17-04-2013, 11:23 PM #451
-
19-04-2013, 12:04 PM #452
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi!! I'm doing some research about the reefer container. Just want to know according to your guys exp, which brand/manufacturer of the reefer container is the best interm of quality/efficientcy?
From my understanding there are 4 big players in the market+Mearsk (Have their own starcool)
-Daikin
-Carrier
-Thermoking
-Mitsubishi
-Mearsk (Starcool)
And what is the market share of these 4 manufacturer+ Mearsk?
If i want more info about the reefer container business, where can i get the info.
Thanks
-
19-04-2013, 12:15 PM #453
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Goldenbull i should help you about your request. pls contact me via reefermechanic@yahoo.com see you reefer mechanic.
-
19-04-2013, 12:16 PM #454
-
24-04-2013, 07:17 PM #455
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
KA9 and KA10 are two separate 18vac power supplies for the ML3 controller which should be referenced against KA12 (Ground). So 33v seems to be around normal if measured across both and the control transformer would seem to be working. Are both evaporator fans working as there is an Internal protector (IP-EM1 and IP-EM2) which are embedded into the motor windings. A shorted evaporator motor can back feed 380v back into the controller through the IP lines usually this is instant once a motor burns out but may take a little longer depending on the severity of the burn out.
The programming language for the Carrier microprocessors is properietary
-
25-04-2013, 01:20 PM #456
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello all i am a refrigeration mechanic from australia and do alot of work on commercial airconditioning but have never seen or worked on any transport refrigeration gear
i have a customer who has the back of a truck at his house that is refrigerated by a thermoking unit
inside it has 2 evaporators and he wants 1 of them moved about 3-5 metres from its current location inside the back of the truck
is it as simple as just pumping down the unit, extending the pipes and all electrical connections or is there something else i should know?
can these units be pumped down like any regular unit so that i can cut the pipes going into the evaporator?
the evaporators have 3 pipes going into them, i would assume one is a hot gas defrost?
will extending the cables effect anything such as the thermostat probes which will obviously also have to be extended??
thanks for any help, the reason for so many questions is that i will be approx 800km when working on this unit so i need to be prepared as i cannot get parts easily
thanks anthony
-
29-04-2013, 11:50 AM #457
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic
I have tried to send you the private mail too many times but, always got auto replied mail back that your email is not valided. Please kindly confirm your email again or mail me at goldenbulls@gmail.com
Thanks,
-
29-04-2013, 08:19 PM #458
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
No problem extending the wiring or the piping.
Is this an older diesel powered unit like an RD-II TCI / TLE?
I recommend against trying to pump down the unit, technically it is possible (high side pump down) but not recommended. You're best to recover the complete charge, makes it easier for nitrogen purge when soldering the pipes and evacuation. There is a mess of valves in those units and chances are you're going to have one leaking past a little bit so you'll never get a solid vacuum. When you evacuate you must do a three point (suction, discharge, receiver)
-
30-04-2013, 06:58 AM #459
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi goldenbull you can chat with me via reefermechanic@hotmail.com and reefermechanic@yahoo.com adresses. see you reefermechanic.
-
01-05-2013, 11:09 PM #460
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello everyone can you please help me with my problem regarding on carrier reefer container because i found out that the controller is damage. I replaced new controller but currently not working yet because i can't configure it. I found a spare of SRAM to cofigure it, but when i put it doing the right procedure on the manual it still not working. My question is, do i need to download new software of ml3 and copy to the SRAM to configure it? I also have a spare of card (I'm not sure if there is program of ml3 inside) and adaptor of SRAM but i don't have pc that can connect it. Also, i cannot put directly the card to the container controller because the connector is for SRAM only. I also try to go in the site of carrier to download this program ml3 but i cannot access it because of password. I want to use emergency bypass but the problem the commodity inside is wine therefore i cannot directly run the reefer to cold mode. Please help me on this problem and if there is any suggestion I appreciate it. Thank you
-
02-05-2013, 01:38 AM #461
-
02-05-2013, 11:28 AM #462
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Friend this is the Cd-18 5148 (i also have a 5318 program),Cd 20 don't exist, and the unit model number is 69NT40-541-301. When I check the reefer this morning it has too many alarms specially on safety device and it's not working. The setting in code select is in default and i try to use the emergency mode but it is not safe for the commodity because it will have too much cooling. Please give me advice for this problem. thank you very much
-
02-05-2013, 11:47 AM #463
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Jayson. DOn't worry. We can repair its together. Trust me pls chat with me via reefermechanic@yahoo.com. see you . Reefermechanic.
-
06-05-2013, 02:16 PM #464
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I am yet to get a model number from the client because e recently got Injured at work.
Could you please explain why I must do a 3 point vacuum? I mostly work on air con systems and only have do high and low side? My gauges are only the standard type with 3 hoses not a manifold set
I look forward to your advice. Thanks
-
07-05-2013, 02:09 AM #465
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
A three point is required due to the disaster of solenoid/check valves in the system. The condenser inlet and suction line solenoids are normally open but the rest are normally closed. In this system when one compartment is calling for heat and the other for cool the compartment calling for heat becomes the condenser. Fun **** when valves start to stick intermittently. On older RD-II the electrical is just as fun.
tci.JPG
This is a TCI system with a host attached to the main unit. A TLE has no host and 2 remote evaps. The plumbing is the same.
-
07-05-2013, 08:05 AM #466
-
07-05-2013, 10:48 AM #467
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Electronic control board for all models. this is video (Thermo King, Carrier, Zanotti)
this is video link http://www.youtube.com/watch?v=0DT7QLmGWMs
-
07-05-2013, 11:00 AM #468
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
All for model electronic control card
this is video link http://www.youtube.com/watch?v=0DT7QLmGWMs
-
07-05-2013, 01:00 PM #469
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
07-05-2013, 01:42 PM #470
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Yes, there would be gas in that line. If you pump down and equalize at the compressor the condenser inlet check valve should hold the charge but I wouldn't trust it. For all the time it takes I would pull the charge. It should be 404a but depending on age it could be 502. As far as mechanically opening the valves, a magnet on each liquid line solenoid should do it. I like the three point, it pulls a better and faster vacuum. If you have an extra port on your pump, hook the receiver directly to your vacuum pump. If there still is shraders on compressor I'd yank them too, with service valves they are redundant.
-
07-05-2013, 10:57 PM #471
-
08-05-2013, 03:06 AM #472
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
No stupid questions. If the unit is running pump out from the receiver into your recovery tank, you'll probably get at least half the charge or most of the liquid, more if you cover the condenser. Then recover the remaining liquid from the receiver after that switch to your compressor connections.
-
10-05-2013, 02:20 AM #473
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
15-05-2013, 12:44 AM #474
-
18-05-2013, 04:54 AM #475
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Just a quick query…..
I have a NT40 reefer used as a static chiller (+5 setpoint), and this has been working well until the last few days when once or twice a day, the power trips at the breaker inside the reefer panel. The incoming mains supply is steady at 385v and everything seems fine. I reset it and it works again. There are no alarm codes. The only change is that the temp here has risen to around +40 in the last few days and this may have an effect.The trip mostly happens in the afternoon when the sun is shinning directly onto the working end of the container.
Have you heard of this happening in the extreme heat ? I am really hoping that its not the compressor windings starting to earth. It’s has the water cooled option but is set for air cooled.
Any wise words please
-
20-05-2013, 07:05 AM #476
-
28-05-2013, 02:27 PM #477
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello...no the problem isnt solved yet as it only seems to trip the CB when its very hot (+40c). Its works well day after day when its below this ambient temp. I have set the amps to 21. Its not an isolated case and can be common as the summer draws near here in the middle east. I am constructing some shading to see if that helps.
-
28-05-2013, 02:53 PM #478
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
you can chat with me via reefermechanic@yahoo.com ? see you , reefer mechanic.
-
28-05-2013, 03:25 PM #479
-
02-06-2013, 07:14 AM #480
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
ust a quick query…..
I have a NT40 reefer used as a static chiller (+5 setpoint), and this has been working well until the last few days when once or twice a day, the power trips at the breaker inside the reefer panel. The incoming mains supply is steady at 385v and everything seems fine. I reset it and it works again. There are no alarm codes. The only change is that the temp here has risen to around +40 in the last few days and this may have an effect.The trip mostly happens in the afternoon when the sun is shinning directly onto the working end of the container.
Have you heard of this happening in the extreme heat ? I am really hoping that its not the compressor windings starting to earth. It’s has the water cooled option but is set for air cooled.
Any wise words please
-
04-06-2013, 10:18 PM #481
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Can anybody help me in understanding, maintaining and repairing of Thermoking Magnum units?
Whats the best way to handle these units. I'm much interested to learn about them.
Please help me.
shehzad.ahmd@gmail.com
-
05-06-2013, 05:32 AM #482
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Does anybody out there have the latest Carrier Microlink software, I'm looking for 5155 and 5355 for both ML2 and ML3 Scroll and Recip. I do not have access to carrier website for download. Can someone please email the files to me, greatly appreciate it.
kyniteowl@gmail.com
best regards all reefer mechanics
-
11-06-2013, 11:57 AM #483
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Good day
I am looking for a data downloader for thermoking and Daikin.
Could you please advise?
many thanks
-
14-06-2013, 02:25 AM #484
-
23-06-2013, 11:24 PM #485
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, can anyone help me ?I have a customer with a old TK reefer model TNE-508-34, this reefer is given me some serious problem I am unable to get it to work properly ,I check and change the following all three (3) sensor supply and return,KVQ valve,filter drier, TXV. Check both condenser and evaporator fans, compressor they are all satisfactory yet the system will not pull down to temperature (-25c) the system start up and the pressure and amps are ok and 5 minutes the suction line will frost up causing the pressure to drop off and the supply and return temp also. The following is the info taken from the controller. Supply LH -4.7. Supply RH -5.7. Return -4.0. Evap -4.9. Cond temp 44.5. KVQ setting -55.4. Cool cap 100%. Ambient temp 28.1c. Hi press 10.5bar. Hi press temp 101.2c. Comp amps 10.8/ 10.5/11.3. Can you help me out here if I am doing something wrong or not checking something or is there a TK emergency hot line number .
Thanks in advance
Lynch
-
30-06-2013, 09:02 AM #486
-
04-07-2013, 10:35 AM #487
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I work in Bagdad, Iraq. The units I maintain are powered by gererators. I have several Carrier 69NT40-541, in which the controllers(micro link 3) have stopped working. The LED is flashing ERR1 or ERR2. Its hard to tell. I have the program card but it doesnt work. Carrier transport reefer div has yet to return phone call. I installed a Dixell controller, it runs but doesnt cool like it should. it is set for -18c but only gets down to -7 or so. I believe the smv is preventing it from reaching temp.
-
04-07-2013, 02:10 PM #488
-
04-07-2013, 02:23 PM #489
-
06-07-2013, 03:39 PM #490
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
thanks guys i need "Ml3_serail_number.bin" so i can program my pc card.
-
12-07-2013, 07:40 AM #491
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello,I need service manual for Thermo King V-300 Max - electro schematics of the electrical board. Does anyone have it?
-
23-07-2013, 02:53 PM #492
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I am having an issue with a TK CRR-40 with a mp-3000 contoller. It showing "Flash Load". What does this mean?
-
23-07-2013, 03:04 PM #493
-
25-07-2013, 07:09 PM #494
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys, If you need laptop and communication programs and also connection cable for transport units you may contact with me.... For truck, trailer and reefer container units of Daikin, Carrier and Thermoking units. see you.. reefermechanic
Send me a PMLast edited by frank; 25-07-2013 at 07:42 PM.
-
26-07-2013, 10:59 PM #495
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I am having a problem with my Thermoking Reefer container and I was hoping you could help. I have a 2003 Thermoking Magnum unit with a MP-3000 controller. The unit is always set for the same temperature 13.3C or 56F. Recently the container has been going into defrost mode and sort of getting stuck there. To try and stop it, I set the 24 hour defrost to ON, and now it will go 24 hours and then get stuck in defrost. By "stuck" what it will do is go into defrost, heat the evaporator to 86F (aprox 10min), shut the heaters off, starts the compressor, runs for 1 min, goes back into defrost, and on and on. Checking the event log it shows Timed Defrost activated, then ended. These defrost cycles continue with intervals of 7-15min between. I have ran Full PTI and all of the temperature sensors seem to be working correctly. What could this be? I am completely stumped!
Thank you in advance,
BananaNick
-
26-07-2013, 11:32 PM #496
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Bananick , Pls check the sensor test on "manual function test" within "PTI COMMAND" MENU. Do you know how can do that? I think defrost sensor/evaporator sensor is defective. Run the sensor test on manual function test. than check the sensors for 5 minutes.. And watch the all sensors. All sensors measurings must be same. Pls check that's and back to me. see you . Reefermechanic
-
21-08-2013, 07:09 PM #497
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi there, can i have some thermoking and xrios 500 service manual/ wiring dia gram.
khalidmz786@hotmail.com
thanks
khalid
-
27-08-2013, 02:29 PM #498
-
11-09-2013, 05:24 AM #499
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Peace,
I have a case of 1 unit 40ft Reefer Container (with Daikin System) shipped with consignment of vegetables with setting temperature at 0 Deg C, however, at sometime transit, noted several alarms/code D type and there on supply temperature went up between 10 to 16 Deg C (From Data Logger). What caused malfuctioned ? Also noted, 2 drain plugs, one at front end and one at door end not inserted. Please help !
-
25-09-2013, 10:50 AM #500
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi there. I am hoping someone can help me, I am having a go for the first time at fixing a refrigerated container, the only details I have is its a "Celsius 3220" if any has had anything to do with these before I am after a service manual or a wiring diagram for it, someone has done something nasty to the wiring and it doesn't like to run real nice. so anyone can help I would be very grateful Thanks
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM