    faulty EPR on coldroom



    got a coldroom running off a pack,temp not dropping below 7 degrees,coldroom has 2 searle evaps and they are just sweating at the exp valves,EPR on top of coldroom a block of ice,adjusted it the other day and coldroom ran fine for 2 days,pressure at EPR 75p.s.i,EPR will not adjust and in my mind is goosed,would it matter if i linked it out or would it be best to replace with new,advise please.........



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: faulty EPR on coldroom

    Ignore!.....

  3. #3
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: faulty EPR on coldroom

    not that simply when it keeps triggering a rdm alarm........

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: faulty EPR on coldroom

    Quote Originally Posted by fazzamouse View Post
    not that simply when it keeps triggering a rdm alarm........
    I mean ignore my post because there is no possibility for me to erase it!

  5. #5
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: faulty EPR on coldroom

    is this a m@s site?

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: faulty EPR on coldroom

    Quote Originally Posted by fazzamouse View Post
    ... pressure at EPR 75p.s.i,...
    Telling us the pressure is meaningless if we don't know what refrigerant is in the system... and we would need to know the pressure both upstream and downstream from the EPR.

  7. #7
    Join Date
    Aug 2007
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: faulty EPR on coldroom

    I'm sure Fazza is the person who got a job with City recently. Without checking the old thread im not certain.

    Anyway as Gary says, we need more info.

  8. #8
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: faulty EPR on coldroom

    pack is on 404a,pressure at condensing unit is 50p.s.1,pressure at EPR 75p.s.1,sorry not got reading at evaporator will check that on monday when i return.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: faulty EPR on coldroom

    Quote Originally Posted by fazzamouse View Post
    pack is on 404a,pressure at condensing unit is 50p.s.1,pressure at EPR 75p.s.1,sorry not got reading at evaporator will check that on monday when i return.
    Are there any devices between the EPR and the condensing unit that might be restricting? It's possible that there might be a SORIT valve or similar device at the suction manifold.

    Will the EPR adjust to a higher pressure?
    Last edited by Gary; 18-10-2008 at 07:50 PM.

  10. #10
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: faulty EPR on coldroom

    the epr is open fully no adjustment left,no other devices between epr and unit,pack runs about 20 metres of multidecks and 2x coldrooms,just getting high temp on this coldroom

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: faulty EPR on coldroom

    Quote Originally Posted by fazzamouse View Post
    the epr is open fully no adjustment left
    Does adjusting it in the other direction change the pressure? If it will adjust above 75psi but not below, then the inlet is restricted.

  12. #12
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: faulty EPR on coldroom

    Are we talking about an electronic EPR? And is the frost just on the pack side of the valve?
    If it ain't broke, it doesn't have enough features yet.


    Damo

  13. #13
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: faulty EPR on coldroom

    just your standard alan key adjusting value,the best i could get it to adjust to at epr on friday was 58p.s.i,just dialled into store and coldroom back at temp,****y e.pr?

  14. #14
    Join Date
    Aug 2007
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: faulty EPR on coldroom

    If its your standard Danfoss EPR that they tend to install in this country then it sounds like its fubar. You should be able to wind that sucker right down.

  15. #15
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: faulty EPR on coldroom

    If its just a case of poor suction pressure control.
    Change the epr as it sounds as if it's passing.
    Do not bypass it!
    Grizzly

  16. #16
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: faulty EPR on coldroom

    Quote Originally Posted by fazzamouse View Post
    pack is on 404a,pressure at condensing unit is 50p.s.1,pressure at EPR 75p.s.1,sorry not got reading at evaporator will check that on monday when i return.

    Sounds like the suction pipe between cold room & pack is too small or overloaded! 25psi pressure drop is excessive..

    possibly it may be the scenario that when other decks go offline the suction pipecopes with the load.

    Billy Ray

  17. #17
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: faulty EPR on coldroom

    do not bypass this epr you really must change this for new as your room will be operating at diff temp from the multi decks so instead of fitting a satilite system to the pack you install epr valves to achive the presure change you will also find this a lot on fresh meat cases on packs

  18. #18
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: faulty EPR on coldroom

    wat is the pressure range on the epr ? it will say on the body .ie 0-60 psi ?
    it could be the inserts in the tevs .are to big ?

  19. #19
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: faulty EPR on coldroom

    tevs may have been adjusted to much

  20. #20
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: faulty EPR on coldroom

    75 psi would giv you a evaporating temp of about +1.no way will the room come down to temp.50 psi about -8,it looks like its u/s to me . fit a new valve

  21. #21
    Join Date
    Sep 2007
    Location
    sydney australia
    Posts
    8
    Rep Power
    0

    Re: faulty EPR on coldroom

    Quote Originally Posted by Billy Ray View Post
    Sounds like the suction pipe between cold room & pack is too small or overloaded! 25psi pressure drop is excessive..

    possibly it may be the scenario that when other decks go offline the suction pipecopes with the load.

    Billy Ray

    The EPR is the restriction. There is obviously a problem with the valve. The EPR's job is to restrict flow to raise the backpressure to the required SET of the Room.

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: faulty EPR on coldroom

    Quote Originally Posted by fazzamouse View Post
    just your standard alan key adjusting value,the best i could get it to adjust to at epr on friday was 58p.s.i,just dialled into store and coldroom back at temp,****y e.pr?
    We need the pressures both before and after the valve, because the upstream pressure can't get any lower than the downstream pressure no matter how much you adjust it.

    For example, if for some reason the suction pressure at the condensing unit goes up to 100psi, then the EPR pressure will go up to 100psi, regardless of the setting.
    Last edited by Gary; 18-11-2008 at 08:08 PM.

  23. #23
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: faulty EPR on coldroom

    Quote Originally Posted by andyrobbo View Post
    The EPR is the restriction. There is obviously a problem with the valve. The EPR's job is to restrict flow to raise the backpressure to the required SET of the Room.
    andyrobbo is in da house!!! when do you lob in sydney again pugz?
    ...and she said "give it to me you big fridgie"

  24. #24
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: faulty EPR on coldroom

    Quote Originally Posted by Gary View Post
    We need the pressures both before and after the valve, because the upstream pressure can't get any lower than the downstream pressure no matter how much you adjust it.

    For example, if for some reason the suction pressure at the condensing unit goes up to 100psi, then the EPR pressure will go up to 100psi, regardless of the setting.


    Gary it does say in 1 of his posts

  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: faulty EPR on coldroom

    Each time he tells us the upstream pressure, we also need to know the downstream pressure.

Similar Threads

  1. new coldroom installation
    By chilltech in forum Fundamentals
    Replies: 8
    Last Post: 23-07-2009, 05:38 PM
  2. Ice Maker (Nice Ice) Faulty: Help!
    By ArthurLeigh in forum Commercial
    Replies: 4
    Last Post: 25-10-2008, 10:49 AM
  3. 0C Coldroom Evaporator operating at 20C
    By samiam in forum System Optimization
    Replies: 6
    Last Post: 29-09-2008, 11:24 PM
  4. problems with coldroom icing up
    By goody in forum Trouble Shooting
    Replies: 40
    Last Post: 28-03-2008, 06:26 PM
  5. FH4518Y comp faulty
    By Jus Walker in forum Commercial
    Replies: 1
    Last Post: 19-07-2006, 10:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •