    Question Accidentally mixed R404A with R134a



    Dear All,

    We had compressor Danfoss MTZ28-4 for food chiller using R404A. Unfortunately our team member did not realize that the compressor is use R404A, he took R134A which we use for our HVAC system to recharge the food chiller. After desired suction pressure reached then he just realize he made mistaken. Now our food chiller still opreating, but cannot reach temperature setting (0-5 degC)? What would happen with our chiller system? Can we recharge it again with R404A to make the lower temperature? Thank you



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Accidentally mixed R404A with R134a

    Remove wrong refrigerant as much as possible with recovery unit and restart with the right refrigerant. Vacuum is not necessary because R404a consists of R134a.
    It will never work and your TEV or capillary is not designed for this refrigerant.
    If you want to destroy your compressor, let it run this way.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. R134a Vs R404A
    By Julia in forum Refrigerants
    Replies: 2
    Last Post: 20-09-2007, 07:30 PM
  3. R134a or R404a
    By jingua_ph in forum Refrigerants
    Replies: 4
    Last Post: 27-09-2006, 03:31 PM
  4. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Replies: 0
    Last Post: 28-02-2005, 09:05 AM
  5. Replies: 5
    Last Post: 01-03-2004, 09:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •