    Liquid solenoid valve mystery



    Could any body give me an explanation for this performance of the liquid solenoid valve. when it was tested outside the refrigeration cycle it worked properly but when it was installed it is stuck and after 10 minutes when the current supply is given again to the valve elect. coil the valve opens and works. I changed the elect coil from 11 W (0.45 Amp & 24 V) to 20 W (0.8 Amp & 24 V) the same problem is existing. Although the manufacturer's catalog 's recommended coil of 11 W for this solenoid valve. So any body can explain what is happened and how to solve/ avoid this problem. Unfortunately, the maximum power is 20 W for this brand (which is working in hazardous area) and after that we have to go to AC not DC.

    Any participation is highly appreciated

    Best regards'

    Mohamed



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Liquid solenoid valve mystery

    Is it a direct-acting solenoid or one that is pilot-operated?
    If all else fails, ask for help.


  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Liquid solenoid valve mystery

    Was it installed in the right direction?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Liquid solenoid valve mystery

    Ok thanks all for your participation it was instated correctly and it is pilot type EVR 20. During the pump down time the discharge pressure reaches 280 PSI and suction pressure 30 PSI this after the solenoid valve closing directly. however, as it was observed that during valve activation to run the system only a very low magnetic field you can feel. And when it is stopped and waiting for almost 10 minutes until the discharge pressure reaches 200 PSI and suction 100 PSI when the valve is activated at this condition it works well. I think that the low magnetic field makes the valve plunger to lift up little bit and infiltration of refrigerant escapes from the upper diaphragm of the valve to the lower side and so the pressure reaches to this value of 200 PSI and 200 PSI. At this moment the restrained pressure above the diaphragm has been released and the diaphragm goes up making full opening for the valve. However, what makes me confused why the plunger was not drawn up although the resistive force is only its weight and the spring force. I wonder the restrained pressure 250 PSI has an influence on the plunger also or not. And why the magnetic field is very low at this moment, any body can explain to me this dilemma and what is the proper solution and many thanks in advance.

    Regards
    Mohamed
    Last edited by mohamed khamis; 25-07-2008 at 07:34 AM. Reason: amedmemnt

  5. #5
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Liquid solenoid valve mystery

    EVR20 is the valve largest with a diaphragm in this range. (the lift of the diafragm is the highest in this range)
    Maximum opening pressure differential with a 20 Watt DC coil is 16 bar (approx. 230 psi) ...
    Which coil do you use (code number)?
    Last edited by BESC5240; 25-07-2008 at 07:57 AM.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid solenoid valve mystery

    The plunger seating is magnetic-permeable. When the coil is dc, the seating magnetises and remains magnetised even when the coil is not engaged, especially in train installations because of the dc field of airwire. Therefore the seating pulls the plunger.
    Increasing the power of the coil doesn't help because the field is applied on the plunger, but also over and under it.
    The only possibility is to increase the voltage (if 24 Vdc, apply 30 or more volts, of 110 Vdc, apply 150 or more Vdc). This does not happen with ac coils.

  7. #7
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by BESC5240 View Post
    EVR20 is the valve largest with a diaphragm in this range. (the lift of the diafragm is the highest in this range)
    Maximum opening pressure differential with a 20 Watt DC coil is 16 bar (approx. 230 psi) ...
    Which coil do you use (code number)?
    ok thanks for your input I used firstly a coil of 12 DC W the number is code 018z6596 then when it was not able to work properly. I changed the coil to 20 DC W and the code number is 018F6857. could u clarify what do u mean Maximum opening pressure differential is 16 bar. As I understand that the difference between the pressure before the diaphragm (outlet from the condenser) and the pressure after diaphragm (inlet to TXV) is 16 bar or what?. Once again I do appreciate ur participation

  8. #8
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by NoNickName View Post
    The plunger seating is magnetic-permeable. When the coil is dc, the seating magnetises and remains magnetised even when the coil is not engaged, especially in train installations because of the dc field of airwire. Therefore the seating pulls the plunger.
    Increasing the power of the coil doesn't help because the field is applied on the plunger, but also over and under it.
    The only possibility is to increase the voltage (if 24 Vdc, apply 30 or more volts, of 110 Vdc, apply 150 or more Vdc). This does not happen with ac coils.
    Thanks but the supply current comes from PLC and this refrigeration system is installed in offshore (oil &gas plant) and it must be DC and explosion proof. The PLC apply only 24 VDC. Any another solution will be highly appreciated.

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by mohamed khamis View Post
    Thanks but the supply current comes from PLC and this refrigeration system is installed in offshore (oil &gas plant) and it must be DC and explosion proof. The PLC apply only 24 VDC. Any another solution will be highly appreciated.
    Is it really 24Vdc? or something less that 24....?
    Do you have big iron parts in the vicinity?
    Do you have big DC buses in the vicinity?

    Try a 12Vdc coil or change the power supply to 24Vac.

  10. #10
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by mohamed khamis View Post
    ok thanks for your input I used firstly a coil of 12 DC W the number is code 018z6596 then when it was not able to work properly. I changed the coil to 20 DC W and the code number is 018F6857. could u clarify what do u mean Maximum opening pressure differential is 16 bar. As I understand that the difference between the pressure before the diaphragm (outlet from the condenser) and the pressure after diaphragm (inlet to TXV) is 16 bar or what?. Once again I do appreciate ur participation
    018Z6596 is a 10 W DC coil (for Atex application). You should use at least this 20 W DC coil (018F6857).

    You should also make sure that you have the 'DC-version' of the valve. The plunjer (or armature, as we call it) is different from an AC-version: it is round, in stead of a square; this gives a bigger surface for the magnetic flux (and will increase the electromagnetic pulling force).

    MOPD is the maximum pressure difference between the inlet and the outlet of the valve. Due to the construction, each valve has it's MOPD, depending on the coil used.

  11. #11
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by NoNickName View Post
    Is it really 24Vdc? or something less that 24....?
    Do you have big iron parts in the vicinity?
    Do you have big DC buses in the vicinity?

    Try a 12Vdc coil or change the power supply to 24Vac.
    It is theoretically 24 VDC but practically 22 to 23 VDC


    No big iron parts nor big DC buses. are you sure the change to 12 VDC will help...The using of AC source is quite restricted in hazardous area such as offshore oil and gas platform, pls suggest

  12. #12
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by mohamed khamis View Post
    It is theoretically 24 VDC but practically 22 to 23 VDC
    The relation between the pulling force, K and the voltage applied, U is:

    K=k.(U/R)²

    So a drop in voltage of 10% will lead to a drop in force of 20% (19%).

    Also the temperature has an on fluence on K. (since it influences R ...

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by mohamed khamis View Post
    It is theoretically 24 VDC but practically 22 to 23 VDC


    No big iron parts nor big DC buses. are you sure the change to 12 VDC will help...The using of AC source is quite restricted in hazardous area such as offshore oil and gas platform, pls suggest
    try. The worst scenario is that you will burn the coil. CAREFUL: it will draw twice the current, so the output of your plc may suffer if not sized properly.

  14. #14
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Liquid solenoid valve mystery

    Thank you all for your participation

    BESC5240,

    Ok when I checked the coil selection with the electrical engineer I found out that the coil code is for AC-version but there is some thing confuses me that I am going to use the same valve model in another project and when I checked the plunger/armature shape I found it is a round. this means this model for DC-version, wright or wrong?. So r u sure that the cross section for DC-version is round?. Once again my appreciation to you all guys

    Regards
    Mohamed

  15. #15
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid solenoid valve mystery

    Yes, DC is round, AC is square.

  16. #16
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Liquid solenoid valve mystery

    Would swapping the live and neutral make any difference to the magnetic field generated? If so you could swap the live and neutral connections on each switching with a relay arangement.

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by monkey spanners View Post
    Would swapping the live and neutral make any difference to the magnetic field generated? .
    No, field changes his direction by frequency of source AC.

  18. #18
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid solenoid valve mystery

    Note that the power supply is DC not AC.

  19. #19
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by NoNickName View Post
    Note that the power supply is DC not AC.
    If you are referring to my answer, note that "Live" and "Neutral" are terms used in AC power supply!
    Positive and Negative are correct terms for DC current.

  20. #20
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by nike123 View Post
    If you are referring to my answer, note that "Live" and "Neutral" are terms used in AC power supply!
    Positive and Negative are correct terms for DC current.
    Yes, but this guy has got DC solenoid valve, not AC, so your comment is off topic.

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Liquid solenoid valve mystery

    Quote Originally Posted by NoNickName View Post
    Yes, but this guy has got DC solenoid valve, not AC, so your comment is off topic.

    I was quoted text at which I was referring in my answer!
    So, as you see, it is not answer to original poster, it is answer to monkey spanners question, and therefore it is not off-topic.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •