temp out of control
what can cause a system which has suction 26PSI discharge 195 psi and 28F at the end of tvx to go to > 60 F when you add refrigerant to it that give suction 44 psi and discharge 225 psi
-
08-10-2008, 03:52 AM #2
Re: temp out of control
Your question doesn't make any sense. Try again.
-
08-10-2008, 06:04 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: temp out of control
Who gives you this "academic" questions.
Maybe, if you present them in original form, you end up with right answers much faster.
-
09-10-2008, 02:04 AM #4
Re: temp out of control
I restart the system but it stay at 52F
i try to be short but it's the original form
-
09-10-2008, 06:02 PM #5
Re: temp out of control
where you have 52F??? evap?? condensor outside ?? before TEV or after ??? more info please
Ice
-
09-10-2008, 11:55 PM #6
Re: temp out of control
after TEV. Condenser outside . subcooling 3.33F. superheat -5F
-
10-10-2008, 12:56 AM #7
Re: temp out of control
after TEV. Condenser outside . subcooling 3.33F. superheat 45F
-
10-10-2008, 06:16 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: temp out of control
Originally Posted by Gary
Or, if you prefer graphical representation of system something like this:
http://www.refrigeration-engineer.co...ad.php?t=15303Last edited by nike123; 10-10-2008 at 06:23 AM.
-
14-10-2008, 06:32 PM #9
Re: temp out of control
This is a kind of chiller (pool) but water is not flow out.
Without load on it we find
Liquid line 96 F
Suction line 65 F
Condenser 89.6 F
Climate 93.2 F
Saturated Suction 5.2 F
Saturated condensing 101 F
-
14-10-2008, 06:40 PM #10
Re: temp out of control
what is the application?
whats the gas?
-
14-10-2008, 06:54 PM #11
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: temp out of control
Cond air in temp?
Cond air out temp?
What is "condenser" and "climate"?
What you mean by "but water is not flow out"?
If "climate" is ambient air temperature and "condenser" is condenser air out temperature, than that numbers doesn't make sense!
What you mean "without load"?
Last edited by nike123; 14-10-2008 at 07:01 PM.
-
14-10-2008, 08:28 PM #12
Re: temp out of control
gas r22
water chiler
climate temp is the temp arount the system
condenser temp is the temp i found on the oposite face of the conderser blower
-
14-10-2008, 08:38 PM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
14-10-2008, 08:51 PM #14
Re: temp out of control
the blower of the condenser is an aspiration one
normaly the load is the water i want to cool . when it's empty i said it is without load
-
14-10-2008, 10:44 PM #15
Re: temp out of control
-
15-10-2008, 07:38 AM #16
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
15-10-2008, 06:43 PM #17
Re: temp out of control
have you got load on the cooler?
i assume that you have a good water flow.
Similar Threads
-
Temp. Rise at duct outlet
By jwasir in forum Trouble ShootingReplies: 13Last Post: 10-05-2008, 04:22 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Control scenario
By Mike Hopkins in forum Technical DiscussionsReplies: 5Last Post: 14-09-2007, 11:25 AM -
New Capacity Control Solution
By embrown in forum New TechnologiesReplies: 19Last Post: 30-12-2003, 01:33 PM