    HI, I would like to know one very important thing that " if im using 4.9 MM fin & tube type cindensor for a low temp application (Freezer). but after comp. discharge i use a 6.35 mm 200 mm long tube to joint condensor. What will the effect bocoz of 6.35 tube joint on the system. when i use i found that tamp. is taking more time then normal. pl. explain what is it ????

    Thanks
    Last edited by chillin out; 09-11-2008 at 08:34 PM.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Technical Question re freezer

    effect should be null if you did all ells properly, ie: sheilding gas, deburring, vacuuming to 200microns or lower.

    I would wager your issue is a thermal one, ie; Unbalanced system.

    That or charge issue, You should perform an audit of the system, good learning tool.

    Air in, air out, coil DT, SH, SC of the evaperator & condensor coils and this will tell you how they are working

Similar Threads

  1. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  2. Freezer efficiency questions
    By M_Q in forum Fundamentals
    Replies: 8
    Last Post: 20-03-2007, 04:38 PM
  3. Technical question
    By SIGNSTU in forum Trouble Shooting
    Replies: 7
    Last Post: 11-02-2007, 01:26 PM
  4. A question about walk-in freezer flooring
    By kengineering in forum Commercial
    Replies: 3
    Last Post: 26-01-2006, 12:34 AM
  5. A question about walk-in freezer flooring
    By kengineering in forum Commercial
    Replies: 0
    Last Post: 25-01-2006, 01:35 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •