08-06-2008, 01:38 PM #1
Trouble with a 240v sensor light, ANY1 interested
If so and I can post it here?
Well I've been here b4 and you guys work with power too!!
-
08-06-2008, 02:10 PM #2
Re: Trouble with a 240v sensor light, ANY1 interested
And the question is??
-
08-06-2008, 02:24 PM #3
Re: Trouble with a 240v sensor light, ANY1 interested
-
08-06-2008, 11:17 PM #4
Re: Trouble with a 240v sensor light, ANY1 interested
If you want a fair answer then give us a fair question..
What sort of sensor switch is it, make, model, sensor etc.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
08-06-2008, 11:32 PM #5
Re: Trouble with a 240v sensor light, ANY1 interested
A thought...
It seems to react on a voltage drop when other equipment is starting up.
Hard to put any filter in for that...(UPS??)
But shouldn't the question be: Why does the voltage drop enough to set this light off?
(Check all the wiring)
-
08-06-2008, 11:41 PM #6
-
09-06-2008, 03:49 AM #7
-
09-06-2008, 12:19 PM #8
-
09-06-2008, 08:34 PM #9
Re: Trouble with a 240v sensor light, ANY1 interested
Can you type out the url ?
w w w . this site . com
It's a strange problem, you've got us going nowBrian - Newton Abbot, Devon, UK
Retired March 2015
-
10-06-2008, 06:36 AM #10
-
10-06-2008, 11:46 PM #11
Re: Trouble with a 240v sensor light, ANY1 interested
You meant "arlec dot com dot au" then ?
http://www.arlec.com.au/display.php?pid=80Brian - Newton Abbot, Devon, UK
Retired March 2015
-
10-06-2008, 11:49 PM #12
Re: Trouble with a 240v sensor light, ANY1 interested
I see that the light has manual override which normally means that by flicking the switch in a certain pattern will turn the light on (no comments please).
So, perhaps, it is seeing a pulse down the live feed somehow.
Is all of the wiring secure in that area ?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-06-2008, 01:20 AM #13
Re: Trouble with a 240v sensor light, ANY1 interested
[quote=Brian_UK;109118]You meant "arlec dot com dot au" then ?
Yeah that's what I meant
Thanks Brian
-
12-06-2008, 01:20 AM #14
Re: Trouble with a 240v sensor light, ANY1 interested
Check wiring.
Have you got an Earth connection to unit?
Try getting hold of an "X rated capacitor, say 0.1mfd, 250vac working". Connect across live and neutral at supply terminals to unit.
Failing that, you might find suppressor in old washing machine ....normally 3 terminal cylindrical device near to mains lead termination point. One terminal goes to Earth.
Do other lights in house 'dim' when loads are switched on? Poor voltage stability?
-
12-06-2008, 05:47 AM #15
Re: Trouble with a 240v sensor light, ANY1 interested
-
12-06-2008, 06:35 AM #16
Re: Trouble with a 240v sensor light, ANY1 interested
Thanks Electrocoolman for joining the post
No earth to our ceiling lights..
Capacitor was my 1st idea but I'm no electrician just a thought from some 3ft fluros I put in my shed have them and hobby's I play with..
I think I have 1 sitting on my bench that would do ( I'll go have a look then) out of my old fridge, it's a SH capacitor 350VAC3.5uF(U) 50Hz 0.38A / 60Hz 0.46A.
No dim lights when loads are switched
-
12-06-2008, 08:12 AM #17
Re: Trouble with a 240v sensor light, ANY1 interested
Hi Mag,
Cap you have is really too large in value...3.5uF(mfd) used for small motor run and power factor correction.
Do you have access to RS Components over there in Adelaide / Aus? I'm sure that there are possibly Tandy / Radio Shack or similar?
The small capacitors are used as motor noise suppressors such as vacuum cleaners, electric drills .....motors with brushes.
Good luck.
-
12-06-2008, 11:30 AM #18
-
12-06-2008, 12:18 PM #19
Re: Trouble with a 240v sensor light, ANY1 interested
This looks like the one
Cap Mains Sup 275V DX2 0.01 uF Mains EMI Suppressor 10n/103
Features:
- Metallized Polyester Film in Solvent Resistant UL94-V0 Casing.
- X2 for EMI Suppression, Meets New IEC 384-14 Specification for 2.5kV.
- Peak Pulse Voltage Test and Approved to 3kV Pulse Test.
- Class X is intended for applications where a short circuit will not cause a dangerous shock and is generally connected between each line conductor in a piece of equipment.
- Operating temperature: -40°C to +100°C
- Capacitance tolerance: ±10%
- Rated voltage: 250-275V AC, 50/60Hz
- Dissipation factor: 0.1% maximum at 1kHz 25°C
- Insulation resistance: >30,000Mohm (C<33uF) >10,000Mohm x uF (>33uF) at 25°C
- Dielectric strength: 2000V DC for 1 second
- Self-healing and high moisture resistant
- UL, CSA, VDE, NEMKO, SEMKO, DEMKO, FEMKO, SEV certified.
- CSA and UL Approved with a Voltage Up to 250VAC Only.
Cat No. R2620 Category: Capacitors - High Voltage
I made a mistake it should be this one as the value needed 0.1mfd and I selected 0.01uf so now I am confused
So is there a chart to workout uf to mfd??
Cap Mains Sup 275V DX2 0.1 uF X2 for EMI suppression, meets new IEC 384-14 specification for 2.5kV. Peak Pulse Voltage Test and approved to 3kV Pulse Test. Intended for applications where a short circuit will not cause a dangerous shock. Self-healing and high moisture resistant.
Features:
- Metallized Polyester Film in Solvent Resistant UL94-V0 Casing.
- X2 for EMI Suppression, Meets New IEC 384-14 Specification for 2.5kV.
- Peak Pulse Voltage Test and Approved to 3kV Pulse Test.
- Class X is intended for applications where a short circuit will not cause a dangerous shock and is generally connected between each line conductor in a piece of equipment.
- Operating temperature: -40°C to +100°C
- Capacitance tolerance: ±10%
- Rated voltage: 250-275V AC, 50/60Hz
- Dissipation factor: 0.1% maximum at 1kHz 25°C
- Insulation resistance: >30,000Mohm (C<33uF) >10,000Mohm x uF (>33uF) at 25°C
- Dielectric strength: 2000V DC for 1 second
- Self-healing and high moisture resistant
- UL, CSA, VDE, NEMKO, SEMKO, DEMKO, FEMKO, SEV certified.
- CSA and UL Approved with a Voltage Up to 250VAC Only.
Last edited by mag; 13-06-2008 at 04:05 AM. Reason: more info
-
12-06-2008, 11:43 PM #20
Re: Trouble with a 240v sensor light, ANY1 interested
Do you ever wish that you hadn't bought the damned light now ?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-06-2008, 03:26 AM #21
-
13-06-2008, 06:25 AM #22
Re: Trouble with a 240v sensor light, ANY1 interested
throw it back at the ARLEC toy shop and buy a real one, check the cct neutral as well. and the main neutral.
if the house was rewired 6yrs ago and there is no earth at the light, ring the inspection authority...NOW
-
13-06-2008, 06:30 AM #23
-
13-06-2008, 07:03 AM #24
-
13-06-2008, 03:36 PM #25
Re: Trouble with a 240v sensor light, ANY1 interested
Well I went to get my Cap 0.1mfd and rang 1st and yes we have 14 in stock, Not when I got there as the draw that should of had them was empty But the computer says we have 14 in stock idiots
I use to be confused but now I'm not so sure..
-
14-06-2008, 05:46 PM #26
-
14-06-2008, 11:08 PM #27
Re: Trouble with a 240v sensor light, ANY1 interested
Sorry Peter, another "lost in translation" expression...
"To set this off" means to get it going, make it work etc.
Similar to the start of a horse race perhaps - "They're off !!"Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-06-2008, 04:08 PM #28
Re: Trouble with a 240v sensor light, ANY1 interested
Hi Mag,
uF and mfd are the same....both stand for microFarad.
-
16-06-2008, 02:42 AM #29
-
20-06-2008, 10:09 AM #30
-
20-06-2008, 08:36 PM #31
Re: Trouble with a 240v sensor light, ANY1 interested
Thanks for the update Mag.
It's time for the Big Hammer I thinkBrian - Newton Abbot, Devon, UK
Retired March 2015
-
21-06-2008, 11:53 PM #32
Re: Trouble with a 240v sensor light, ANY1 interested
Mag,
one further thought...
you've probably removed the batten lamp holder and wired direct to the wires?
Have you tried swapping the phase and neutral connections to the unit?
....just a thought.