correctly not sure if i may have restriction or if orifice needs changing or even checking and adjusting super heats i have many years expirence in domestic refrigeration and whitegoods so if any q's on these dont hesitate also ill be askin on pressure controls soon but more interested in txv's at moment thanks guys hope to chat about things soon
-
13-11-2008, 09:01 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Trouble shooting tx valves
Last edited by nike123; 13-11-2008 at 09:16 AM.
-
13-11-2008, 02:16 PM #3
Re: Trouble shooting tx valves
Last edited by Gary; 13-11-2008 at 02:20 PM.
-
13-11-2008, 02:30 PM #4
Re: Trouble shooting tx valves
tech tim,
what is the application,btuh rating of equipment,system pressure and txv rating?
regards,abet
-
13-11-2008, 11:04 PM #5
Re: Trouble shooting tx valves
Thank for links very helpful
-
13-11-2008, 11:07 PM #6
Re: Trouble shooting tx valves
Thanks Gary for your reply that has seemed to be the case after running 24hr or so evap seem alot better thanks again
-
13-11-2008, 11:13 PM #7
Re: Trouble shooting tx valves
not real sure on tech specs i have been workin on various displays and drink fridges mainly, most jobs have been compressor changes but i havnt had much to do with tx valves etc and have noted coils flood differently to domestics wich is my forte... im wanting to leave that behind and move on to commercial/ industrial all in good time i guess thanks for your replie
-
13-11-2008, 11:32 PM #8
Re: Trouble shooting tx valves
Direct expansion evaporators are NEVER flooded (on purpose).
The inside of the evaporator coil will have approx. 80-85% of it's internal area wetted by liquid refrigerant. The last 15-20% of the coil surface area is used for superheating the refrigerant vapor.
If you start a system up warm, the superheat will be higher than normal. Do not adjust the TXV during this time.
Wait until the temperatures are down to the expected range and then check the superheat.If all else fails, ask for help.
-
24-01-2009, 05:00 PM #9
Re: Trouble shooting tx valves
excellent posts with links thanks guys helped me work out why my 404 walkin freezer isnt getting the right superheat after compressor and evep change
-
01-02-2011, 03:39 PM #10
Re: Trouble shooting tx valves
its very wrong and sily to adjust the txv. the txv is pre-set by the factory
now you have big problem you compressor will damage and txv need to replace good luck
-
01-02-2011, 04:49 PM #11
-
01-02-2011, 05:13 PM #12
Similar Threads
-
LG split system fan cont. trouble shooting
By ianv in forum Trouble ShootingReplies: 9Last Post: 01-02-2011, 03:31 PM -
Contactor service and trouble shooting
By zerodegreec in forum ElectricalReplies: 13Last Post: 16-09-2008, 12:58 PM -
Trouble Shooting
By Vincent Yu in forum FundamentalsReplies: 20Last Post: 22-11-2005, 02:04 PM -
Trouble shooting Guide
By raghu in forum Trouble ShootingReplies: 2Last Post: 21-05-2005, 03:03 PM -
24V trouble shooting
By Frig Pig in forum Trouble ShootingReplies: 9Last Post: 09-01-2004, 05:58 AM