    2 Stage unit blowing



    I was asked this at the weekend wen a bit out of it which didn't help matters. Bassicly it's a 2 stage unit, R507 to R1150, 2 compressers.

    The 1st stage fire up fine and pull down to temp then the 2nd starts and pulls to temp fine, both stages running fine.

    Soon as any load is put on the system from idel bang it trips out and trips the mains RCD.

    It has been fine but randomly started doing this.

    The unit is run off an externsion lead, could this be at fault or is it doggy house hold electricals as it has worked fine in 3 different places!

    It's a 240v single phase on each compresser



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 2 Stage unit blowing

    Unsure as to why the unit should trip when 'loading up' as it must already be loaded when it starts.

    However, yes check the power supply.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2008
    Location
    Bristol
    Posts
    48
    Rep Power
    0

    Re: 2 Stage unit blowing

    Quote Originally Posted by Brian_UK View Post
    Unsure as to why the unit should trip when 'loading up' as it must already be loaded when it starts.

    However, yes check the power supply.
    It's a cooling unit for the CPU of a PC. 260W heat load is whats put on the system once running. The load it's cooling can't be there till the evap ia at -100c cos the PC/CPU will blow and then need to pay £1000 for a new one!

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Replies: 3
    Last Post: 04-03-2007, 07:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •