30-06-2008, 11:23 PM #1
orifice
plea help,how to size expansion internal orifice,isit by compressor or evaporator coil temperature capacity.
-
01-07-2008, 12:00 AM #2
Re: orifice
Originally Posted by Ray Ang SM
If you would have said evaporator coil capacity I see what you are asking for? However, the use of the word temperature in that description is confusing.
The TXV's have to be sized for the respective evaporator coil capacity at the specific operating parameters the evaporator will be operating at during normal conditions.
TXV orifices are rated on cooling capacity at a specific pressure differential and the temperature of the liquid refrigerant feeding the TXV.
Do not over-size the orifice capacity. If the orifice capacity is within 10% of what you need for the evaporator capacity you should be OK.If all else fails, ask for help.
-
01-07-2008, 03:48 AM #3
Re: orifice
Iceman,
I read the question somewhat different.
My answer would be that a TEV is sized according to the compressors btuh capacity at a given SST or as ray states, "evaporator coil temp".
regards...............powell
-
01-07-2008, 03:58 AM #4
Re: orifice
Originally Posted by powell
What if you have more than one evaporator connected to a single compressor? Or, if the multiple evaporators each have a different capacity?If all else fails, ask for help.
-
01-07-2008, 04:22 AM #5
-
01-07-2008, 04:45 AM #6
Re: orifice
Have you seen the Danfoss or Sporlan catalouge for selection of expansion valve.
If you required i will send.
raj
-
01-07-2008, 03:23 PM #7
Re: orifice
Originally Posted by powell
You cannot size a TXV on a system containing multiple evaporators by using the compressor capacity though. If you get used to using the evaporator capacity then your selection will be accurate all of the time (if the valve is selected for the appropriate capacity in the first place by using the proper correction factors).If all else fails, ask for help.
-
01-07-2008, 11:40 PM #8
Re: orifice
thank guyfor helping alot.
-
02-07-2008, 01:29 AM #9
Re: orifice
Correct. I used the plural form of evaps in my statement.
It seems we agree to disagree on how to explain the specifics of designing a valve. I'm sure that any valve that you and I design would probably match and work properly.
This discussion could evolve into a highly debated subject like the superheat/subcooling debates.
regards..................powell
-
02-07-2008, 02:34 AM #10
Re: orifice
Originally Posted by powell
I stand corrected on the issues of the plural use of evaps. I did not catch that on the first pass I made.
What I have been trying to say (and apparently failing) is that you need more information than the compressor capacity to size the TXV's. For a single compressor/evaporator system the compressor capacity has to equal both the TXV and evaporator capacity so no argument on that point. If the capacities don't match, something is wrong.
The point I was attempting to make is that if you base your decisions/selections for the TXV on the evaporator capacity and operating conditions that the TXV will work at you can't go wrong.
Then (on a multiple evap. system) the total evaporator capacity should equal the total TXV capacity and the total capacity of either one (evap.'s or TXV's) should match the total compressor capacity.
This way you don't have any accounting errors on something not adding up properly.
Originally Posted by powell
And the most confusing thing to do is to try to explain how to do something. Look at the trouble we are having and we share a common language. Just imagine the person who is trying to read this and translate it into their native language. All we have to work with is pictures and language in trying to help someone. What one says, the others disagree with, but it's harder still for someone else who only has the written word to work from.Last edited by US Iceman; 02-07-2008 at 02:35 AM. Reason: edit
If all else fails, ask for help.
Similar Threads
-
How to design the orifice of the evaporator
By ntfreezer in forum New to REReplies: 10Last Post: 03-04-2007, 04:10 PM -
sizing up an orifice
By frosty74 in forum CommercialReplies: 13Last Post: 30-09-2006, 02:18 PM -
superheat with the wrong orifice
By superheat in forum Air ConditioningReplies: 9Last Post: 25-10-2002, 08:54 PM -
Orifice
By reggie in forum FundamentalsReplies: 13Last Post: 11-10-2002, 10:56 AM -
Orifice Plates
By Tony in forum IndustrialReplies: 5Last Post: 18-07-2002, 09:51 PM