    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Sounds like a failed discharge pressure regulator (DPRV). Mounted in the discharge line behind the compressor. If it fials to open then the unit shuts down on HP

  2. #2
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    plugged DPRV

  3. #3
    ngamyst's Avatar
    ngamyst Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefermechainc
    I have one of thermoking MD 200 used Driver Operation-TS Series Truck Unit problem of frequently defrost.What problem?
    Thank before.

  4. #4
    Join Date
    Mar 2014
    Location
    USA
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefermachanic , can you please help me with a service manual and diagrams for a Thermoking V250 ? My email is AR74Hog@yahoo.com
    Thanks so much !!!

  5. #5
    Join Date
    Apr 2014
    Location
    Philippines
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I need help with my mitsubishi tu73d. I need an english service manual and english electrical diagram.

  6. #6
    Join Date
    Apr 2014
    Location
    Philippines
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Please send me a private messsge if you csn help. I cant understand the controls of the systemcoz its in japanese

  7. #7
    Join Date
    Apr 2014
    Location
    Nigeria
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefermechanic,
    I'm in the haulage business,my co. recently decided to try our hands on refrigerated transport so we purchased a Thermoking V500 max tc 20 mounted on a mercedes benz atego truck from England.
    TK unit was supposedly working when purchased, but when we took delivery of the truck we discovered that the printed circuit board was missing from the unit.
    We have ordered for a new PCB and we have mounted it with all required relays and fuses.
    The problem now is that the in-cab control box comes on,displays the return temprature and the set.point temperature, but the unit does not come on,the fans do not work and there is no indication that the unit is working at all, even though the cooling indicator light is on.
    We are still trying to run it in vehicle mode.
    It is a 24v unit.
    We have also tried in vain to locate fuse F21 which supposedly supplies power to the unit from the vehicle battery.
    Please do you have any ideas how we can get the unit running? or any ideas what may be the problem.
    Thanks a lot.

  8. #8
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Guys,

    Pls ask the questions to me about refrigerated container units.

    All the best,
    See you
    Reefermechanic

  9. #9
    Join Date
    Apr 2014
    Location
    mauritanie
    Age
    45
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Reefer Mechanic,

    Would you please help me to download a operation manual for CD TTT M5, please send to:
    passionplayer@live.com
    best regards

    Thanks a lot!

  10. #10
    Join Date
    May 2014
    Location
    Afghanistan
    Age
    55
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Reefermechanic, Friend of mine at another FOB is having trouble with...
    It's a 69NT40-541-302 running 1 or maybe 2 degrees of differential on supply/return. Won't cool below 45F here in the high desert. It got a new Controller, "Micro-Link P/N 12-00579-00 or approved equal" before I saw it and fired it up. Ran okay--Except for Alarm 67--but we don't control humidity anyhow, so I ignored it. It ran good for a few months, then cooling petered out.
    Checked the usual--cleaned both evap and cond coils, fans run hard, changed filter drier and put in correct 8.75 pound charge of 134a. It pulls 8-9 amps per leg and suction of zero to -10 inches. Discharge runs 110 to 195 as condenser fan cuts in and out. So what red flag am I missing here?

  11. #11
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by BIGABOW View Post
    Reefermechanic, Friend of mine at another FOB is having trouble with...
    It's a 69NT40-541-302 running 1 or maybe 2 degrees of differential on supply/return. Won't cool below 45F here in the high desert. It got a new Controller, "Micro-Link P/N 12-00579-00 or approved equal" before I saw it and fired it up. Ran okay--Except for Alarm 67--but we don't control humidity anyhow, so I ignored it. It ran good for a few months, then cooling petered out.
    Checked the usual--cleaned both evap and cond coils, fans run hard, changed filter drier and put in correct 8.75 pound charge of 134a. It pulls 8-9 amps per leg and suction of zero to -10 inches. Discharge runs 110 to 195 as condenser fan cuts in and out. So what red flag am I missing here?
    Hi Friend

    You can use whatsup?

    İf you have +905366678279 of my mobile number. Pls write to me via whatsup.

    see you

    reefermechanic.

  12. #12
    Join Date
    May 2014
    Location
    Afghanistan
    Age
    55
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi Friend

    You can use whatsup?

    İf you have +905366678279 of my mobile number. Pls write to me via whatsup.

    see you

    reefermechanic.
    sorry I don't have that app. I will let him know you replied on HVAC-TALK as well. take care......and Thanks a Million!

  13. #13
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by BIGABOW View Post
    sorry I don't have that app. I will let him know you replied on HVAC-TALK as well. take care......and Thanks a Million!
    Hi Friend,

    you have account for skype or facebook?

    see you

    reefermechanic

  14. #14
    Join Date
    May 2014
    Location
    Usa
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have 4 years experience in commercial a/c. I've currently put in for a job as a reefer tech. Is there any basic stuff that would help me out on these reefer units that's different from commercial air? Common problems, and such. Anything will be grately appreciated.

  15. #15
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by Kf1234 View Post
    I have 4 years experience in commercial a/c. I've currently put in for a job as a reefer tech. Is there any basic stuff that would help me out on these reefer units that's different from commercial air? Common problems, and such. Anything will be grately appreciated.

    Hi Kf1234

    How can i help you?

    see you

    reefermechanic

  16. #16
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Thein,There is no any wesite or mobile application for your request. See youReefermechanic

  17. #17
    Join Date
    Jun 2014
    Location
    FL
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I am having code 26 and 32 on a sb 200 thermo king any suggestions?

  18. #18
    Join Date
    Jul 2014
    Location
    United Arab Emirates
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi All,

    I am new in this forum. can anybody suggest me how to reset AL22 on 69NT20/40? My understanding is Alarm 22 responds to the evaporator motor internal protectors.

    Regards

    Mohsin

  19. #19
    Join Date
    May 2003
    Location
    Syracuse, NY, USA
    Posts
    42
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by Mohsin Yasin View Post
    Hi All,

    I am new in this forum. can anybody suggest me how to reset AL22 on 69NT20/40? My understanding is Alarm 22 responds to the evaporator motor internal protectors.

    Regards

    Mohsin
    The better question to ask is, Are the evaporator motors running? AL22 responds to loss of control voltage at TP5 on the controller (ECJ2 on the input plug). Loss of control voltage at this point stops the evaporator fans ans sets AL22. Verify which motor has failed and change it and then use the Alarm key on the keypad scroll to Clear and press enter. Until the evaporator motors are repaired the alarm will continue to appear.

  20. #20
    Join Date
    Oct 2013
    Location
    viet nam
    Age
    38
    Posts
    4
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    My email adress: nhadth07@gmail.com. Thanks.

  21. #21
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi all
    i have a starcool unite and i have alarm for motor evap failr.but in my stor i have not the same motor marc. I have a ABB motor.when i changed the unit work good but a few minut alarm caming again.what you must do.

  22. #22
    Join Date
    Nov 2013
    Location
    Singapore
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi terminal,
    u have to change some wiring of new ABB motor.
    motor side wire to incoming supply wire
    " 4 to 6 "
    " 5 to 4 "
    " 6 to 5 "

  23. #23
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Thank you sur. When i have this problem i wil try to change wirs.thanks

  24. #24
    Join Date
    Oct 2013
    Location
    Serbia
    Age
    58
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I apologize to other members of this community, reefer mechanic and bruisermac are two best men who gave best answers all the time on this forum.Cheers

  25. #25
    Join Date
    Dec 2010
    Location
    Paranagua
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear reefer mechanic,

    Someone has the carrier scrl5364.ml3 software, and the software menu0116.m2x?
    Please send me m_heckert@yahoo.com

  26. #26
    Join Date
    Apr 2013
    Location
    lusaka
    Posts
    14
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi All,
    I have a problem with a 69 NT 511 - 353 CARRIER CONTAINER

    The unit seems to be running in a vacuum on the suction side? it is equipped with a modulation valve and quench valve these seem to be both iced upto the suction service valve.

    the refrigerant seems to be charged ok because the unit is cooling at a struggle to - 8 - 10C the balls in the site glass on both glasses are at the top.

    Please advise if anyone has good knowledge of these units.

    Thanks


    New Picture.jpg

  27. #27
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    drier is probably plugged

  28. #28
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Probably problem with the regulation valve..
    Did you try to re-set the valve to a specific value?

  29. #29
    Join Date
    Apr 2013
    Location
    lusaka
    Posts
    14
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi no I didnt how would I do this?

  30. #30
    Join Date
    Oct 2015
    Location
    US
    Age
    57
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    New to the forum, and looking for any manuals, schematics, etc... on Noske-Kaeser refrigerated chemical trailers. The company that has them in my area got a 5 page printout from them but it is in German. I can't read German. Any help would be appreciated.

  31. #31
    Join Date
    Oct 2015
    Location
    Lithuania
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello, i'm new in the forum and i'm looking for Carrier and Thermo King manuals, if you have some please send me, i'll be very grateful.

    My email: lukaspavalkis@gmail.com

    Thanks in advance.

  32. #32
    Join Date
    Oct 2015
    Location
    Lithuania
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    To be accurate i'm looking for Thermo King SLX, SL series and Carrier Vector, Maxima manuals. Thanks guys.

    my email: lukaspavalkis@gmail.com

  33. #33
    Join Date
    Mar 2007
    Location
    UAE
    Age
    43
    Posts
    78
    Rep Power
    18

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear all,

    I need some suppliers for reefer containers.

    I am in oman.

    Kindly give a mail to jeyakumar@sfomuscat.com

  34. #34
    Join Date
    Jan 2016
    Location
    TURKEY
    Age
    47
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys

    i m at here

    Best regards
    Reefermechanic

  35. #35
    Join Date
    Jan 2016
    Location
    TURKEY
    Age
    47
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi tjk2007
    I did send an email to you.. How can i help you?

    Regards
    reefermerchanic

  36. #36
    Join Date
    Mar 2016
    Location
    China
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi all,
    I want to know if there‘s any software to read the real-time Tsup and Tret of MP3000 & MP4000? I know LogManPC can read the USDA values of MP3000, but now, many MP3000 containers have no these data. And, the LogManIIPC just downloads recording data from the Data Recorder. So, can anybody help me?
    my email:ap0505138@yahoo.com
    Thanks!
    Wenping

  37. #37
    Join Date
    Apr 2016
    Location
    KENYA
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Any one with the manual for Thermo king CB MAX + 20

  38. #38
    Join Date
    Apr 2016
    Location
    KENYA
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    my email ; nictind@yahoo.com

  39. #39
    Join Date
    May 2016
    Location
    Poland
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys.
    How to change fahrenheit degrees to degrees Celsius in Thermoguard 5D52175G01?

    Thanx

  40. #40
    Join Date
    Apr 2009
    Location
    viet nam
    Age
    47
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi! All
    Help me
    I'm having problems with one machine SB3 SR +, cycle-sentry operating mode, the engine does not work for high-speed mode, but when operating at continue mode, works well for high-speed mode

    Tks

  41. #41
    Join Date
    Aug 2016
    Location
    usa
    Age
    41
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have reefer trailer with SB-210. I have just replaced filters and run pretrip. It failed with clearable alert "refrig capacity low". This unit is only used for heating so do I need to add refrig r404a or is it ok to leave it like that?

  42. #42
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello Reefer Mechanic and others!
    I am a newbie here and I am happy to be part of this forum.

    Our 69NT40-541-322 have a problem on sup and ret temp. The sup cannot reach the set point of -23°C and it stays only at -20°C and ret at -18°C. When it was loaded the sup was -23°C and ret -19°C. My mate charge about 1kg of refrigerant even the DP already high but he suspect it has low charge. After the charging the sup and return goes up insted of going down and of course it alarmed HPS. He recover some to just below the limit of HP. We also observe some oil down of compressor and this compressor was recon because of the paint. We cannot find the leaking part by using electronic leak checker we did not find the leak. The next day i found it was off and main breaker was tripped off. We turned it on and observed. We obsrerved that warm air out of condenser fan was disappearing after few seconds of running, we change the drier. But still the sup and ret temp cannot reach set point. Here are some data I have:
    Suction pressure -0.6 bar
    Discharge pressure 20 bar
    CD60 -18°C, we dont know this
    Ambient 36°C
    SMV 100

    We tried defrost, plenty of water comes out but nothing change in temp after. We turned off the reefer but discharge pressue does not drop, it almost remain high but suction pressure goes up. By pump down the DP goes down. The reefer does not trip anymore. Tommorow i will check the DPRV by checking the pressure on discharge of compressor vs liquid-line. What do you think the problem is? Sorry for my grammar.

  43. #43
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Checked DPRV, 1bar diff, seems ok.

  44. #44
    Join Date
    May 2008
    Location
    Kazakhstan
    Age
    57
    Posts
    12
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello everyone! It became necessary to replace the so-called Quench Expansion Valve (part n. 14-00212-03SV). Absolutely no desire to buy it for $ 200 plus shipping (such prices at us, unfortunately), when it is possible to replace the OEM. The only problem is unknown, its capacity. Does anyone know? If so please respond.

  45. #45
    Join Date
    Oct 2016
    Location
    NJ
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello everyone.

    I am working on a Thermo King TS-300 with a code 17, which is "engine failed to crank". I manually tested the starter, and it is good. The 8S circuit from the relay board is also good.

    Since I have an identical scrap unit handy, I tried a different relay board, microprocessor, cab command, cab command cable, and main on/off switch. None of those made a difference.

    The unit will preheat and the buzzer sounds, but it does not crank. Also, it appears that the pull in circuit for the fuel solenoid does not have voltage either. There is voltage at the 2A terminal on the board.

    I'm stumped. Has anyone dealt with this before? Thanks in advance for any assistance.

  46. #46
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    What voltage do you have at the feed to the solenoid of the starter,try disconnecting the feed and testing if you have a feed to it pretty sure there is a plug on this feed close to the starter maybe a break in the feed try a temporary cable from that 8s and see if it engages the starter ?

  47. #47
    Join Date
    Oct 2016
    Location
    NJ
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have done that. If I put direct power on 8S, the starter cranks. That tells me the plug and circuit are good.

  48. #48
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Over here we use desperate battery for the unit,sometimes I believe in the states they tap into the truck battery,there is an extra heavy wire fitted to the battery not sure if it goes to number ,has this wire got good power/ connection ?

  49. #49
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Whoops spellchecker ,should have spelt seperate!!! not desperate?

  50. #50
    Join Date
    Dec 2009
    Location
    Egypt
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    All dears,
    I have problem with MItsubishi Transport refrigeration unit with model CPE15-3B H?
    I need help please

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 08:11 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 05:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •