Defrost Elements in series?
Hi Guys,
In Tasmania we have 240v supply. Originally on a evaporator I had 2 x 1,6kw 115v defrost elements in series connected to the 240v.
These elements blew so the suppliers sent me 2 x 3,2kw 240v defrost elements.
If I connect these in series to 240v will they give me the same amount of heat (Kw) as the originals?
-
24-06-2008, 06:47 AM #2
Re: Defrost Elements in series?
I should have mentioned that the original elements blew after 8 years and they where wired up correctley
-
24-06-2008, 11:52 AM #3
Re: Defrost Elements in series?
No do not connect these elements in series ! . You can fit these element but wire them up in parellel . One element will give you 3.2 kw the same as the two 1.6 kw elements you had before in series.
Last edited by philfridge; 24-06-2008 at 03:52 PM.
Transvestites are men who like to eat, drink, and be Mary.
-
24-06-2008, 06:02 PM #4
Re: Defrost Elements in series?
-
25-06-2008, 01:18 AM #5
Re: Defrost Elements in series?
Maths:
Power=Voltage*Current
Voltage=Current*Resistance
Power=Voltage*Voltage/Resistance
2*3.2kw heaters 240v
Resistance=Voltage*Voltage/Power
therefore
Resistance=240*240/3200
say approx 20 ohms
Resistance in series will mean total resistance of approx 40 ohms with a voltage of 240v
therefore power will halve to 1.6kW
Resistance in parallel would have 2 lots of 3.2kW totalling 6.4kW.
Very confusing but hope this helps.
-
25-06-2008, 11:20 PM #6
Re: Defrost Elements in series?
Wait a minute, if he had 2 * 1.6kw 115v in series and got 2 * 3.2kw 240v.
How would these ever fit?
2 * 3.2kw in series gives 1.6kw
Therefore 2 * 1.6kw in series would give 0.8kw
Or am I missing something because of the voltage?
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
25-06-2008, 11:26 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Defrost Elements in series?
You should fit only one element for same power as before.
-
26-06-2008, 02:15 AM #8
Yep, you are missing the voltage. The new elements is 240 V, therefore 2*3.2 kW in serie gives only 25% of total power, IE 25% of 6.4 kW total is 1.6 kW total.
The old elements was 115 V, therefore 2*1.6 kw in serie at 240V gives 100% of total power IE 100% of 3.2 kW is 3.2 kW.
But you are right, these elements wount give the same capasity as the old elements if it is necessary to install both elements for proper distribution of the heat.Last edited by SteinarN; 26-06-2008 at 02:19 AM.
-
26-06-2008, 07:28 AM #9
Re: Defrost Elements in series?
This must do and the rest is up to you http://www.the12volt.com/ohm/ohmslaw.asp
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Toshiba RAV SM/SP1400 defrost problem
By SteinarN in forum Heat PumpsReplies: 11Last Post: 20-02-2008, 04:25 PM -
No Power for Defrost Timer Motor
By kln in forum DomesticReplies: 6Last Post: 21-01-2008, 08:22 AM -
Hot gas defrost vs Electric defrost
By herdian in forum IndustrialReplies: 19Last Post: 13-08-2007, 11:25 PM -
VRV fault
By Jase in forum Air ConditioningReplies: 10Last Post: 16-05-2007, 08:21 PM