    over size



    hi engineer

    when compressor hp is much more bigger than cooier coil what is correct pressure and charging.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: over size

    Quote Originally Posted by Ray Ang SM View Post
    hi engineer

    when compressor hp is much more bigger than cooier coil what is correct pressure and charging.
    There is no correct pressure and charging (what ever that means) for that case.
    You, firstly, need correct "cooier" coil for that compressor, or correct compressor for that "cooier" coil. Then we could talk about correct pressures (temperatures) and charge.

  3. #3
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: over size

    Quote Originally Posted by Ray Ang SM View Post
    hi engineer

    when compressor hp is much more bigger than cooier coil what is correct pressure and charging.
    Ray,

    To determine the pressures one would need to at least know the designed TD across the evap and the application.

    High TD's are quite common on beer coolers and applications where high humidity is not required.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: over size

    Compressor HP has nothing to do with the coil size.

    The compressor capacity should be matched with the total evaporator capacity only (including the TXV and other components).
    If all else fails, ask for help.


  5. #5
    Join Date
    Jun 2008
    Location
    Singapore
    Age
    46
    Posts
    19
    Rep Power
    0

    Re: over size

    Quote Originally Posted by nike123 View Post
    There is no correct pressure and charging (what ever that means) for that case.
    You, firstly, need correct "cooier" coil for that compressor, or correct compressor for that "cooier" coil. Then we could talk about correct pressures (temperatures) and charge.
    can u teach how correct pressure(temperature)charge.

  6. #6
    Join Date
    Jun 2008
    Location
    Singapore
    Age
    46
    Posts
    19
    Rep Power
    0

    Re: over size

    Quote Originally Posted by powell View Post
    Ray,

    To determine the pressures one would need to at least know the designed TD across the evap and the application.

    High TD's are quite common on beer coolers and applications where high humidity is not required.
    can u teach me how to appiy on it.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: over size

    Quote Originally Posted by Ray Ang SM View Post
    can u teach how correct pressure(temperature)charge.


    http://tinyurl.com/56jrzl

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: over size

    Quote Originally Posted by Ray Ang SM View Post
    can u teach me how to appiy on it.
    I made some videos for you!

    Evaporator TD

    Condenser TD

    Password for both files is same and sent to you by visitor message.
    Last edited by nike123; 12-06-2008 at 10:05 PM.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: over size

    I do not mean to discredit anyone here, but these questions are being asked and replied to in a confusing order.

    HP for compressors and coils is not related and the aspects of charging for pressures lead me to believe this is a fundamentally flawed conversation.

    A lot of this material has been asked and answered in various locations on this site (probably multiple times). I suggest a search be performed for some of the questions you have and then spend some time reading the posts.

    It's not that I mind trying to answer some questions, but these two questions are not related at all.
    Last edited by US Iceman; 13-06-2008 at 02:37 AM. Reason: spelling
    If all else fails, ask for help.


  10. #10
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: over size

    Quote Originally Posted by Ray Ang SM View Post
    hi engineer

    when compressor hp is much more bigger than cooier coil what is correct pressure and charging.
    Ang, what is your application, comfort air-conditioning or refrigeration? What kind of temperature are you looking at? please elaborate more details so that the members here can give you a more definite answer.

Similar Threads

  1. Duct Size Calculations
    By hamidpia in forum Tools and Calculators
    Replies: 17
    Last Post: 21-06-2010, 01:56 PM
  2. Molecule size?
    By nike123 in forum Fundamentals
    Replies: 7
    Last Post: 03-03-2008, 01:14 AM
  3. Evaporator design: minimal channel size.
    By DaBit in forum CPU Overclockers
    Replies: 9
    Last Post: 05-06-2003, 03:47 PM
  4. Urgent!!! S.O.S. - nozzle size
    By herefishy in forum Fundamentals
    Replies: 3
    Last Post: 25-05-2002, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •