    Condensing Unit



    What would happen to the capacity of a condensing unit if you 1/2" Instead of 5/8" Suction and 3/8" instead of 1/2" for the pipe run which is about 25m? The Condensing Unit is a Maneurop MCZC054MTA02G. The units are outside about 3m high.



  2. #2
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: Condensing Unit

    It would definetley reduce but by how much I dont know.
    High discharge pressure, evap being starved of enough liquid, longer run time, poor performence and excessive wear on the plant are a few of things that will occurr. you may get it to work but not as it should.

  3. #3
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Condensing Unit

    Well assuming its not a capillary system and that the original pipe sizing is correct then you'll see a lower suction pressure and a pressure drop between evap and comp in the suction line, this will increase at higher loads. You will experience longer run times due to this PD and a lot more energy input to do the work, so if your unit is borderline on the sizing it may struggle a max design conditions. On the liquid side you may also experience a pressure drop which if you don't have a good amount of subcooling can end up flashing off liquid and decreasing your capacity as well.
    Last edited by 750 Valve; 13-08-2008 at 01:49 PM.
    ...and she said "give it to me you big fridgie"

  4. #4
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Condensing Unit

    why would you even consider doing it ? its a long pipe run and if anything they need to go up a size not down and fit a oil seperator , why look for trouble.

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Condensing Unit

    this is a stupid thing to even consider IMO are you qualified? Never undersize your piping, the reasons given here should be evidence enough!

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. condensing unit selection?
    By ibraheem in forum Technical Speculations
    Replies: 0
    Last Post: 28-05-2008, 06:06 PM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. TXV sizing with a larger condensing unit
    By kengineering in forum Technical Discussions
    Replies: 13
    Last Post: 27-08-2007, 10:44 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •