    evaporator?



    Have searched the web for info on these evaps and found nothing.Anyone know where I can get some info on these(TD,BTU ect)?Here are some numbers...blanchard ness model#LS-631-A8.and model#LS-989-E6......Thanks!!
    Last edited by cretan; 01-10-2008 at 07:12 PM.



  2. #2
    chaser1013's Avatar
    chaser1013 Guest

    Re: evaporator?

    I scaned two pages, with any luck I have attached them. Hope this helps.

  3. #3
    chaser1013's Avatar
    chaser1013 Guest

    Re: evaporator?

    Ok, my scanned file is too large to attach. Here is the short version of what I have.

    LS-631-A8 is 6270 BTU @ 10 FDT or 9405 @ 15 FDT, 900CFM, one motor @ 2amps.

    Could the LS-989-E6 be LS-981-E6? I do not find a LS-989-E6.

    LS-981-E6 is 9800 BTU @ +20 evap or 8330 BTU @
    -20 evap, 1650cfm, 2motors @ 2amps each, Heat 3100watts 8.8amps.

    Hope this helps.

  4. #4
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: evaporator?

    Thanks for reply.The last digit looks like a 0 or 9(can't tell for sure).So it may be a LS-980.Do you have specs for a LS-980?

  5. #5
    chaser1013's Avatar
    chaser1013 Guest

    Re: evaporator?

    LS models that end in E6 are
    MODEL +20 -20 #OF FANS
    LS-0501-ES 5000 4250 1
    LS-0571-ES 5700 4850 1
    LS-0841-ES 8400 7140 2
    LS-0981-ES 9800 8330 2
    LS-1131-ES 11300 9605 2
    LS-1421-ES 14200 12070 3
    LS-1691-ES 16900 14365 3
    LS-2261-ES 22800 19210 4
    LS-2821-ES 28100 23970 5
    LS-3301-ES 33000 28050 6

    I have an old Blanchard Ness catalog scanned in a pdf file, but it is too large to attach here. It is
    14,635 KB.

  6. #6
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: evaporator?

    Thanks for the info.One question if I may?I am working on a walk-in cooler.Size is 7x12x7.On the quick reference guide it shows 7000 btu average use and 9400 heavy use.Evap is rated at 631btu per degree.This is my first install.I am going with a water cooled condensor.404 gas.what size condensing unit is a good choice and matching txv?

  7. #7
    chaser1013's Avatar
    chaser1013 Guest

    Re: evaporator?

    A cond unit rated at 9,600 BTU to 10,000 BTU at your cond temp and 15 degree evap temp.

    1/2 ton expansion valve with SC charge.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Evaporator TD and refrigeration effect
    By nambiandy in forum Fundamentals
    Replies: 2
    Last Post: 11-10-2008, 11:39 AM
  3. Absortpion Refrigeration - Evaporator Basics
    By knudo in forum Fundamentals
    Replies: 4
    Last Post: 28-08-2007, 08:03 AM
  4. What is the best location for a evaporator fan?
    By Jasno999 in forum Fundamentals
    Replies: 3
    Last Post: 21-02-2007, 12:34 AM
  5. Change evaporator
    By tralex in forum Fundamentals
    Replies: 6
    Last Post: 29-12-2005, 07:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •