04-10-2009, 07:45 PM #101
-
05-10-2009, 12:01 AM #102
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
yes it could...it is hard to help a guy over the internet isnt it...the best is when they say its messed up but the pressures are "good" that is funny sh@t!!!
-
05-10-2009, 03:15 PM #103
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
05-10-2009, 04:04 PM #104
-
05-10-2009, 06:52 PM #105
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I think Reefermech was thinking that if the voltage leaving the transformer was higher that this could cause higher current draws for the controllers devices. This does make logical sense, but since you have proper voltage on the secondary, then transformer is not the issue.
You have changed the controller twice and still pops the fuses, do you know exactly when the fuses pop? Do they pop right away or does the unit continue through its start up sequence and then pop. If so in which part of the sequence does the fuse blow? During Evap fan start up, during condensor fan start up, during compressor start up? Typically this will give you clues as to what device that the controller is blowing the fuse on.
If it is popping right away then you will probally have to get out your DMM and perform a resistance check on all inputs and outputs for a path to ground or internal low resistance due to a faulty shorted electrical device.
Let us know what you find
A-Z
-
07-10-2009, 09:40 AM #106
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi William,
As I know, just go to misc. function menu to reset time and date. No need password.
-
07-10-2009, 08:25 PM #107
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Good day.
i'm a biginner technician in reefer side.i want to bay some data retreive connector .but i have problem to found them ...
can some body assist.
badilou.nabil@hotmail.com
-
08-10-2009, 04:31 AM #108
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
everybody,
sorry, wrong post yesterday
-
08-10-2009, 08:29 AM #109
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi!
Please help to send these manuals to my email: khoadg@yahoo.com
Thank a million!
-
09-10-2009, 06:54 AM #110
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Whats ya doing teguh ? lol
-
27-10-2009, 06:14 PM #111
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Does anybody have documents about general principles of reefer's control system and how it designed? Information about connection of sensors,cable diagrams and repair manuels would hellp me too, Thank you..
-
31-10-2009, 01:31 PM #112
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a carrier 511-362 thats going off on Alarm 15 but that alarm does not appear on the list of alarm codes on the reefer or in the manual that I can locate...if you know what this means let me know. I'm a newbie and working by myself and don't really want to call someone else in if its just something stupid.
-
31-10-2009, 10:09 PM #113
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
02-11-2009, 07:37 AM #114
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
The latest SW ver. is 5146.
-
02-11-2009, 09:23 AM #115
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys,
I am new to this site. I have 2 faults codes on sr-2 alarm window: 4 and 204. I found a plastic back stuck in evaporator so it was preventing airflow. I fixed but need to reset these codes. Can anyone pls help.
Thanks
Jesmond
Rig19 Electrician
-
03-11-2009, 07:09 PM #116
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
........................
Last edited by reefermechanic; 27-02-2013 at 08:56 AM.
-
05-11-2009, 11:11 AM #117
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi, only new to this site and new to transport Refrig. I have just recently started work on a Truck with an RD11 50SR 380V
B/M No. 915527. on R404a ...
the in cabin computer is a Thermoking Thermoguard Base - 5D52175G01
S.P 45-1066
The problem that has been occuring is the unit runs until the temp decreases to about 2degrees C then unit cuts into defrost then cools again then defrosts etc etc..
The screen showed just before defrosting
Room 1.3oC
DIS -2.7oC
Coil -7.2oC
Set up for DF1 4 and DDR 45
The air pressure switch has been disconnect. I have checked the operating pressures 120kpa suction and 1650 kpa Head pressure. I hosed out condensor coil and check evap conditon No ice on coil..
What does
(("SELECTING CYCLE SENTRY OR
CONTINUOUS MODE"
1. Press the On Key to turn the unit on.
2. Press the Select key to display [CYCLS]
and [YES] or [nO].
3. Press the Up or Down Arrow key to
select the desired mode. [YES] = Cycle
Sentry, [nO] = Continuous.
4. Press the Enter key. The display will
briefly show [Lod], and then the new mode
will reappear.))
Is it possible to change how the unit activates defrost.? becuase the owner only uses the truck for about 4 hours a day can the defrost relay be removed ?? I would appreciated any help or ideas!!
-
09-11-2009, 08:17 AM #118
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi
good day
i want to know aboutthermo king reefer unit on message (quest not allowed by timer). can u explain me and how to clear this message ?
thanks you
pyae
-
09-11-2009, 09:49 PM #119
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.............................................
Last edited by reefermechanic; 27-02-2013 at 09:00 AM.
-
11-11-2009, 09:02 AM #120
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello sr, I HAVE A PROBLEM WITH MY REFEER , HAS THIS MESSAGE. ENGINE STALLED. IDONT NOT WATH IS THAT CAN YOU HELP ME IM SORRY FOR MY BAD WRITER THANX SO MUCH
-
11-11-2009, 09:03 AM #121
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I forgot my unit its a carrier ultima53 year 2000
-
11-11-2009, 09:37 AM #122
-
17-11-2009, 12:48 PM #123
-
18-11-2009, 02:26 AM #124
Request Service Manual Reefer Container "DAIKIN" LXE 10 D
Dear Reefer Mechanic,
Would you like to sent me Service Manual / Operating Manual of Reefer Container "DAIKIN" LXE 10 D ?
My Email Address is tri_ardi@yahoo.com
Best Regards,
Triardi S.
-
24-11-2009, 07:36 AM #125
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear bro...
When i was doing pti (thermoking unit,magnum), alarm 115 and 116 were come out.it does mean sensors faulty but when i check connection and ohm,showing that all in good condition (2000 ohm) please help me how should do?
-
26-11-2009, 03:23 PM #126
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.....................
Last edited by reefermechanic; 27-02-2013 at 09:00 AM.
-
28-11-2009, 10:53 PM #127
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HAY ALL,
i am technician in the reefer , pls i have probleme with t.KING ( quest allowed) i want to clear it but i need help .
BESTB REGARD
-
02-12-2009, 06:56 AM #128
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Sorry for late reply,mate ! I haven't try to change yet coz i haven't spare part yet but i'll be change return air sensor and reply you no sooner.
Thank you so much for your reply.
-
03-12-2009, 04:27 AM #129
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thanks a ton. It's really worked!
When i was changed return air sensor , the unit is ok and pti pass.....i am quite curious coz the measure the value of ohm is nothing different with the old and new one sensor..? ?
-
03-12-2009, 04:33 AM #130
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, banana
Try icebath calibration
-
06-12-2009, 01:58 AM #131
To ppsmtu - re QUEST
Hi, you shouldn't need to clear this. Quest is a power saving initiative. Starcool and ThermoKing also use it, Daikin call it DTMS2.
It is exactly as you state "a message". It is telling you that the power saving mode (Quest) is currently not active due to a controller initiated time delay.
As per Reefermechanic's menu picture, it is in the MISC sub menu Under STATUS.
Quest should be left to do what it is supposed to, and only turned off if you have a very good reason :-)
"QUEST power-saving mode is a software-based control option for Carrier Transicold refrigeration units that intelligently cycles refrigeration on and off based on temperature limits designed for specific perishables. It can cut energy requirements for refrigeration by up to 50% while also reducing power-related emissions."
-
21-12-2009, 08:44 AM #132
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
pak teguh...
punya softwere untuk daikin, \tk, mitshubisi.
kalo ada boleh untuk di share ke saya
terima kasih
-
25-12-2009, 10:47 PM #133
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please i need manuel for trailer theroking
-
25-12-2009, 10:50 PM #134
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please i need manuel for trailer theroking ANYONE CAN HELP ME SEND IT TO ZAHERADIDAS@HOTMAIL.COM
-
29-12-2009, 10:43 PM #135
-
29-12-2009, 11:02 PM #136
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
note that it's no alarm ,i thinc sae tect reefer play in cofiguration i check and i bac whit good ansower. tnks/reefer sup
-
29-12-2009, 11:03 PM #137
-
30-12-2009, 02:06 PM #138
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic ,can you advice me on truck unit - T/K Spectrum MT ?
-
30-12-2009, 02:12 PM #139
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
PM me .tq.
-
03-01-2010, 02:20 AM #140
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have an old carrier 511-331. Its not modulating at all and also seems to be turning on only when the return comes 1 degree over set point and will go down 4 or so degrees under setpoint. Now I havent spent much time on it but have tested power coming to the plug connected to the stepper motor..I have voltage coming through on all 4 lines.. Should only have power on A/B or C/D at one time as A/B open and C/D close it if my memory serves me correctly. So that tells me the stepper motor itself is not the issue, however does this mean somehow it is the microlink or could it be the power module or even something else? just trying to get another opinion as it is a leased box and I cant just start changing random parts. P.S I did check to see if quest software was on this box and it is not.
-
05-01-2010, 06:34 AM #141
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
dear all;
first happy now year;i have reefer daikin with AL :d301;but i dont new the solution,plz help me urgently
-
10-01-2010, 05:22 AM #142
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey 1612
check for broken wires behind the compressor and suction valve. they rub on the back wall sometimes. also the drive module or if its an APL the emergency module fails. if it has an emergency module remove it and plug into the SMV directly
-
11-01-2010, 01:43 PM #143
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
good day evey body .
i look for some advice from the refrigeration-engineer experiance.
me issus is i can found the stare cool reefer unit softwear to import the data logger from this unit..
please advice .
badilou.nabil@yahoo.com
-
21-01-2010, 12:41 PM #144
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi
I need 2 manuals for these equipments:
ThermoKing MDII-MAX
Carrier Mistral 800
please send it to nunovgato at gmail.com
Thanks
-
04-02-2010, 03:53 AM #145
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
alguien en español por favor nesesito datos diagramas de carrier intercambio informacion tengo todo de thermo king grasias ggeras@hotmail.com
-
04-02-2010, 05:58 AM #146
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Climo-tecnica,
Could you speak in English?
-
04-02-2010, 06:05 AM #147
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Ci 1612,
I think you should check CD18 CD20 and CD34 to verify the setting of configuration, software versions and Economy mode.
-
04-02-2010, 06:25 AM #148
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Starezone,
Please receive email for software.
-
05-02-2010, 05:34 AM #149
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, reefermechanic
Im Dante, can I charge a Carrier reefer with 404a its present refrigerant is 134a?....Pls. give me more info about this. Thanks
Dante
-
05-02-2010, 06:37 AM #150
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Dante,
I think you can not charge it with R404a. Because the working pressure of R404A is too high to fit this pipe system. and the components, for example compressor, TXV, HPS.... are not suit R404A.
transcold.
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM