Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
check the heater kliksons or the smv module. the easiest way is to disconnect the loads then slowly plug them in until u blow a fuse.
-
04-10-2009, 07:20 PM #3
-
05-10-2009, 04:04 PM #4
-
30-09-2009, 05:51 AM #5
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I am having a problem with a TK CF-2 M39 container unit that was built for Crowley. Software Rev 0, 08/95 It operates on R404a not 134a, so because of the higher pressure there is no liquid line solenoid for pumping down when the unit is in heat.
During the defrost cycle the compressor, evap fans, and the condenser fan should stop, and the heater coils come on. The problem is that the compressor is not turning off but the condenser and evap fans do, as they should. So the unit goes out on a code 10 and 40
(40, Pump down terminated on time limit, does not apply to this unit, but its still coming up.)
The relays, wiring, and contactors are all good. The unit works good except for on the defrost event.
When put into a manual defrost with the condenser fan running, the compressor and fan continue to run, then shut off together and the defrost is completed successfully.
When put into a manual defrost when the condenser fan is in an off cycle, the fan stays off, but the compressor stays on, that is when the unit goes out on high head.
???????????????????????????????????????????????????????
-
02-10-2009, 07:07 AM #6
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey M L CA ... sounds like you need to wire your condenser fan to run all the time. that should be fine with R404a as you needed the cycling action with R134a to keep the head pressure up in cold ambients.
the reason its tripping is cause it wants to pump down on defrost but because the fan is off it builds head and trips fast even before it can shut off. you may have a problem with the cycle switch as it should cut in on a rise in pressure. i have seen before that the compressor contactors stick and work erratically at best. we always lube those contactors.
-
04-10-2009, 07:45 PM #7
-
05-10-2009, 12:01 AM #8
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
yes it could...it is hard to help a guy over the internet isnt it...the best is when they say its messed up but the pressures are "good" that is funny sh@t!!!
-
05-10-2009, 03:15 PM #9
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
18-11-2009, 02:26 AM #10
Request Service Manual Reefer Container "DAIKIN" LXE 10 D
Dear Reefer Mechanic,
Would you like to sent me Service Manual / Operating Manual of Reefer Container "DAIKIN" LXE 10 D ?
My Email Address is tri_ardi@yahoo.com
Best Regards,
Triardi S.
-
03-01-2010, 02:20 AM #11
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have an old carrier 511-331. Its not modulating at all and also seems to be turning on only when the return comes 1 degree over set point and will go down 4 or so degrees under setpoint. Now I havent spent much time on it but have tested power coming to the plug connected to the stepper motor..I have voltage coming through on all 4 lines.. Should only have power on A/B or C/D at one time as A/B open and C/D close it if my memory serves me correctly. So that tells me the stepper motor itself is not the issue, however does this mean somehow it is the microlink or could it be the power module or even something else? just trying to get another opinion as it is a leased box and I cant just start changing random parts. P.S I did check to see if quest software was on this box and it is not.
-
10-01-2010, 05:22 AM #12
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey 1612
check for broken wires behind the compressor and suction valve. they rub on the back wall sometimes. also the drive module or if its an APL the emergency module fails. if it has an emergency module remove it and plug into the SMV directly
-
11-01-2010, 01:43 PM #13
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
good day evey body .
i look for some advice from the refrigeration-engineer experiance.
me issus is i can found the stare cool reefer unit softwear to import the data logger from this unit..
please advice .
badilou.nabil@yahoo.com
-
02-10-2009, 06:54 AM #14
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
also i have seen the cool light in the display do funky stuff when it shorts
-
07-10-2009, 08:25 PM #15
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Good day.
i'm a biginner technician in reefer side.i want to bay some data retreive connector .but i have problem to found them ...
can some body assist.
badilou.nabil@hotmail.com
-
08-10-2009, 04:31 AM #16
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
everybody,
sorry, wrong post yesterday
-
21-12-2009, 08:44 AM #17
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
pak teguh...
punya softwere untuk daikin, \tk, mitshubisi.
kalo ada boleh untuk di share ke saya
terima kasih
-
26-02-2010, 07:59 PM #18
-
27-10-2009, 06:14 PM #19
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Does anybody have documents about general principles of reefer's control system and how it designed? Information about connection of sensors,cable diagrams and repair manuels would hellp me too, Thank you..
-
03-11-2009, 07:09 PM #20
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
........................
Last edited by reefermechanic; 27-02-2013 at 08:56 AM.
-
31-10-2009, 01:31 PM #21
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a carrier 511-362 thats going off on Alarm 15 but that alarm does not appear on the list of alarm codes on the reefer or in the manual that I can locate...if you know what this means let me know. I'm a newbie and working by myself and don't really want to call someone else in if its just something stupid.
-
31-10-2009, 10:09 PM #22
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
02-11-2009, 07:37 AM #23
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
The latest SW ver. is 5146.
-
02-11-2009, 09:23 AM #24
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys,
I am new to this site. I have 2 faults codes on sr-2 alarm window: 4 and 204. I found a plastic back stuck in evaporator so it was preventing airflow. I fixed but need to reset these codes. Can anyone pls help.
Thanks
Jesmond
Rig19 Electrician
-
09-11-2009, 08:17 AM #25
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi
good day
i want to know aboutthermo king reefer unit on message (quest not allowed by timer). can u explain me and how to clear this message ?
thanks you
pyae
-
09-11-2009, 09:49 PM #26
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.............................................
Last edited by reefermechanic; 27-02-2013 at 09:00 AM.
-
06-12-2009, 01:58 AM #27
To ppsmtu - re QUEST
Hi, you shouldn't need to clear this. Quest is a power saving initiative. Starcool and ThermoKing also use it, Daikin call it DTMS2.
It is exactly as you state "a message". It is telling you that the power saving mode (Quest) is currently not active due to a controller initiated time delay.
As per Reefermechanic's menu picture, it is in the MISC sub menu Under STATUS.
Quest should be left to do what it is supposed to, and only turned off if you have a very good reason :-)
"QUEST power-saving mode is a software-based control option for Carrier Transicold refrigeration units that intelligently cycles refrigeration on and off based on temperature limits designed for specific perishables. It can cut energy requirements for refrigeration by up to 50% while also reducing power-related emissions."
-
11-11-2009, 09:03 AM #28
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I forgot my unit its a carrier ultima53 year 2000
-
11-11-2009, 09:37 AM #29
-
24-11-2009, 07:36 AM #30
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear bro...
When i was doing pti (thermoking unit,magnum), alarm 115 and 116 were come out.it does mean sensors faulty but when i check connection and ohm,showing that all in good condition (2000 ohm) please help me how should do?
-
26-11-2009, 03:23 PM #31
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.....................
Last edited by reefermechanic; 27-02-2013 at 09:00 AM.
-
02-12-2009, 06:56 AM #32
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Sorry for late reply,mate ! I haven't try to change yet coz i haven't spare part yet but i'll be change return air sensor and reply you no sooner.
Thank you so much for your reply.
-
03-12-2009, 04:27 AM #33
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thanks a ton. It's really worked!
When i was changed return air sensor , the unit is ok and pti pass.....i am quite curious coz the measure the value of ohm is nothing different with the old and new one sensor..? ?
-
03-12-2009, 04:33 AM #34
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, banana
Try icebath calibration
-
28-11-2009, 10:53 PM #35
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HAY ALL,
i am technician in the reefer , pls i have probleme with t.KING ( quest allowed) i want to clear it but i need help .
BESTB REGARD
-
29-12-2009, 11:02 PM #36
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
note that it's no alarm ,i thinc sae tect reefer play in cofiguration i check and i bac whit good ansower. tnks/reefer sup
-
29-12-2009, 11:03 PM #37
-
25-12-2009, 10:50 PM #38
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please i need manuel for trailer theroking ANYONE CAN HELP ME SEND IT TO ZAHERADIDAS@HOTMAIL.COM
-
30-12-2009, 02:06 PM #39
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic ,can you advice me on truck unit - T/K Spectrum MT ?
-
30-12-2009, 02:12 PM #40
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
PM me .tq.
-
05-01-2010, 06:34 AM #41
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
dear all;
first happy now year;i have reefer daikin with AL :d301;but i dont new the solution,plz help me urgently
-
21-01-2010, 12:41 PM #42
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi
I need 2 manuals for these equipments:
ThermoKing MDII-MAX
Carrier Mistral 800
please send it to nunovgato at gmail.com
Thanks
-
04-02-2010, 03:53 AM #43
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
alguien en español por favor nesesito datos diagramas de carrier intercambio informacion tengo todo de thermo king grasias ggeras@hotmail.com
-
04-02-2010, 05:58 AM #44
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Climo-tecnica,
Could you speak in English?
-
04-02-2010, 06:05 AM #45
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Ci 1612,
I think you should check CD18 CD20 and CD34 to verify the setting of configuration, software versions and Economy mode.
-
04-02-2010, 06:25 AM #46
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Starezone,
Please receive email for software.
-
05-02-2010, 05:34 AM #47
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, reefermechanic
Im Dante, can I charge a Carrier reefer with 404a its present refrigerant is 134a?....Pls. give me more info about this. Thanks
Dante
-
08-05-2010, 01:53 PM #48
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Have sombody experiance whit a diesel/elektical reefer
45ft slx 300 from themo king
thanks
-
24-05-2010, 11:24 AM #49
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please help me.
I need Thermoking ThermoGuard MPIV User manual
-
24-05-2010, 11:54 AM #50
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM