Thread: faulty EPR on coldroom
-
18-10-2008, 09:24 AM #1
faulty EPR on coldroom
got a coldroom running off a pack,temp not dropping below 7 degrees,coldroom has 2 searle evaps and they are just sweating at the exp valves,EPR on top of coldroom a block of ice,adjusted it the other day and coldroom ran fine for 2 days,pressure at EPR 75p.s.i,EPR will not adjust and in my mind is goosed,would it matter if i linked it out or would it be best to replace with new,advise please.........
-
18-10-2008, 09:58 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: faulty EPR on coldroom
Ignore!.....
-
18-10-2008, 10:14 AM #3
Re: faulty EPR on coldroom
not that simply when it keeps triggering a rdm alarm........
-
18-10-2008, 10:21 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
18-10-2008, 03:08 PM #5
Re: faulty EPR on coldroom
is this a m@s site?
-
18-10-2008, 04:31 PM #6
Re: faulty EPR on coldroom
-
18-10-2008, 06:15 PM #7
Re: faulty EPR on coldroom
I'm sure Fazza is the person who got a job with City recently. Without checking the old thread im not certain.
Anyway as Gary says, we need more info.
-
18-10-2008, 06:22 PM #8
Re: faulty EPR on coldroom
pack is on 404a,pressure at condensing unit is 50p.s.1,pressure at EPR 75p.s.1,sorry not got reading at evaporator will check that on monday when i return.
-
18-10-2008, 07:45 PM #9
Re: faulty EPR on coldroom
Last edited by Gary; 18-10-2008 at 07:50 PM.
-
18-10-2008, 09:39 PM #10
Re: faulty EPR on coldroom
the epr is open fully no adjustment left,no other devices between epr and unit,pack runs about 20 metres of multidecks and 2x coldrooms,just getting high temp on this coldroom
-
18-10-2008, 09:53 PM #11
Re: faulty EPR on coldroom
-
18-10-2008, 09:57 PM #12
Re: faulty EPR on coldroom
Are we talking about an electronic EPR? And is the frost just on the pack side of the valve?
If it ain't broke, it doesn't have enough features yet.
Damo
-
18-10-2008, 10:12 PM #13
Re: faulty EPR on coldroom
just your standard alan key adjusting value,the best i could get it to adjust to at epr on friday was 58p.s.i,just dialled into store and coldroom back at temp,****y e.pr?
-
19-10-2008, 08:13 AM #14
Re: faulty EPR on coldroom
If its your standard Danfoss EPR that they tend to install in this country then it sounds like its fubar. You should be able to wind that sucker right down.
-
19-10-2008, 08:39 AM #15
Re: faulty EPR on coldroom
If its just a case of poor suction pressure control.
Change the epr as it sounds as if it's passing.
Do not bypass it!
Grizzly
-
19-10-2008, 11:10 AM #16
-
21-10-2008, 09:03 AM #17
Re: faulty EPR on coldroom
do not bypass this epr you really must change this for new as your room will be operating at diff temp from the multi decks so instead of fitting a satilite system to the pack you install epr valves to achive the presure change you will also find this a lot on fresh meat cases on packs
-
21-10-2008, 12:31 PM #18
Re: faulty EPR on coldroom
wat is the pressure range on the epr ? it will say on the body .ie 0-60 psi ?
it could be the inserts in the tevs .are to big ?
-
21-10-2008, 12:32 PM #19
Re: faulty EPR on coldroom
tevs may have been adjusted to much
-
21-10-2008, 06:34 PM #20
Re: faulty EPR on coldroom
75 psi would giv you a evaporating temp of about +1.no way will the room come down to temp.50 psi about -8,it looks like its u/s to me . fit a new valve
-
18-11-2008, 07:06 PM #21
-
18-11-2008, 07:45 PM #22
Re: faulty EPR on coldroom
We need the pressures both before and after the valve, because the upstream pressure can't get any lower than the downstream pressure no matter how much you adjust it.
For example, if for some reason the suction pressure at the condensing unit goes up to 100psi, then the EPR pressure will go up to 100psi, regardless of the setting.Last edited by Gary; 18-11-2008 at 08:08 PM.
-
19-11-2008, 09:32 AM #23
-
19-11-2008, 05:24 PM #24
-
19-11-2008, 07:22 PM #25
Re: faulty EPR on coldroom
Each time he tells us the upstream pressure, we also need to know the downstream pressure.
Similar Threads
-
new coldroom installation
By chilltech in forum FundamentalsReplies: 8Last Post: 23-07-2009, 05:38 PM -
Ice Maker (Nice Ice) Faulty: Help!
By ArthurLeigh in forum CommercialReplies: 4Last Post: 25-10-2008, 10:49 AM -
0C Coldroom Evaporator operating at 20C
By samiam in forum System OptimizationReplies: 6Last Post: 29-09-2008, 11:24 PM -
problems with coldroom icing up
By goody in forum Trouble ShootingReplies: 40Last Post: 28-03-2008, 06:26 PM -
FH4518Y comp faulty
By Jus Walker in forum CommercialReplies: 1Last Post: 19-07-2006, 10:34 PM