Hi
ive been asked to quote a service visit on a large number of VAVs in a office , i am not familiar with them as such i was wondering if anyone would know what is to be done during a service on these units. I have also been told by the client that we will need a trend engineer along so any info from you would be appreciated.
03-06-2008, 12:47 AM #2
Re: Carrier VAV
Start by getting the model numbers and then download the manuals from Carrier.
From memory you'll need to check/calibrate the AHU and then check the boxes.
Depending on the age of the kit then the controllers can go sticky.Brian - Newton Abbot, Devon, UK