    single phase scroll comp direction



    can a single phase scroll comp run the wrong direction if so hw do we reverse the direction



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: single phase scroll comp direction

    Single phase comressors, regardless of the type, can only turn to one direction.

    Nothing to worry about.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: single phase scroll comp direction

    They will run the correct way if they are wired correctly and the capacitor is ok.

    What can happen if the power goes off for a second is that when the power comes back on, the compressor is spinning backwards (as many scrolls do when the power is removed) and it will continue to do so now the power is back on until turned off long enough for it to stop and then restarted. Or it trips on internal overload and then starts up ok when it resets.

    Jon

Similar Threads

  1. Single Phase Compressor Connections
    By Grizzly in forum Electrical
    Replies: 2
    Last Post: 06-05-2008, 12:25 AM
  2. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  3. Variable speed drives for single phase motors
    By PRESS in forum Air Conditioning
    Replies: 10
    Last Post: 10-12-2007, 07:23 PM
  4. Single stage Vs 2 stage comp rack
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 01-02-2007, 03:05 PM
  5. Single phase contactor
    By Andy T in forum Commercial
    Replies: 9
    Last Post: 23-10-2006, 01:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •