    temp out of control



    what can cause a system which has suction 26PSI discharge 195 psi and 28F at the end of tvx to go to > 60 F when you add refrigerant to it that give suction 44 psi and discharge 225 psi



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: temp out of control

    Your question doesn't make any sense. Try again.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: temp out of control

    Who gives you this "academic" questions.
    Maybe, if you present them in original form, you end up with right answers much faster.

  4. #4
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: temp out of control

    I restart the system but it stay at 52F
    i try to be short but it's the original form

  5. #5
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: temp out of control

    where you have 52F??? evap?? condensor outside ?? before TEV or after ??? more info please

    Ice

  6. #6
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: temp out of control

    after TEV. Condenser outside . subcooling 3.33F. superheat -5F

  7. #7
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: temp out of control

    after TEV. Condenser outside . subcooling 3.33F. superheat 45F

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: temp out of control

    Quote Originally Posted by Gary
    For a proper evaluation, we need the following information:

    Low side:

    Evap air in temp
    Evap air out temp
    Saturated suction temp (SST) converted from pressure
    Suction line temp at evap outlet

    High side:

    Cond air in temp
    Cond air out temp
    Saturated condensing temp (SCT) converted from pressure
    Liquid line temp at receiver outlet
    __________________

    Or, if you prefer graphical representation of system something like this:
    http://www.refrigeration-engineer.co...ad.php?t=15303
    Last edited by nike123; 10-10-2008 at 06:23 AM.

  9. #9
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: temp out of control

    This is a kind of chiller (pool) but water is not flow out.
    Without load on it we find
    Liquid line 96 F
    Suction line 65 F
    Condenser 89.6 F
    Climate 93.2 F

    Saturated Suction 5.2 F
    Saturated condensing 101 F

  10. #10
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: temp out of control

    what is the application?
    whats the gas?

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: temp out of control

    Cond air in temp?
    Cond air out temp?

    What is "condenser" and "climate"?
    What you mean by "but water is not flow out"?
    If "climate" is ambient air temperature and "condenser" is condenser air out temperature, than that numbers doesn't make sense!
    What you mean "without load"?
    Last edited by nike123; 14-10-2008 at 07:01 PM.

  12. #12
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: temp out of control

    gas r22

    water chiler

    climate temp is the temp arount the system

    condenser temp is the temp i found on the oposite face of the conderser blower

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: temp out of control

    Quote Originally Posted by nike123 View Post

    If "climate" is ambient air temperature and "condenser" is condenser air out temperature, than that numbers doesn't make sense!
    What you mean "without load"?
    Quote Originally Posted by payoute View Post
    climate temp is the temp arount the system

    condenser temp is the temp i found on the oposite face of the conderser blower
    What you mean by "without load"?
    Describe evaporator!

    Why I have feeling like I am pulling informations you hesitate to give?
    Or it is language barrier?

  14. #14
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: temp out of control

    the blower of the condenser is an aspiration one

    normaly the load is the water i want to cool . when it's empty i said it is without load

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: temp out of control

    Quote Originally Posted by payoute View Post
    This is a kind of chiller (pool) but water is not flow out.
    Without load on it we find
    Liquid line 96 F
    Suction line 65 F
    Condenser 89.6 F
    Climate 93.2 F

    Saturated Suction 5.2 F
    Saturated condensing 101 F
    101F minus 96F = 5F subcooling.

    Add refrigerant until the subcooling is 15F.

    Then take all of these measurements again... with load.

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: temp out of control

    Quote Originally Posted by payoute View Post
    the blower of the condenser is an aspiration one

    normaly the load is the water i want to cool . when it's empty i said it is without load
    Sorry, aspiration condenser is something I never heard or saw.

    How you move water around evaporator, or it moves naturally?

  17. #17
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: temp out of control

    have you got load on the cooler?
    i assume that you have a good water flow.

Similar Threads

  1. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Replies: 13
    Last Post: 10-05-2008, 04:22 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  4. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •