    Question daiken ducted aircondition malfunction ..PLEASE HELP....



    Hi guys, Iam new to this forum. I just need some help with the malfunction code appeared on the controll panael of the ducted air conditioner. It reads as U4 which i understood that it is System Transmission between indoor units. What do I do to fix it? When I pressed on one of the button thats when it appeared. Also the operation re/green button flashing as well. What do I do? is it serious? Please help..........
    thanks kakka...



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: daiken ducted aircondition malfunction ..PLEASE HELP....

    U4, is communication between indoor unit and outdoor unit (or outdoor unit and BC box).

    The normal reason for this code to flag up is in multi indoor applications where the indoor units got their own electrical supply, someone has isolated the power to the outdoor unit.

    Should this not be the case, you are looking at communication wiring/transformers/PCBs.

    Good hunting.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Troubleshooting for Daikin Aircon CTK25FVEN
    By JCTK in forum Air Conditioning
    Replies: 19
    Last Post: 05-06-2010, 07:18 PM
  3. Absolute Zero, Daiken manuals
    By deu58 in forum Transport
    Replies: 3
    Last Post: 19-05-2008, 12:59 AM
  4. LG ducted split
    By Abe in forum Air Conditioning
    Replies: 20
    Last Post: 08-06-2005, 07:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •