    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Sorry for late reply,mate ! I haven't try to change yet coz i haven't spare part yet but i'll be change return air sensor and reply you no sooner.
    Thank you so much for your reply.

  2. #2
    Join Date
    Nov 2009
    Location
    singapore
    Age
    40
    Posts
    11
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Thanks a ton. It's really worked!
    When i was changed return air sensor , the unit is ok and pti pass.....i am quite curious coz the measure the value of ohm is nothing different with the old and new one sensor..? ?

  3. #3
    Join Date
    Nov 2008
    Location
    Surabaya/Indonesia
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi, banana
    Try icebath calibration