    plea help,how to size expansion internal orifice,isit by compressor or evaporator coil temperature capacity.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: orifice

    Quote Originally Posted by Ray Ang SM
    ...evaporator coil temperature capacity
    What is this?

    If you would have said evaporator coil capacity I see what you are asking for? However, the use of the word temperature in that description is confusing.

    The TXV's have to be sized for the respective evaporator coil capacity at the specific operating parameters the evaporator will be operating at during normal conditions.

    TXV orifices are rated on cooling capacity at a specific pressure differential and the temperature of the liquid refrigerant feeding the TXV.

    Do not over-size the orifice capacity. If the orifice capacity is within 10% of what you need for the evaporator capacity you should be OK.
    If all else fails, ask for help.


  3. #3
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: orifice

    Iceman,

    I read the question somewhat different.

    My answer would be that a TEV is sized according to the compressors btuh capacity at a given SST or as ray states, "evaporator coil temp".

    regards...............powell

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: orifice

    Quote Originally Posted by powell
    My answer would be that a TEV is sized according to the compressors btuh capacity at a given SST or as ray states, "evaporator coil temp".
    That would work if.... you only have one evaporator.

    What if you have more than one evaporator connected to a single compressor? Or, if the multiple evaporators each have a different capacity?
    If all else fails, ask for help.


  5. #5
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: orifice

    Quote Originally Posted by US Iceman View Post
    That would work if.... you only have one evaporator.

    What if you have more than one evaporator connected to a single compressor? Or, if the multiple evaporators each have a different capacity?
    First, one would need to know the design SST and design TD of the evaps and then size the TEV accordingly, if by percentage, to the unit/compressors btuh capacity.
    Last edited by powell; 01-07-2008 at 03:16 PM.

  6. #6
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: orifice

    Have you seen the Danfoss or Sporlan catalouge for selection of expansion valve.
    If you required i will send.

    raj

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: orifice

    Quote Originally Posted by powell
    First, one would need to know the design SST and design TD of the evaps and then size the TEV accordingly, if by percentage, to the unit/compressors btuh capacity.
    True, but... either way you need to know some information before you can make an informed decision. The assumption that needs to be defined is if the system has one or more evaporators.

    You cannot size a TXV on a system containing multiple evaporators by using the compressor capacity though. If you get used to using the evaporator capacity then your selection will be accurate all of the time (if the valve is selected for the appropriate capacity in the first place by using the proper correction factors).
    If all else fails, ask for help.


  8. #8
    Join Date
    Jun 2008
    Location
    Singapore
    Age
    46
    Posts
    19
    Rep Power
    0

    Re: orifice

    thank guyfor helping alot.

  9. #9
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: orifice

    Quote Originally Posted by US Iceman View Post
    True, but... either way you need to know some information before you can make an informed decision. The assumption that needs to be defined is if the system has one or more evaporators.
    Correct. I used the plural form of evaps in my statement.

    Quote Originally Posted by US Iceman View Post
    You cannot size a TXV on a system containing multiple evaporators by using the compressor capacity though. If you get used to using the evaporator capacity then your selection will be accurate all of the time (if the valve is selected for the appropriate capacity in the first place by using the proper correction factors).
    It seems we agree to disagree on how to explain the specifics of designing a valve. I'm sure that any valve that you and I design would probably match and work properly.

    This discussion could evolve into a highly debated subject like the superheat/subcooling debates.

    regards..................powell

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: orifice

    Quote Originally Posted by powell
    This discussion could evolve into a highly debated subject like the superheat/subcooling debates.
    Probably... just like the adjust or don't adjust TXV's thread.

    I stand corrected on the issues of the plural use of evaps. I did not catch that on the first pass I made.

    What I have been trying to say (and apparently failing) is that you need more information than the compressor capacity to size the TXV's. For a single compressor/evaporator system the compressor capacity has to equal both the TXV and evaporator capacity so no argument on that point. If the capacities don't match, something is wrong.

    The point I was attempting to make is that if you base your decisions/selections for the TXV on the evaporator capacity and operating conditions that the TXV will work at you can't go wrong.

    Then (on a multiple evap. system) the total evaporator capacity should equal the total TXV capacity and the total capacity of either one (evap.'s or TXV's) should match the total compressor capacity.

    This way you don't have any accounting errors on something not adding up properly.

    Quote Originally Posted by powell
    It seems we agree to disagree on how to explain the specifics of designing a valve.
    We are not designing valves, the manufacturers do that. We are applying the valves to a specific operating condition. We may fully agree on the end result, but the methods I use and try to suggest are based on what I've done and been successful with.

    And the most confusing thing to do is to try to explain how to do something. Look at the trouble we are having and we share a common language. Just imagine the person who is trying to read this and translate it into their native language. All we have to work with is pictures and language in trying to help someone. What one says, the others disagree with, but it's harder still for someone else who only has the written word to work from.
    Last edited by US Iceman; 02-07-2008 at 02:35 AM. Reason: edit
    If all else fails, ask for help.


Similar Threads

  1. How to design the orifice of the evaporator
    By ntfreezer in forum New to RE
    Replies: 10
    Last Post: 03-04-2007, 04:10 PM
  2. sizing up an orifice
    By frosty74 in forum Commercial
    Replies: 13
    Last Post: 30-09-2006, 02:18 PM
  3. superheat with the wrong orifice
    By superheat in forum Air Conditioning
    Replies: 9
    Last Post: 25-10-2002, 08:54 PM
  4. Orifice
    By reggie in forum Fundamentals
    Replies: 13
    Last Post: 11-10-2002, 10:56 AM
  5. Orifice Plates
    By Tony in forum Industrial
    Replies: 5
    Last Post: 18-07-2002, 09:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •