    Flame Proof heaters for the drain pan



    We are working on a project to store chemicals. The evap side has to have all the flameproof fittings. Fans is not a problem. We are looking for Drain pan heaters I know those are available. has anyone used such heaters 7 what was the performance?



  2. #2
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Flame Proof heaters for the drain pan

    You need the exact electrical rating for the area and the gas involved. You may not be able to use electric heaters at all and have to go to a warm glycol coil to do the job.

    Ken

  3. #3
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Flame Proof heaters for the drain pan

    You will need to establish which standard you're going to work to such as ATEX (BASEEFA is no longer valid in the UK) and then find a heater that complies to that standard. As TXiceman states you must identifiy the gas/dust (hazard) type because the heater will need to be restricted to a surface temperature that falls within the classification of that gas/dust or hazard.

    I would agree with TXiceman that the best option would be to use hot gas or glycol defrost coil. Much safer and probably a lot cheaper.

Similar Threads

  1. Searle Evaporator Heaters
    By Abe in forum Commercial
    Replies: 14
    Last Post: 31-12-2005, 10:24 AM
  2. drain heaters
    By jamcool in forum Technical Speculations
    Replies: 7
    Last Post: 04-08-2005, 05:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •