    Hot Gas Bypass (HGBP)



    Hi All

    Has anyone got any info on a hot gas bypass installation.
    We a pricing a job at the moment and they require HGBP in a DX AHU
    We are to install it on the first stage of cooling to regulate the cooling load.

    Any diagrams/pipe selection tools would be great.

    Regards

    Coolkids



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hot Gas Bypass (HGBP)

    Is this for capacity control ??
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2007
    Location
    Peoples Republic of Geordie Land
    Posts
    47
    Rep Power
    0

    Re: Hot Gas Bypass (HGBP)

    Yes

    Coolkids

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Hot Gas Bypass (HGBP)

    Hot gas bypass does not regulate the cooling load. The hot gas is injected into the evaporator as the cooling load decreases. A pressure regulator controls the flow of hot gas into the evaporator, which is then cooled off by the TXV injecting small amounts of liquid to cool down the hot gas.

    The total volume of gas flows back to the compressor to keep it operating at it's minimum capacity. The hot gas valve is typically sized for the minimum step of compressor capacity available.

    If the compressor has unloaders, then you size the hot gas valve for that minimum step of compressor capacity.

    If the compressor does not have internal unloaders, then you have to size the valve for the total compressor capacity.

    That way when the cooling load drops off, the compressor suction pressure remains constant. With this type of an arrangement the compressor is doing no cooling (because the load is decreasing or zero).
    Last edited by US Iceman; 18-06-2008 at 07:07 PM. Reason: clarification
    If all else fails, ask for help.


  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Hot Gas Bypass (HGBP)

    What you need is evaporator pressure regulator.

    HGBP is as explained by my wise friend

  6. #6
    rd_shetty2003's Avatar
    rd_shetty2003 Guest

    Re: Hot Gas Bypass (HGBP)

    For installation instructions search in google hot gas bypass 30ga900161

  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Hot Gas Bypass (HGBP)

    Quote Originally Posted by US Iceman View Post
    Hot gas bypass does not regulate the cooling load. The hot gas is injected into the evaporator as the cooling load decreases. A pressure regulator controls the flow of hot gas into the evaporator, which is then cooled off by the TXV injecting small amounts of liquid to cool down the hot gas.

    The total volume of gas flows back to the compressor to keep it operating at it's minimum capacity. The hot gas valve is typically sized for the minimum step of compressor capacity available.

    If the compressor has unloaders, then you size the hot gas valve for that minimum step of compressor capacity.

    If the compressor does not have internal unloaders, then you have to size the valve for the total compressor capacity.

    That way when the cooling load drops off, the compressor suction pressure remains constant. With this type of an arrangement the compressor is doing no cooling (because the load is decreasing or zero).

    wouldnt it be easier to just "short circuit" the hotgas line and suction line?

    And I call this method the "BTSITH" or "Bite thy self in the hind" method.

    Run a frequency converter on the compressor and at minimum load and maybe 1200 rpm it would have so little to work with that if it stops on LP, there really isnt any need for the compressor to start in a while, in comparison to stopping at 3000 rpm where the system might start calling for the compressor to start again after a few minutes and it only gets a 15 minute downtime each stop.
    -Cheers-

    Tycho

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Hot Gas Bypass (HGBP)

    Quote Originally Posted by Tycho
    wouldnt it be easier to just "short circuit" the hotgas line and suction line?

    And I call this method the "BTSITH" or "Bite thy self in the hind" method.
    Yes, it would be easier to just dump the hot gas in the suciotn line, but then you also need a liquid injection valve for desuperheating the hot gas. And, with this method a suction accumulator is not a bad idea to install.

    If you dump the hot gas into a side-port distributor the main TXV takes care of the desuperheating.

    I think your name for the "short circuit" method is aptly named!
    If all else fails, ask for help.


  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hot Gas Bypass (HGBP)

    Avery un-economical way of regulating
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Hot Gas Bypass (HGBP)

    Quote Originally Posted by US Iceman View Post
    Yes, it would be easier to just dump the hot gas in the suciotn line, but then you also need a liquid injection valve for desuperheating the hot gas. And, with this method a suction accumulator is not a bad idea to install.

    If you dump the hot gas into a side-port distributor the main TXV takes care of the desuperheating.

    I think your name for the "short circuit" method is aptly named!
    I see your point, the ones I have come across have been a simple solenoid/PM valve from HP to LP on the compressor.

    for continued operation I see how bleeding it to the evap would be better.


    the ones I have seen has a OM valve with a CVP attached, and as the suction pressure reaches the set opening pressure of the CVP you hear *WHOOOOOOOOAMH* as the PM valve opens and short circuits the compressor and also dumps alot more hotgas into the LP side than is really needed.


    I am sorry to say I have been part of installing a system with this as part of the "capacity control" it was two horizontal plate freezers injected with HP liquid and a LP reciever (when the liquid boiled of it injected more hp liquid) fair enough an ok system.

    I was laid of due to bad economy from my regular company at the time and to make ends meet I helped a competitor of my regular company to supervising the build of this plant on my spare time and got fairly paid, I felt like they worked by the "Let's use what we have availavle" instead of "We'll have the proper valve in three days, let's wait till we have it before we proceed"

    anyways... the system was to have the LP hp Comnnection, and there was this huuuuge PM valve short circuiting the compressor...

    I was up in the galley getting food one day after the plant had been started, and I could hear *FWOOOOMPH FWOOOOMPH FWOOOOMPH* as the valve was working, and it felt bad every time I heard it..
    -Cheers-

    Tycho

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Hot Gas Bypass (HGBP)

    I like your sound effects in the post. Very descriptive.
    If all else fails, ask for help.


  12. #12
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Hot Gas Bypass (HGBP)

    Gentlemen,

    would there be any benifit dumping saturated gas from the top of the receiver into the suction, oposed to hot discharge gas? would this limit compressor discharge superheat?

    Alternatively, could this be dumped into the evaporator instead?

    Billy Ray

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Hot Gas Bypass (HGBP)

    Hi Billy Ray,

    That is one possibility. Although, what I think would happen is the receiver pressure could decrease and limit how much liquid flows to the TXV.

    If I had to use a gas bypass for part load control in today's environment I think I would use an inverter to control the compressor speed down to the minimum allowable RPM (suggested by the compressor manufacturer) as Tycho suggested. Then at that minimum capacity use the gas bypass. This helps to minimize the power use by the compressor and you end up with a fairly simple system that would work well.
    If all else fails, ask for help.


  14. #14
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Hot Gas Bypass (HGBP)

    The only disadvantage of using an inverter as against hot gas injection is that with the inverter the swept volume of the compressor effectively reduces as the speed reduces which reduces the velocity in the pipework leading to problems with oil return. With hot gas injection the minimum velocity required by the system can be maintained to aid oil return and still meet the rduced load on the evaporator.

    Ian

  15. #15
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19
    Hot gas bypass (HGBP) has some short comings such as introducing problems stemming from insufficient oil return and refrigerant logging in the HGBP line. And in all cases, hot gas bypass inflates the life-cycle cost of the system:
    HGBP increases the initial cost.such as requiring an additional refrigerant line, which also increases the likelihood of refrigerant leaks and oil/refrigerant logging.
    HGBP greatly reduces operating efficiency because the bypassed vapor does no
    useful cooling.
    HGBP costs more to operate because as the load fluctuates, the compressor
    consumes more energy because it’s forced to operate at a compression
    step that is likely one stage higher than necessary.

    You should only use hot gas bypass if all other design
    options fail to meet the demands of the application.
    Most comfort cooling applications can operate between steps of loading
    without loss of temperature or humidity control. Not only does this statement
    hold true between the third and fourth steps of cooling, when the outdoor
    latent load is high, but it also holds true for the step between off and first-stage
    cooling when the outdoor latent load is comparatively low.

    If you still feel the need for HGBP then be aware that diverting
    hot gas from the discharge line and around the condenser reduces the
    head pressure of the air conditioning
    system. As head pressure decreases, operation may become unstable — and
    unreliable. To avoid this risk, iyou need to include a method for head pressure control in
    every HGBP application.
    Last edited by wambat; 20-06-2008 at 12:35 AM.

  16. #16
    Join Date
    Jun 2002
    Location
    Mumbai, India
    Age
    66
    Posts
    25
    Rep Power
    0

    Re: Hot Gas Bypass (HGBP)

    Hi Coolkids,
    I notice that you have mentioned you wish to regulate cooling in first stage.
    Perhaps this isn't a comfort cooling application.

    Hot Gas Bypass will artificially load the system and is very useful when you have to cool ambient air in a once through system. Such systems are online systems - i.e. you cannot switch-off the compressor and you need to balance the fluctuating load which varies with the ambient temperature and ambient R.H.

    'Sporlan' has very good literature on this.
    You can visit www.sporlan.com and download bulletin 90-40 which gives all the information you need.
    If the system is piped as shown in this bulletin you will not encounter any problem at all.

    I have installed this type of system - without any crankcase or evaporator pressure regulating valve where I needed to cool ambient air down to 2 Deg. C Dew Point (entering air was between 5 Deg. C DB to 32 Deg.C DB and also varying WB).
    This was a once through system and the air was consumed in pneumatic conveying. The system is operating for more than 2 years without any problem.

    Needed a monster coil for this one though - 18 rows deep to cater to the dehumidification load during monsoon.

    In case you need any further help pm me.
    Last edited by S.M.Gokhale; 20-06-2008 at 05:44 AM.

Similar Threads

  1. Scroll internal bypass
    By Larry2 in forum Heat Pumps
    Replies: 27
    Last Post: 15-05-2009, 09:23 AM
  2. old system with hot gas bypass. help!
    By joapysoe in forum Trouble Shooting
    Replies: 8
    Last Post: 20-01-2008, 11:58 PM
  3. Dont be shy, advice needed.
    By Sledge in forum Air Conditioning
    Replies: 9
    Last Post: 27-06-2007, 03:09 PM
  4. Hot gas bypass control?
    By Jase in forum Air Conditioning
    Replies: 9