    How to drain and discharge Ammoni/water chiller



    I'm operating a 5 ton Robur ammonia/water absorption chiller and i need to do a routine maintenace of the system. The manaul states that i would need to use amonia R 717 7.5 kg and Water H2O 10 kg but it just doesnt quite tell me how to charge them up to the system. Also when I open the outlet valve, which is used to intall a pressure gauge, to drain the Ammonia/water, how would i get rid of all the water that still remains inside ie, rectifier absorber and so on. If anyone is experienced in this field please kindly educate me, thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How to drain and discharge Ammoni/water chiller

    You don't normally need to remove the mixture from the unit.

    For example, I once had to remove the evaporator coil which meant cutting the pipework.

    All I had to do was de-pressurize the system by venting the vapour under water. The pipes were then cut, the work completed and the pipes reconnected using the specified connectors.

    The system was re-pressurized using a pre-mix bottle and the operating pressures restored with the unit running.

    You should check with the instruction manual first however.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015