    Smile defrosting of freezer system [-40°]



    with water cooled condenser freezer cooling coil defrostining system with hot gas by pass is not performing properly? whay to do? - shaukat



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Shaukat View Post
    with water cooled condenser freezer cooling coil defrostining system with hot gas by pass is not performing properly? whay to do? - shaukat

    The condenser is getting to much water. check if the watervalve is working properly, or if it's there at all.
    -Cheers-

    Tycho

  3. #3
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Tycho View Post
    The condenser is getting to much water. check if the watervalve is working properly, or if it's there at all.
    if that's not it, let us know how the HP line is designed, what valves there are and what kinda valves there are around the freezer.
    -Cheers-

    Tycho

  4. #4
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: defrosting of freezer system [-40°]

    Condenser discharge water will be best for defrosting as it is simle and only care to be taken care in Piping the drain as well as defrost header.Check in Roy J Dossat Book the slope is clearly given

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: defrosting of freezer system [-40°]

    The condenser is not a part of HG defrost so its not relevant if its cooled by water or air. If your evaporator is flooded one, allow time between LSV closed and HG valve opening to empty all the liquid out. Check the operating of KVL, some of them have strainers on the enterance and if blocked or even partialy, you don't get good suction.

    Is this a sudden problem, or it has been for a long time?

  6. #6
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    tanx, during the defrosting ,water pump is 'off' condition ,

  7. #7
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Sridhar1312 View Post
    Condenser discharge water will be best for defrosting as it is simle and only care to be taken care in Piping the drain as well as defrost header.Check in Roy J Dossat Book the slope is clearly given
    at -40°c , we may not use water to defrost cooling coil, as i know there 2 option 1- hot gas ,2- electric heater. do you know any other option.

  8. #8
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by chemi-cool View Post
    The condenser is not a part of HG defrost so its not relevant if its cooled by water or air. If your evaporator is flooded one, allow time between LSV closed and HG valve opening to empty all the liquid out. Check the operating of KVL, some of them have strainers on the enterance and if blocked or even partialy, you don't get good suction.

    Is this a sudden problem, or it has been for a long time?
    at -40°c , we may not use water to defrost cooling coil, as i know there 2 option 1- hot gas ,2- electric heater. do you know any other option.

  9. #9
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    18

    Re: defrosting of freezer system [-40°]

    We have been using HGDF system with water cooled condensers without any problems. What exactly is the problem? U r not getting enough Hot gas? R Connections OK?

  10. #10
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by chemi-cool View Post
    The condenser is not a part of HG defrost so its not relevant if its cooled by water or air. If your evaporator is flooded one, allow time between LSV closed and HG valve opening to empty all the liquid out. Check the operating of KVL, some of them have strainers on the enterance and if blocked or even partialy, you don't get good suction.

    Is this a sudden problem, or it has been for a long time?
    And how is the condenser not part of the hotgas defrost?
    -Cheers-

    Tycho

  11. #11
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Maybe you should tell us a little more of what is happening.


    You are saying the water pump is in the off position during defrost. this makes me believe there is not a PM valve on the high pressure line

    what refrigerant are you using?

    are there a manometer on the evaporator, what pressure do you get on the evap during defrost?

    what is the HP of the compressor?
    -Cheers-

    Tycho

  12. #12
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Shaukat View Post
    at -40°c , we may not use water to defrost cooling coil, as i know there 2 option 1- hot gas ,2- electric heater. do you know any other option.
    hi,
    no, it is not suddanly , it is from date of installation

  13. #13
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Tycho View Post
    Maybe you should tell us a little more of what is happening.


    You are saying the water pump is in the off position during defrost. this makes me believe there is not a PM valve on the high pressure line

    what refrigerant are you using?

    are there a manometer on the evaporator, what pressure do you get on the evap during defrost?

    what is the HP of the compressor?
    f-22 , temp of hot gas is unsufficeent heat to remove ice from coil, i desided to use elecrict heaters.

  14. #14
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Shaukat View Post
    f-22 , temp of hot gas is unsufficeent heat to remove ice from coil, i desided to use elecrict heaters.
    Maybe with a PM valve on the compressor, during defrost you could make all the hotgas go to the evap, giving you better pressure and heat.


    welp...
    -Cheers-

    Tycho

  15. #15
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by smpsmp45 View Post
    We have been using HGDF system with water cooled condensers without any problems. What exactly is the problem? U r not getting enough Hot gas? R Connections OK?
    yh, i m not geting enough hot gas

  16. #16
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    dear frindes, i solved my problem with electric heater, a old man tehnician advice me to not use over size water cooled condenser if you are going for hot gas defrost. .. thanx again

  17. #17
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by Shaukat
    ...advice me to not use over size water cooled condenser if you are going for hot gas defrost.
    That does not have anything to do with the problem. The problem is you don't have enough hot gas. How will an air-cooled condenser or any other type of condenser give you more hot gas?

    They won't!

    What you have is a fundamental problem with the hot gas defrost system. Are you defrosting more than one evaporator at a time? Or worse, do you only have one evaporator on the compressor?
    If all else fails, ask for help.


  18. #18
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by US Iceman View Post
    That does not have anything to do with the problem. The problem is you don't have enough hot gas. How will an air-cooled condenser or any other type of condenser give you more hot gas?

    They won't!

    What you have is a fundamental problem with the hot gas defrost system. Are you defrosting more than one evaporator at a time? Or worse, do you only have one evaporator on the compressor?


    If the condenser is oversized, and there is a PM valve on the hp line, and the hotgas is connected on the condenser side of the PM

    Or if the condenser is correctly sized and there is no PM valve, and the compressor is on low capacity (if there is capacity control on the compressor), compressor on low capacity - little to no hotgas - not enough hp to overcome the hotgas return valve (if it's set to high)



    there's not enough info to make anything close to an educated guess
    -Cheers-

    Tycho

  19. #19
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: defrosting of freezer system [-40°]

    I don't disagree with you Tycho, but to say a water-cooled condenser is the reason is not correct either.

    Something else is wrong.
    If all else fails, ask for help.


  20. #20
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by US Iceman View Post
    I don't disagree with you Tycho, but to say a water-cooled condenser is the reason is not correct either.

    Something else is wrong.
    he said "over size water cooled condenser"

    So we agree, and I wasnt pointing my finger at you, just generally waving it around
    -Cheers-

    Tycho

  21. #21
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: defrosting of freezer system [-40°]

    That's fine, I'm a big boy.

    There is definitely a system design problem though. Sure an over-sized condenser would make the problem worse instead of better.

    I'm going back to my corner now....
    If all else fails, ask for help.


  22. #22
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: defrosting of freezer system [-40°]

    Quote Originally Posted by US Iceman View Post
    That does not have anything to do with the problem. The problem is you don't have enough hot gas. How will an air-cooled condenser or any other type of condenser give you more hot gas?

    They won't!

    What you have is a fundamental problem with the hot gas defrost system. Are you defrosting more than one evaporator at a time? Or worse, do you only have one evaporator on the compressor?
    i think water quantity in water cooled condensor is more and defrosting time is less , [or ambiant is < 25°c]

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  4. beacon system freezer
    By tony_rich in forum Technical Discussions
    Replies: 0
    Last Post: 10-02-2002, 07:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •