Condensing Unit
What would happen to the capacity of a condensing unit if you 1/2" Instead of 5/8" Suction and 3/8" instead of 1/2" for the pipe run which is about 25m? The Condensing Unit is a Maneurop MCZC054MTA02G. The units are outside about 3m high.
-
13-08-2008, 01:31 PM #2
Re: Condensing Unit
It would definetley reduce but by how much I dont know.
High discharge pressure, evap being starved of enough liquid, longer run time, poor performence and excessive wear on the plant are a few of things that will occurr. you may get it to work but not as it should.
-
13-08-2008, 01:46 PM #3
Re: Condensing Unit
Well assuming its not a capillary system and that the original pipe sizing is correct then you'll see a lower suction pressure and a pressure drop between evap and comp in the suction line, this will increase at higher loads. You will experience longer run times due to this PD and a lot more energy input to do the work, so if your unit is borderline on the sizing it may struggle a max design conditions. On the liquid side you may also experience a pressure drop which if you don't have a good amount of subcooling can end up flashing off liquid and decreasing your capacity as well.
Last edited by 750 Valve; 13-08-2008 at 01:49 PM.
...and she said "give it to me you big fridgie"
-
13-08-2008, 02:33 PM #4
Re: Condensing Unit
why would you even consider doing it ? its a long pipe run and if anything they need to go up a size not down and fit a oil seperator , why look for trouble.
-
13-08-2008, 10:17 PM #5
Re: Condensing Unit
this is a stupid thing to even consider IMO are you qualified? Never undersize your piping, the reasons given here should be evidence enough!
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
condensing unit selection?
By ibraheem in forum Technical SpeculationsReplies: 0Last Post: 28-05-2008, 06:06 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
TXV sizing with a larger condensing unit
By kengineering in forum Technical DiscussionsReplies: 13Last Post: 27-08-2007, 10:44 PM -
Matching Evaporator with Condensing Unit
By Abe in forum Technical DiscussionsReplies: 12Last Post: 25-07-2001, 08:57 AM