    Defrost Elements in series?



    Hi Guys,
    In Tasmania we have 240v supply. Originally on a evaporator I had 2 x 1,6kw 115v defrost elements in series connected to the 240v.
    These elements blew so the suppliers sent me 2 x 3,2kw 240v defrost elements.
    If I connect these in series to 240v will they give me the same amount of heat (Kw) as the originals?



  2. #2
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    216
    Rep Power
    18

    Re: Defrost Elements in series?

    I should have mentioned that the original elements blew after 8 years and they where wired up correctley

  3. #3
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Defrost Elements in series?

    No do not connect these elements in series ! . You can fit these element but wire them up in parellel . One element will give you 3.2 kw the same as the two 1.6 kw elements you had before in series.
    Last edited by philfridge; 24-06-2008 at 03:52 PM.
    Transvestites are men who like to eat, drink, and be Mary.

  4. #4
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Defrost Elements in series?

    Quote Originally Posted by Drew View Post
    Hi Guys,
    In Tasmania we have 240v supply. Originally on a evaporator I had 2 x 1,6kw 115v defrost elements in series connected to the 240v.
    These elements blew so the suppliers sent me 2 x 3,2kw 240v defrost elements.
    If I connect these in series to 240v will they give me the same amount of heat (Kw) as the originals?
    Two 3.2 kW elements in series will give you a total of 1.6 kW. Thus you get only half the capasity you had previously. If you need two elements, the alternatives these elements is giving you is: series 1.6 kW total, and paralell 6.4 kW total.

  5. #5
    Join Date
    Jun 2008
    Location
    England
    Age
    53
    Posts
    5
    Rep Power
    0

    Re: Defrost Elements in series?

    Maths:

    Power=Voltage*Current
    Voltage=Current*Resistance
    Power=Voltage*Voltage/Resistance


    2*3.2kw heaters 240v

    Resistance=Voltage*Voltage/Power
    therefore
    Resistance=240*240/3200
    say approx 20 ohms

    Resistance in series will mean total resistance of approx 40 ohms with a voltage of 240v
    therefore power will halve to 1.6kW

    Resistance in parallel would have 2 lots of 3.2kW totalling 6.4kW.

    Very confusing but hope this helps.

  6. #6
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Defrost Elements in series?

    Wait a minute, if he had 2 * 1.6kw 115v in series and got 2 * 3.2kw 240v.
    How would these ever fit?

    2 * 3.2kw in series gives 1.6kw
    Therefore 2 * 1.6kw in series would give 0.8kw

    Or am I missing something because of the voltage?

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Defrost Elements in series?

    You should fit only one element for same power as before.

  8. #8
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17
    Quote Originally Posted by chillin out View Post
    Wait a minute, if he had 2 * 1.6kw 115v in series and got 2 * 3.2kw 240v.
    How would these ever fit?

    2 * 3.2kw in series gives 1.6kw
    Therefore 2 * 1.6kw in series would give 0.8kw

    Or am I missing something because of the voltage?

    Chillin
    Yep, you are missing the voltage. The new elements is 240 V, therefore 2*3.2 kW in serie gives only 25% of total power, IE 25% of 6.4 kW total is 1.6 kW total.
    The old elements was 115 V, therefore 2*1.6 kw in serie at 240V gives 100% of total power IE 100% of 3.2 kW is 3.2 kW.

    But you are right, these elements wount give the same capasity as the old elements if it is necessary to install both elements for proper distribution of the heat.
    Last edited by SteinarN; 26-06-2008 at 02:19 AM.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Defrost Elements in series?

    This must do and the rest is up to you http://www.the12volt.com/ohm/ohmslaw.asp
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  3. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM
  4. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Replies: 19
    Last Post: 13-08-2007, 11:25 PM
  5. VRV fault
    By Jase in forum Air Conditioning
    Replies: 10
    Last Post: 16-05-2007, 08:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •