    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi



    thanks! go reefer techs!



  2. #252
    LTP-Jon's Avatar
    LTP-Jon Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi. I'm searching high and low for software to allow connection to the Mitsubishi MMCC3A unit on refrigerated containers. It's usually called "Mitsubishi Heavy Industries Data Logger System". Would anyone know where this is available to download? Thank yo very much.

  3. #253
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Jon, welcome to RE.

    Is this what your looking for ?

    http://truck.mhi.co.jp/gen/acrmw/ser...orma/act5.html

  4. #254
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    call up StarCOOL and they will send you the manuals. They have them on the site but you have to register to get the access.

  5. #255
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi guys,

    everythings ok))

    all the best...

    reefer mechanic

  6. #256
    mike50's Avatar
    mike50 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi. Iam a commercial refrigeration tech Electronic . I was just to repair a carrier 12-60028 controller because it's no turn on the system, let me know where I find the manual for get more information about it

  7. #257
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by mike50 View Post
    Hi. Iam a commercial refrigeration tech Electronic . I was just to repair a carrier 12-60028 controller because it's no turn on the system, let me know where I find the manual for get more information about it

    Hi Mike,

    Whats the problem? Controller doesn't work or controller doesn't control some components? ( Etc. kompressor, fan motorrs?))

    So you cant find any manual about controller on web... (((

    Waiting your reply...

    See you..

    Reefer mechanic...

  8. #258
    lool's Avatar
    lool Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Carrier doesn't gives information about controllers or sales spare parts for them. if you can send it to carrier and they will send you a repaired one for about 350EURO.

    In other hands you should try if its possible to do a software uprade maybe it's a software/set up problem. For that you need a software card.

    Tell us what is the exact problem. Doesn't turn on at all, turns on but nothing happend ...

  9. #259
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi all
    iam a new reefer tech ,
    i want to thanks all tech persenels her;
    i have one quation i have a lap top with windOwz xp tkt 2008;is possible to work tihs windOwz with dataline carrier.AND SMART SPONG THERMO KING.
    BEST REGARD

  10. #260
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    [QUOTE=Vans;214947]hello everyone!
    does anyone have manuals for starcool and the carrier primeline? I am a Reefer Technician working in Dole Philippines. we come across these reefer units but we dont have manuals. any help is appreciated. email me vans@hot-shot.com.[/ I HAVE ONE MANEUL OF STARCOOL
    I SEND YOU NOW .
    BEST REGARD

  11. #261
    Join Date
    May 2003
    Location
    Syracuse, NY, USA
    Posts
    42
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Carrier container reefer manuals can be downloaded from their public website at

    http://www.container.carrier.com

    Select Literature in the left hand menu bar
    Then manuals on the literature page
    Manuals for the last 12 years at least are available direct online with out ID or password

  12. #262
    Join Date
    Apr 2010
    Location
    US
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi all, I have a Carrier Thinline 69NT40-489, how can I set temperature range so do unit don't run 24/7. I guess what I'm asking is if the unit is controlled by thermostat? Seems like the one I have is always on.

  13. #263
    Join Date
    May 2003
    Location
    Syracuse, NY, USA
    Posts
    42
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I assume from your request that you are running this unit as a static store in the perishable range - Setpoint above minus 10°C. Under these conditions the unit is set to run continuously to provide optimum temperature control for perishable product. It does this by throttling the compressor suction line by slowly closing the suction modulation valve just before the compressor. In this way the air supplied into the container is controlled to setpoint +/- 0.25°C. The power draw under these conditions is significantly reduced as the compressor, the only major power draw item on the unit, is running light and current could be as low as 8-9amps from a high of 15amps. There is no way using the Carrier MicroLink controller to change this.

  14. #264
    Join Date
    Apr 2010
    Location
    US
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by adacus1 View Post
    I assume from your request that you are running this unit as a static store in the perishable range - Setpoint above minus 10°C. Under these conditions the unit is set to run continuously to provide optimum temperature control for perishable product. It does this by throttling the compressor suction line by slowly closing the suction modulation valve just before the compressor. In this way the air supplied into the container is controlled to setpoint +/- 0.25°C. The power draw under these conditions is significantly reduced as the compressor, the only major power draw item on the unit, is running light and current could be as low as 8-9amps from a high of 15amps. There is no way using the Carrier MicroLink controller to change this.
    Thank you.

  15. #265
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    a pleasant day to you sir now....can u you help me i am reefer technician from Philippines can i have any you have a about reefer that makes me to improve my skills,we handle thermoking/carrier/daikin/Mitsubishi but i dont have any books or any thing abouts reefer just a diagram.

    i hope you will help me and thanks in advance sir

    lilgenesis_19@yahoo.com....

  16. #266
    Join Date
    Mar 2011
    Location
    INDIA
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hey i have a problem with thermoking magnum its supply is going below the set point the set point is -20 and supply is -27 return is -29

  17. #267
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    349
    Rep Power
    18

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hey i have a problem with thermoking magnum its supply is going below the set point the set point is -20 and supply is -27 return is -29[/QUOTE]

    was the product loaded at -29 ? It being more frozen should make no difference.
    If it was freezing fresh range products then i would be acting.

  18. #268
    hrichards's Avatar
    hrichards Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi. Could someone help me identify this ThermoKing model? I know it uses a C201 engine and V style (two piston?) pump.
    I can not find the location of the model number.

    Here is a picture.

    It was involved in a cabin fire and the fuel lines melted. I am rerunning the fuel lines but I do not know which line is the return and which is the supply. I would think the supply would go through the filter first. The only place I see this is possible is at a T near the filter, there is a line from the injectors going to one side of this T, The fuel filter is on the other side of the T, and one of the burn off lines at another point on this T.

    The other place is on the diesel pump, right under the priming plunger, there is another line that is burned off, but this line does not go to the filters, so I think it is the return line.

    what has me confused is the T by the filter. I guess the return from the injectors could possibly refeed into the supply and be refiltered.

  19. #269
    Join Date
    Sep 2006
    Location
    england
    Posts
    285
    Rep Power
    18

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    the fridge in picture is a snwd 30 = no electric standby

  20. #270
    hrichards's Avatar
    hrichards Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Clivemtk,

    Thanks for the quick response. After googling that model, I realize this was an antique that might have been worth salvaging instead of taking it apart. It was complete until I started taking it apart including a very nice chrome grill that I had to save for the man cave. It was last ran in 1997 as marked on the shiney like new oil and fuel filters. The front service doors were smashed in a way that would not allow them to be opened, so it was like a time capsule when I finally got the doors opened. The compressor is locked up, but after disconnecting the compressor, the engine turns easily (I haven't turned it more than a quarter of a turn though, I don't want to spin it arround until I'm ready to turn it over for a while to get oil pressure up). This is my first diesel engine.

    I'm not trying to turn this into a "How To". Your answer was all I needed. Thanks for having this forum.

  21. #271
    janneman913's Avatar
    janneman913 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hello all

    I'm new here on this forum, am a technician who has + -11 years working mainly on carrier reefers
    I've recently started a new company but we are no yet a official carrier dealer.
    We have all manuals and part list of the reefers but no service bulletins,
    can anyone provide me with the last bulletins or tell me where to find them.

    thans and greetings

  22. #272
    RAFIQ's Avatar
    RAFIQ Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    dear all;

    i want cancel alarm H002 for daikin reefer.

    tnx.

  23. #273
    Join Date
    Mar 2011
    Location
    INDIA
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by gravy258 View Post
    hey i have a problem with thermoking magnum its supply is going below the set point the set point is -20 and supply is -27 return is -29
    was the product loaded at -29 ? It being more frozen should make no difference.
    If it was freezing fresh range products then i would be acting.[/QUOTE]

    no it was not frozen its was ok whille ago but i dont know wht happen its goes like this...

  24. #274
    RAFIQ's Avatar
    RAFIQ Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    impossible !!!!!!!!!!!!!!!!!!!!

  25. #275
    Join Date
    Apr 2009
    Location
    viet nam
    Age
    47
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi! All,

    I have som prolem with daikin reefer machine, compressor eun verry nosie and can not pumdown how about it?

    pls, help me

  26. #276
    waleed's Avatar
    waleed Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi, I have a mitsubishi reefer system that runs for five minutes then stops due to alarm code 413 compressor overheat. Any suggestions on how to solve this problem or what may be causing this?

  27. #277
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    try checking to make sure the liquid injection valves are opening during compressor operation. Also make sure of hte basics like ***** level and compressor amp draws stuff like that.

    next time post more information about the reefer like model and serial number. Setpoint info and other detailed info is needed for proper troubleshooting.

  28. #278
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    more power to us all reefer man lastly hi to all pinoy ^^

  29. #279
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hello to all boss.....i am curious because i have a compressor a new overhaul compressor this is my question the new compressor is running at +02 setpoint in that SP there's no any problem with in 2mos so now i'll change the set point because i want to use my reefer in frozen mode at -25 SP after 3hrs when we conduct a PTI or Pre Trip Inspection i heard a hamming from a compressor and the next is my breaker is trip off and our report is many option and will tell everything what i make in my report.

    this what i write in my report and a bases in my experience.
    1. Oil in my compressor is low
    2. High Ampere
    3. Not enough *****
    4. Maybe the compressor have a foreign material in the system "but i think that is not a strong bases because the unit is new flashing"

    and in myself this is what happen but i did not write to my report in office.

    1. maybe the new overhaul compressor is synthetic or local material only.
    2. maybe the piston is this allign.
    3. over use

    the unit is microlink 2 carrier.

  30. #280
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi there was wondering if someone can help.......
    I have been working on a nt40-511-332 box and when it gets thru to P8 on the PTI it gets down to 1.0deg C then goes back into defrost.The box then fails the PTI. I have replaced a set of defrost heaters as they were down to earth. The contrtoller software is 5146. I have had this before and it turned out to be the controller (ML2I). The refrigerant charge sees to be ok and it passes all steps up to the P8. Havent tried the P10 by itself yet, might try that but any hints or tips that anyone can give would be very much appreciated.

    Has anyone had any issues with the 5146 software?


    Thanks very much in advance

  31. #281
    nekigosu's Avatar
    nekigosu Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hey guys i need some urgent help here.

    I have a Carrier Reefer Container and just now the Controller Alarm was displaying AL60 (Defrost Termination Sensor Failure) and a while ago it completely shut down and the Controller Alarm was displaying AL61 (Heaters Failure).

    But after i restart everything, it is fine up till now (fingers crossed)

    Are these 2 errors code AL60 and AL61 something serious and do i need to send a technician straight away to rectify the problems?

  32. #282
    ramakrishna's Avatar
    ramakrishna Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear Sir,

    I have problem with my container refrigeration unit. It is carrier transicold unit model no.69NT40-511-11. When start the unit compressor is getting full frosting. Can you help me to solve this problem?
    Thanks & Regards

    Krish
    Quote Originally Posted by Will View Post
    Welcome Reefermechanic.

    What ?, no StarCool ?

  33. #283
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear to all RE:

    I need some advice because i will conduct a flashing. the unit is carrier although i have experience to do that but i want to have advice for some important to because the last compressor of that unit is broken so we buy a new compressor.

    thank you and regards to all out there ^^

  34. #284
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by phil Landon View Post
    hi there was wondering if someone can help.......
    I have been working on a nt40-511-332 box and when it gets thru to P8 on the PTI it gets down to 1.0deg C then goes back into defrost.The box then fails the PTI. I have replaced a set of defrost heaters as they were down to earth. The contrtoller software is 5146. I have had this before and it turned out to be the controller (ML2I). The refrigerant charge sees to be ok and it passes all steps up to the P8. Havent tried the P10 by itself yet, might try that but any hints or tips that anyone can give would be very much appreciated.

    Has anyone had any issues with the 5146 software?


    Thanks very much in advance


    Hi Sir you try to replace a new DTS and HTS???

  35. #285
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by hzu View Post
    On a recent trip i had this problem. I was on a ship and had a carrier reefer that had a bad smv valve ( would only open 27%). I didn't have a spare on board so I took the valve apart and removed the piston as the manual said. Well while trying to adjust the temp with the suction service valve i encountered the following problem. The discharge pressure would go so high that it kept opening high pressure cutout switch. I had the suction valve almost closed then the pressure would go almost to the cutout limit and then back on and of while the temp would go down only during the period when the discharge pressure was going from high to low while average temp was going slowly up. I noticed that the quench valve kept closing and opening all the time. Now i always thought that when the smv is fully open the quench valve is suppose to remain shut. I keep wondering what did i do wrong and what was the problem.
    maybe the unit is equip a STEPPER MOTOR i know 27 % in starting is ok base on my own observation ^^

  36. #286
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by ramakrishna View Post
    Dear Sir,

    I have problem with my container refrigeration unit. It is carrier transicold unit model no.69NT40-511-11. When start the unit compressor is getting full frosting. Can you help me to solve this problem?
    Thanks & Regards

    Krish

    Hi Krish

    Some times that s normal. But some times that s not normal. Yo have to check step by step below mationed;

    * You have to do P-6 SMV test, pass or fail?
    * You have to check refrigerant level in the system. Maybe refrigerant level is too much??
    * You have to check TXV.


    If all them ok below mationed no need repair to your unit...

    Good luck.

    see you

    Reefer mechanic.

  37. #287
    avicente's Avatar
    avicente Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefer mechanic,
    Just to ask you about SMV of reefer containers what will happen to the temperature if the SMV does not fully close while the fregiration system is running?

  38. #288
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by avicente View Post
    Hi reefer mechanic,
    Just to ask you about SMV of reefer containers what will happen to the temperature if the SMV does not fully close while the fregiration system is running?
    Hi Avicente,

    When did you see SMV fully close ? SMV dosn't fully close never while the refrigeration system running. SMV does modulation cool when reefer working.

    What you want learn about SMV? If SMV fully open every time while the refrigeration system running thas big problem...

    Waiting your reply.

    see you

    reefer mechanic..

  39. #289
    ramakrishna's Avatar
    ramakrishna Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    my dear friend,

    thank you very much for the suggession. container is in transit and will do the test once it reach.

    Thanks & Regards

    Krish

  40. #290
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Alarm 60 is minor details. It will terminate the defrost on the HTT anyway. The sensor reading is wrong. Very common issue.

    Quote Originally Posted by nekigosu View Post
    Hey guys i need some urgent help here.

    I have a Carrier Reefer Container and just now the Controller Alarm was displaying AL60 (Defrost Termination Sensor Failure) and a while ago it completely shut down and the Controller Alarm was displaying AL61 (Heaters Failure).

    But after i restart everything, it is fine up till now (fingers crossed)

    Are these 2 errors code AL60 and AL61 something serious and do i need to send a technician straight away to rectify the problems?

  41. #291
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    the 5146 software is bad.. Carrier has released 5151 now and it has repaired a few glitches. 5148 is reliable as well if you have that one around.

    Can you open the controller and see if the SMV capacitor is blown? Sometimes the controller will act funny when it tries to control the SMV. Thats usually what the damage isinside the controller from my experience anyway.

    Quote Originally Posted by phil Landon View Post
    hi there was wondering if someone can help.......
    I have been working on a nt40-511-332 box and when it gets thru to P8 on the PTI it gets down to 1.0deg C then goes back into defrost.The box then fails the PTI. I have replaced a set of defrost heaters as they were down to earth. The contrtoller software is 5146. I have had this before and it turned out to be the controller (ML2I). The refrigerant charge sees to be ok and it passes all steps up to the P8. Havent tried the P10 by itself yet, might try that but any hints or tips that anyone can give would be very much appreciated.

    Has anyone had any issues with the 5146 software?


    Thanks very much in advance

  42. #292
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi there Bruisermac, thanks for the reply, I reconfigured the controller and updated the software, still no chnage. I ended up changing the controller and that seemed to solve the problem. the box has since sailed and seems to be ok.

    cheers

  43. #293
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi to all reefer technician and pleasant day to all...

    i want advice from the other techncian who's have a long experience in daikin reefer van

    i wonder what is the common problem of daikin reefer van the compressor is hermetic,....and what is the most important to check up always after PTI

    thank you and take care ^^

  44. #294
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi to all reefers technicians and good day to all
    i have a big probleme with carrier but rearly i need solution .
    the probleme is ice in he pannel reefers alwys reefer is out of range.
    i make defrost ,wather in the evap .but same probleme.
    best regard

  45. #295
    heaviw8's Avatar
    heaviw8 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys,

    1st time here. got an alarm E109 on Daikin unit LXE10E-A1. ANY SUGGESTIONS? I regularly working on TK, Carrier and Mitsubishi but not Daikin. Any help is highly appreciated.

  46. #296
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by heaviw8 View Post
    Hi guys,

    1st time here. got an alarm E109 on Daikin unit LXE10E-A1. ANY SUGGESTIONS? I regularly working on TK, Carrier and Mitsubishi but not Daikin. Any help is highly appreciated.

    hi heaviw8

    i was send e-mail to your e-mail adress. Have you check it?? Whats happen, problem solved??

    see you

    reefermechanic

  47. #297
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi to all reefers technicians and good day to all
    i have a big probleme with carrier but rearly i need solution .
    the probleme is ice in the pannel of supply alwys the reefer is out of range.
    best regard


  48. #298
    Join Date
    Aug 2010
    Location
    ukraine
    Age
    48
    Posts
    4
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    wrong litium battery into controler. Replace battery and softweare.

  49. #299
    Join Date
    Aug 2010
    Location
    ukraine
    Age
    48
    Posts
    4
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by obet View Post
    hi, all power relay replace with new one and the keypad we put also new one but the same problem " emergency program"
    wrong litium battery into controler. Replace battery and softweare.

  50. #300
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hhhhhhhhhmmmmmmmmfffffffffff

    a good day to all of us reefer technician

    i have a problem in my daikin FAILURE of RETURN SENSOR alarm although the unit is running i can't see the display monitoring of RETURN in reefer i want to replace the sensor but i can't find any dealer here in my country so what can i do now???can i use the sensor from the partlow???so can i use again the unit while im waiting to have a brand new return sensor???

    thank u

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 09:11 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 06:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •