    Talking a/c fault



    Hi all
    Heres a easy question to answer
    (the fault stemmed from installation)
    Small paper shop two seperate ceiling suspended a/c units electrical supplied to outside c/u (single phase).Inside ahu fed via interconnecting cable.(single phase)Each a/c independantly controlled via controller.
    The area suffers a power cut in storms ,power comes back on circuit breaker tripped on one unit customer resets breaker.
    He then decides to switch one a/c off via controller.
    What happend to a/c systems?

    regards mark



  2. #2
    shogun7's Avatar
    shogun7 Guest
    In comming line feeds both circuit breakers but line is too small for both units pulling LRA so the weakest CB trips is a possibility me thinks
    cheers what
    Last edited by shogun7; 21-02-2004 at 04:54 AM.

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Post a/c fault

    ok, the two a/cs functioned ok until one controller was turned off,



    mark

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    One unit outside or bisplit?
    Electonically controlled?

    Otherwise, a gues... supplies switched, setting off one indoor unit but outside unit keeps cooling a non powered inside unit and freezes completely??
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    a/c fault

    Hi peter

    2 a/cs in papershop.

    1x ahu fed by 1x c/u.
    1x ahu fed by 1x c/u.

    Both electronic no thrills hard wired controller for each system.

    mark

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    mark,


    if the main switch was on and the guy swichd it off by the controller, so it went off.

    chemi

  7. #7
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Post a/c fault

    ok ,I will elaborate i was asked by an engineer if i could attend site with him and find wiring fault?.


  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    its not common, but some times, un experianced tech's, connect one c/u of one ac to the other one's ahu.

    I mean ofcours the controls.

    chemi

  9. #9
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Post a/c fault

    Hi all

    The two a/cs would work together cooling,heating .
    When the circuit breaker tripped originally one ahu came back on and would not function normally,the manager manually reset circuit breaker and noticed the strange operation and consequently turned circuit breaker off .The engineer attended site tested reset circuit breaker both a/cs worked ,When the customer turned one unit off by controller both stopped heating (as per command from one controller) and shop ambient dropped.
    I get a phone call can you attend a job to locate wiring fault get to site find out the cowboys who installed had crossed ahu feed from the condensing unit ummmm the units had worked like this since installed and had gone un-noticed.Lol


    regards mark


  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    mark,

    I saw something even worse.

    I was called to look at a 20000 L milk tank that had cooling problems. it turned out that the cowboy (a compliment in this case) had crossed the suction and liquid line from two c/u!!

    chemi

Similar Threads

  1. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  2. Chigo Cpa-09co Fault Codes? E4?
    By chigosimon in forum Trouble Shooting
    Replies: 5
    Last Post: 24-11-2007, 12:46 AM
  3. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Replies: 3
    Last Post: 31-10-2006, 07:43 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •