    apac indoor fan motor blowing fuses



    workin on an apac unit indoor model S0321hcsaa,
    with three phase belt driven indoor fan motor,rated amps 3.6 running at 2.9 amps .continously blowin fuses two sometimes all three .have meggered motor windin and supply cables all ok .overload set at 4 amps. voltage balanced on all windings .resistance winding balanced all 6.8ohms.

    cld I be missing something .\
    this happens after some months .



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: apac indoor fan motor blowing fuses

    Don't know what area the unit is in but start checking the power wiring.

    I recently had a system start blowing fuses when the mechanics all checked out OK.

    Found bad wiring inside a switched isolator which had corroded due to moisture. Every now and then the moisture would create an electrical short across the phases and blow the fuses.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: apac indoor fan motor blowing fuses

    Brian has a good point there!
    You might like to check the incoming voltages as well.
    Heavy fluctuations of these would have an influance upon the Amperages being drawn.
    If you have the time and option available ?
    You could always leave a clamp meter on set to record max amp drawn.
    Grizzly
    What sort of time scale are we talking about between fuses blowing?

  4. #4
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: apac indoor fan motor blowing fuses

    Grizly ,time scale is once in every 2months we now keep extra fuses on site ,
    too bad hey.Hw is the max amp record gonna help me thot they blow because exceed fuse rated amperage.
    thanks guys wil implement ur sugestions .