    What happens when i install a FH-4525-YHR 220V/1PH/50Hz (L'unité Hermétique) cooler on 220V/1PH/60Hz?

    Grtz Joeri



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Re: L'unité hermétique FH-4525-YHR 220V/1/50Hz

    Dont bother as it will damage the electrical components. Ie compressor and fan motor.
    Transvestites are men who like to eat, drink, and be Mary.

  3. #3
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: L'unité hermétique FH-4525-YHR 220V/1/50Hz

    Hi Joeri,
    The frequency affects the speed of rotation of the compressor, which will affect the refrigeration capacity. To obtain refrigeration capacity at 60Hz multiply 50Hz value by 1.2 .

    Following info from Unite Hermetic (Techumseh) relating to their dual frequency rated reciprocating compressors:

    .....Rated............Approved
    A) 100-1-50.........90/110-1-50
    ....115-1-60........103/127-1-60

    C) 208-1-50....... 187/230-1-50
    ....230-1-60....... 207/253-1-60

    J) 380-3-50........ 340/440-3-50
    ...440-3-60......... 396/484-3-60

    K) 220-3-50 ........180/253-3-50
    ....220-3-60........ 187/264-3-60

    As you can see, when you run on 50Hz as opposed to 60Hz, the voltage range that you can use is reduced.
    This is because the reduced motor speed results in a reduced 'back emf' from the motor, and so inorder to keep motor current within limits, you need to reduce the line supply voltage.

    In your case, running a 50Hz unit on 60Hz, the increased back emf will result in a reduced current draw, with a corresponding reduction in motor power. It will run, but to be on the safe side I would contact the compressor manufacturer to see what they advise?

    ECM.

  4. #4
    Join Date
    Jul 2006
    Location
    New Zealand
    Age
    77
    Posts
    65
    Rep Power
    18
    I think this has come up before. The power supply here is 230V 50Hz, but a company I service, has ships with a 230V 60Hz power supply. I can not obtain 60Hz compressors and so have been fitting what is available locally with no apparent problems. I have had the odd failure but these can generally be attributed to other reasons.

    Because you pick up about 12% capacity I downsize the replacement compressor
    Last edited by kiwireeferman; 06-06-2008 at 09:08 AM.

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Re: L'unité hermétique FH-4525-YHR 220V/1/50Hz

    Quote Originally Posted by Electrocoolman View Post
    It will run, but to be on the safe side I would contact the compressor manufacturer to see what they advise?
    Yes it will run then burn out windings
    Transvestites are men who like to eat, drink, and be Mary.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Joeri, welkom op dit forum.
    Van welke streek bent u? Post ook even een berichtje in de introductiesectie.

    Sorry for the Dutch my friends.

    Joeri, it will give 20% more cooling capacity because it runs 20% faster (frequency is direct related to rotational speed) and as long as the running current stays below max current, I don't see any problem.
    Most of these UH's runs far below max current, so you can say that the motor most likely will not be overloaded and you will not suffer overheating.

    What's the application? Will this machine be exported to AUS or NZ?
    Last edited by Peter_1; 08-06-2008 at 07:50 AM.

  7. #7
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: L'unité hermétique FH-4525-YHR 220V/1/50Hz

    Hi Phil,

    Quote Originally Posted by philfridge View Post

    Yes it will run then burn out windings
    Please expand on your reasons for your statement.

    We are talking about using a 50 hz unit on 60 hz and not the other way around. The supply voltage as I understand will remain the same. As PETER says the current should not exceed the rated current.

Similar Threads

  1. l'unite hermetique R12 Condensing unit
    By airefresco in forum Commercial
    Replies: 13
    Last Post: 08-02-2008, 09:08 PM
  2. L'Unite hermetique wiring
    By Chilly willy in forum Electrical
    Replies: 11
    Last Post: 20-08-2007, 06:38 AM
  3. L'unite Hermetique
    By Tycho in forum Chit Chat & Service Stories
    Replies: 0
    Last Post: 24-06-2006, 01:50 AM
  4. L'Unite Hermetique compressor
    By iceman007 in forum Commercial
    Replies: 4
    Last Post: 27-06-2004, 08:15 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •