Thread: Bottle cooler tripping
20-06-2008, 06:54 PM #1
Hi, i got called to a dump fridge bottle cooler today,that as soon as you switch on trips the breaker.I took the relay off the compressor and it still triped,is it the electrics you would change?Iv wired the fans out,and they run fine,so it isnt them.Then i thought the compressor,but would it still trip when the relay isnt conected?Thanks.
20-06-2008, 06:58 PM #2
Re: Bottle cooler tripping
If you disconnect everything from the compressor and it doesnt trip then its a good bet it is a faulty comp.
If you pull the electrics off and it trips then its probably a faulty relay or klixon.So yes it sounds like electrics,but make sure theres nothing else on the fridge thats wired up.Last edited by Chunk; 20-06-2008 at 07:01 PM. Reason: baboons bottoms
If it ain't broke, it doesn't have enough features yet.
Damo
20-06-2008, 10:07 PM #3
I disconnected the compressor,and both fans ran fine.Then took replay off compressor,still wired up.{nothing connected to comp}.And it tripped again.So would you go down the road of changing,relay clixon,and capasitor?Thanks for your help.
20-06-2008, 10:20 PM #4
Yep - sounds like the electrics
TXV hunting in a walkin cooler
By dkemper in forum Trouble ShootingReplies: 9Last Post: 15-11-2007, 03:14 PM -
Bottle Cooler on Propane
By smpsmp45 in forum DomesticReplies: 0Last Post: 13-09-2007, 12:07 PM -
Bottle cooler
By Dave M in forum DomesticReplies: 3Last Post: 05-09-2007, 11:52 PM -
Quest bottle cooler
By Andy AC in forum CommercialReplies: 5Last Post: 24-06-2007, 11:32 AM -
caravell bottle cooler
By jon007 in forum CommercialReplies: 9Last Post: 06-07-2006, 10:15 PM